A Minimum Safety Factor for FM Global Projects?

4/26/2023

18 Comments

 
Is there an FM Global requirement for a minimum safety factor in a hydraulic calculation?

We have a project that is following FM requirements, and the calculation "safety cushion" is coming in at 2 PSI.

We have looked through the FM Data Sheets, but cannot find anything to give a minimum criteria.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
18 Comments
Josh
4/26/2023 08:07:29 am

Doesn't FM Global require a 1.4?

Reply
Josh
4/26/2023 08:19:44 am

Edit: I mean isn't it a 1.4 design factor. Not the same thing I was thinking. I typically use 10 psi across the board in my intent drawings. That typically keeps everyone at FMG happy.

Reply
Felipe
4/26/2023 08:41:43 am

FM Data Sheet 3-0 - Hydraulics of Fire Protection, Section 2.1.2.2.3.1 - Density/Demand Area Format will show when the 1.2 vs 1.4 shape factor is utilized.

Jesse
4/26/2023 08:17:27 am

Typically, the requirement for safety factor is from the AHJ and they derive it from IBC. In the FM criteria projects I've designed, I had to meet the AHJ requirement for +10-psi.

Reply
Nic Larrieu
4/26/2023 08:18:31 am

We have always used a safety factor of 10 psi as minimally acceptable for our industrial clients.

Reply
WC
4/26/2023 08:21:36 am

There is no specific safety factor listed in FM Global's public Data Sheets. You can ask the FM engineer assigned to the project or use 10-psi or 10% of the demand pressure whichever is less. Personally, I would not accept a 2-psi cushion.

Reply
Alex
4/26/2023 08:54:59 am

I strive for a 10 psi safety, minimum. Even with a 10 psi safety, I take into consideration my velocity. Once you start getting velocities above 20 (25/30), you are going to lose pressure quickly through additional fittings that may not be within your calc.

Reply
Josh
4/26/2023 09:00:41 am

This is a good thing to point out. I have a note in my 0 sheet that limits the velocity to not exceed 30 ft/s for Hazen-Williams equations.

Reply
Casey Milhorn
4/26/2023 08:57:41 am

NFPA nor FM require a safety margin. My opinion, though it might be unpopular, is that if additional safety margin was vital to these systems doing their job, they would be required. NFPA and FM build in safety margins already, in the density, in the design area, in the C factor. They are X% of the time overdesigned, which is a good thing when it comes to a life safety system. Cost to the end user is a factor in promoting our industry and is an important factor that we must take into consideration. More than once I've had to have the conversation of needing a fire pump on a light hazard project because the water supply was mediocre and due to an attic, or elevation, or some other reason, we couldn't quite get the "extra safety margin" that an AHJ wanted, even though it would work with a few psi "extra" safety margin. NOW, I will say under certain circumstances I do err on the side of caution, especially when it comes down to a 13D or 13R system. I am in favor of some safety margin. Number 1 because a 2 or 4 head design is cutting things a little close (not a lot of room for error), and number 2, because of the bucket test. Also if I suspect the water supply is inconsistent, or I'm not familiar with it, etc... Again, just my opinion and the "extra" safety margin does have it's place, but needs to be looked at on a case by case basis.

Reply
CJ Bonczyk
4/26/2023 09:00:32 am

I assume this project has a municipal supply as opposed to a water storage or break tank. I also assume this is not a manual standpipe system, but rather a standard sprinkler system calculation. That said I have done a lot of FM projects and 10psi
cushion is what is (recommended) in most of the Risk Analysis reports that have been written for those. Occasionally I have seen where the reports states minimum 10 psi or 10% whichever is less safety factor or per AHJ whichever is greater. I strongly do not recommend submitting a set of hydraulic calculations with a 2 psi cushion unless the city provides a water model that already has a certain % deduction built in that used for hydraulic calculations. The city Fire Code Amendments should indicate what the AHJ will require. Please note that regardless of what FM requires you still must adhere to the AHJ requirements as well, thus I would reach out to both parties and determine what is acceptable prior to submittal.

Reply
Dan Wilder
4/26/2023 09:02:28 am

Just about all the projects I have done included a water supply summary from the FM Global Rep for the site/area or we just followed the local AHJ water supply reduction requirements or jobsite specifications.

FMDS0200 (Installation Guide), FMDS0300 (Hydraulics), and FMDS0329 (Water Supplies) reference "Reliable Water Supplies" or when the building is high risk, use of "Enhanced Water Supplies." but I've not taken a reduction in a water supply from a data sheet reference that I remember.

Reply
danefre
4/26/2023 04:01:05 pm

FM also sets the discharge coefficient for a smooth outlet at 0.8.

Another "safety margin" added on top of everything else!

Reply
David Kendrick
4/26/2023 09:46:39 am

This will probably come across as a rant. Apologies to all.

If you look at the front end of any of the standards and notice all the represented industries, organizations and firms please remember their collection, processing and publishing standards has their name connected to the document.

That being said if they publish, it is adequate.

For example, ESFR systems that have a 12 head design area perform well with two heads operating. So what is published is a 12 head design area. For someone to say "well that is what is in the book but I want to be better/safer" is saying they have more knowledge that the creator of the standards.

I'm aware of the industry practices and if its published that you need 10% or 10 psi that is what you work/layout towards.

There is an issue that I'm not referring to which is seasonal water supplies. These have data to back up what supply is available and back that up. This is a different.

It is when you find a "rule" promulgated by the arbitrary decision.

Personally I look at the NFPA standards for water based fire protection are largely a cookbook. A set of instructions.

Over the years the committees found the issues and after research and collecting data the industry publishes a new rule.

This is MY personal opinion.

Reply
Anthony Brown
4/26/2023 10:47:58 am

I use 10% of supplied pressure. The many AHJ that I deal with all accept this number. The only exception is if the local water authority supplies me with a "Historical average low pressure" number than I will use that regardless of the current pressure reading.

Reply
Glenn Berger
4/26/2023 11:05:44 am

The answer to the question is specific to the local FM rep or the local AHJ, and maybe the FPE.

I think that we all in agreement that there needs to be a safety factor. but there is no published minimums,

Reply
David Kendrick
4/26/2023 11:11:28 am

The published pressures, quantities, spacings are all the minimum requirement printed with the safety factor already included.

Water service piping and fittings with 175 psi working pressure (published) have a safety factor or bursting pressure of 700 psi.

Reply
Max
4/28/2023 02:29:56 pm

I agree with Casey. Examining the loss data, most fires open, and are controlled by, one to three fire sprinklers. In storage scenarios, 4 sprinklers typically open. For a light hazard system with remote area decreases, there are 9 sprinklers calculated on average. This gives a safety factor of 3 to 9. For the storage scenario, this also gives a safety factor of 3 if we consider an ESFR system. So a safety factor of 3 is typically built in. Additional safety factors don’t seem to be needed.

Reply
Mike
4/28/2023 05:27:42 pm

I don't think 2 PSI is wise regardless of any published or required minimum. It's so easy to go over that by only adding a few offsets in a bulk main or end of line. There are always unforeseen circumstances.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT