Do Other Consultants Review Site Utility Plans?

12/30/2020

11 Comments

 
I've been seven years in the chair, and the most thankless job I encounter on every project is - reviewing the site utility plan and picking it apart.

I've now made my own rule that I will only point the civil engineer's mistakes once, early in the project, and when it comes time to stack the riser, pressure test, etc, all I can say is "I pointed that out to you on Aug 11 2020 email."

Am I going about this the wrong way? SHould I even be investing energy into correcting the engineer with the stamp?

Recent example is a two story building with concrete tees. We're adding third and fourth floors from new structural members. The underground man took the site utility and started digging. Check valve was exposed above ground (supposed to be in pit) and the FDC was connected to the underground on the system side of the backflow preventer. Now he has to dig it up, cap the tee after the backflow preventer, and run it around and inside the building. The job requires a small pump (CL1 manual wet standpipe), and the underground man wasn't happy. All I was doing was point out wrong installations before it was too late.

I'm always left thinking, "this isn't even in my scope of work, but it affects everything downstream."

​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
Michael Ruck
12/30/2020 09:13:51 am

You do what is right to protect the public health and safety. It's the number 1 responsibility of an engineer.

You are all on the same design team. Note the errors in a field report. The owner reads those reports. He'll appreciate the fact that it was caught before it became a bigger problem.

Reply
Alex Jenness
12/30/2020 09:18:28 am

Agreed. Projects are a team sport. While you're not expected to hand-hold someone else's scope we're all responsible to point out errors we see. It's all intertwined. The civil affects my work, my work affects the structural, and on and on.

I've also learned that we're all fallible. A stamp or a certification doesn't mean you won't miss something. What's important is that errors are caught, fixed and we learn from what we can.

Reply
Jose Cruz
12/30/2020 12:15:34 pm

What you did is a good engineering practice, at the start up of a project that includes FPS, I use to call a meeting with other trades contractors, trying to make them aware of the rules at the least of NFPA, regarding, mainly obstructions, underground pipe depth, an so on.

Reply
Jonathan Sullivan
12/30/2020 09:24:21 am

100% agree with Michael. I appreciate comments on my designs (hvac, fire protection, and plumbing) from any team member whether they're in the field or at the desk. I usually end up learning something new or adding a new item to a design checklist.

Yes, it can be exhausting to repeat yourself. At the end of the day, your client (and their budget) will appreciate it, and usually the person on the other end will to.

Reply
Glenn Berger
12/30/2020 09:43:33 am

Teamwork and documentation!

Do not get complacent.

Reply
Casey Milhorn
12/30/2020 10:18:14 am

Great comments. Definitely takes a team. These type of mistakes are fairly common where we are and as a sprinkler contractor, we usually end up being the last line of defense, whether we are doing the underground or not. Curious if your area has a requirement for the fire line to be installed by a licensed fire sprinkler contractor. That has helped to alleviate some of the issues in our area. FDC locations seem so simple to us because we understand the purpose of them, unfortunately it's like black magic to a lot of the site utility contractors. They think that we just make up the location as we go along. Keep educating everyone and fighting the good fight. All you can do.

Reply
HJ
12/30/2020 11:24:26 am

Yes, you should look at the civil plans.

To clarify, the FDC must be on the sprinkler system side of the backflow preventer. There can be no shutoff valve between the FDC and the riser. Not sure if that is what you meant.

Reply
Pete D.
12/30/2020 03:26:51 pm

The A&E firm or Architect of record, whoever submits the package to planning, should allow time for interdisciplinary review. Many states, such as TX and TN require that the UG sprinkler work be done by a licensed sprinkler company, that is, no Joe the plumber. If that is the case, there will be a FP sheet for underground sprinkler pipe, and I insist that my design is mirrored on the civil site utility plan. It has to be coordinated for clearance to high voltage, etc.

Reply
Tony Brownanthonycert@yahoo.
1/2/2021 08:31:10 pm

I always review Site Plans and Mech. plans to make sure that I won't have unforseen "gotchas" down the road. I also make it my policy that i will size the Fire Sprinkler service. Last Project that I am working on was asked to submit a letter as to why the Project couldn't have just one service especially seeing the the big name NYCEngineering Firm (I'm a tiny mname firm, there are three of us) had down a 3/4" service for both fire and domestic. The Project is a 4 story (Cellar and three floors) residence with a portable design flow of 180 gpm. That was a fun letter I wrote...

Reply
Mike M
1/3/2021 09:23:58 pm

Great Responses!

When do we stop doing the QA/QC for an engineering / architectural firm? Is that our job? I have been a fire marshal for over 12 years and I recently asked a licensed architect why I am teaching the code, and doing quality control work for a person that makes 200 more dollars an hour than I do. He replied that most of the mistakes come from the 12 dollar an hour intern or drafts person, not the architect. I am not sure this is true, and I am also not sure I should except this type of business model. I rely on my third party consultants to help get the construction documents in line. They are a valuable asset to have, so as a building official...THANK YOU! for checking those civil sheets.

Reply
Chad P.
2/8/2021 03:01:00 pm

As a fellow AHJ it infuriates me that licensed RDP's, despite the fact that they are supposed to check all drawings that bares their stamp, they rarely do and, get pissy when we call their blatantly obvious mistakes out.

Unfortunately, most licensing entities do not care to take action against sloppy work, we we're told not to bother filing complaints and after reading the responses to other AHJ complaints I see why, no one cares. Well until its so egregious, causes a big dollar or life loss.

No one is perfect but a lot of those firms just do not care and downshift 100% of the liability to the subs doing the work. Its sad that there is so much apathy and lack of pride in work.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT