Foam Design Criteria for Diesel Storage Tank?

11/8/2023

8 Comments

 
We have a project design for a single room (26'-0" x 14'-6", height of 13'-2"). The room is noncombustible and is solely for the storage of one large metal diesel fuel storage tank in the basement of a hospital. The tank is under 8-ft tall.
Picture
I have researched NFPA 13, 16, and NFPA 30. I used the tables for sprinkler type and criteria.

My confusion is the amount of storage and the size of the tank.

The tables in NFPA 30, starting with Chapter 16.5.2.1, have guidelines for tank sizes up to 60 gallons only. This is a much larger, metal, stationary tank (3,000 gallons).

What table or design criteria can be used?

K-factors of 8.0 or 11.2 - and 0.30 or 0.40 density?

We will be using foam for this project and I just want to be sure that I'm approaching and educating myself for the correct approach without missing or violating limitations within NFPA 30 (or the other standards). Thanks for the help!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Jose Pinies
11/8/2023 08:38:15 am

I´d like to know too

Reply
Adam
11/8/2023 08:48:11 am

I am not experienced in this topic, either, but it appears that NFPA 30, Chapter 16 does not apply due to such tanks being excluded under 9.1.4 sentence (2).

See NFPA 30 16.4.1. and the associated flow charts.

Where to go next? I'll have to leave that to someone else!

Reply
Anthony
11/8/2023 09:34:30 am

What we're missing is a code path something pointing you to a particular code/standard. Generally building code will point you to NFPA 13. 13 will point you to 30 and 30 will point you to 11, 15

In this case Building code icc ch9 points toNFPA13. NFPA 13-2022 27.2 points you to NFPA 30. NFPA 30-2024 22.8.1(1) point you to NFPA 11 or 15.

I'm not an expert on 11 or 15 and will let other comment the design requirement from there.

Reply
Eric R
11/8/2023 10:44:16 am

If the jurisdiction has adopted the ICC standards then tank storage of flammable liquids actually is covered via the IFC under chapter 57.

5704.2.9.2 Fire protection.
Fire protection for above-ground tanks shall comply with Sections 5704.2.9.21 through 57042.9.2.4.

5704.2.9.2.1 Required foam fire protection systems.
Where required by the fire code official, foam fire protection shall be provided for above-ground tanks other than pressure tanks operating at or above 1 pound per square inch gauge (psig) (6.89 kPa) where such tank, or group of tanks spaced less than 50 feet (15 240 mm) apart measured shell to shell, has a liquid surface area in excess of 1 ,500 square feet (139 m2), and is in accordance with one of the following.
1. Used for the storage of Class I or II liquids.
2. Used for the storage of crude oil.
3. Used for in-process products and is located within 100 feet (30 480 mm) of a fired still, heater, related fractioning or processing apparatus or similar device at a processing plant or petroleum refinery as herein defined.
4. Considered by the fire code official as posing an unusual exposure hazard because of topographical conditions; nature of occupancy, proximity on the same or adjoining property and height and character of liquids to be stored; degree of private fire protection to be provided; and facilities of the fire department to cope with flammable liquid fires.

5704.2.9.2.2 Foam fire protection system installation.
Where foam fire protection is required, it shall be installed in accordance with NFPA 11.

NFPA 11 does have "generic" design criteria for foam systems, but also requires that other occupancy related codes take precedence if they apply. Also, since new foam systems should be SFFF type, NFPA 11 requires you to use the MFG's design densities per their listing/approval.

So for example if you went with Viking Sprinkler's USP SFFF foam for Hydrocarbons you would need a 0.22 density to meet their UL listing or a 0.30 density if you needed to use their FM approval. (Just reading off their data sheet here)

Flammable liquid storage and foam systems require a lot of time and effort to work through the code path and design process. It is generally a good idea to reach out to the manufacturer's engineering team as they really know this stuff.

Reply
Anthony
11/9/2023 01:33:40 pm

Good to know! Thanks!!

Jesse
11/8/2023 10:07:37 am

I'd like to know more about the tank and the room. Regardless, 13 will push you toward NFPA 11

Reply
Michael P Venneri
11/9/2023 07:13:55 am

It is not immediately obvious but as stated above, some applications are contained in the IFC for protection of flammable liquids. These designs are acceptable to most unless the IFC is not adopted by the Jurisdiction.
One word of caution is that the new SFFF foam may have a different and increased density than what is contained in the codes referenced for AFFF. There are also specific requirements for foam systems by manufacturer depending on what the equipment is. Most manufacturers have their own listings for their own equipment. That listing will contain specifics related to sprinkler type, proportioner and other details. One day the codes will catch up but make sure whatever your design is it is run by the manufacturer. Especially of a retrofit situation.

Reply
Franck
11/11/2023 04:21:35 am

There is no detailed/precise information in NFPA 11 for the design parameters of the sprinkler/deluge system (chapter 6).
The only information is that the area of application should normally be 5000 sq ft (except of occupancy states otherwise):

6.5.2.2.2.1 Total Design Area.
(A) * The total design area shall be 5000 ft2 (465 m2).

(B) Where applicable occupancy standards specify design areas different from that specified in 6.5.2.2.2.1(A), the occupancy standards shall take precedence.


More practical information is found in NFPA 15 in chapter 7.4 Exposure Protection.

The purpose of the protection of the diesel tank is to avoid that a fire in the surrounding can make troubles to the tank (and its content) and in case of fire involving the tank that it creates unecessary exposure to the outside.

Recommended protection is then found in:

7.4.2 * Vessels.
7.4.2.1
Water spray shall be applied to vessel surfaces (including top and bottom surfaces of vertical vessels) at a net rate of not less than 0.25 gpm/ft2 [10.2 (L/min)/m2] of exposed surface.

Do not forget to provide sprinkler protection below the tanks as they may be exposed to a pool fire and water spray may be ostructed by the tank itself.

7.4.2.5
Where projections (manhole flanges, pipe flanges, support brackets, relief valves, etc.) will obstruct water spray coverage, including rundown on vertical surfaces, additional nozzles shall be installed around the projections to maintain the wetting pattern that otherwise would be seriously interrupted.


I personally generally recommend a sprinkler protection with K8.0, 286°F rated sprinklers with a minimum density of 0.3 gpm/sq ft (12.2 mm/min) over the entire room (or up to 2500 sq ft (232 m2) as it would be for an EH group 1 occupancy.
And same density in the case of deluge system.
This is also in line with recommendations from FM data sheet 7.32 (IGNITABLE LIQUID OPERATIONS).
Information is detailed in Table 2.4.3. Sprinkler Protection for Occupancies Using Ignitable Liquids

Note that there is no need to provide film forming foam in addition to the water spray protection. But this not an issue if provided anyway.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT