MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Duct-Detectors Req'd for RTUs Under 2,000 CFM?

5/17/2023

8 Comments

 
I have a Business occupancy building that is being remodeled and new RTUs units are being installed.

There was a mechanical inspection done recently and the inspector is asking for duct smoke detectors on the supply-side of units under 2,000 CFM.

The units supply air to common areas to a single floor and don’t physically share ducts or plenums.

There is no smoke detector coverage since it’s a sprinklered building. We do have smoke detectors above fire alarm equipment are required.

I tried searching for an answer in IBC, IFC, and NFPA standards, but couldn’t find a definite answer.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
5/17/2023 07:58:35 am

Not a FA guy however this chart comes to mind...

https://www.meyerfire.com/uploads/1/6/0/7/16072416/duct_detector_requirements_-_nfpa_90a_v1.pdf

Reply
Dan Wilder
5/17/2023 08:01:17 am

Check the comments for some additional requirements from the original post as well, maybe there is some confusion on what is being asked...

https://www.meyerfire.com/blog/does-my-unit-require-a-duct-smoke-detector

Reply
Ira Matthews
5/17/2023 07:59:49 am

The requirements for duct smoke detection are found in section 606 of the 2018 International Mechanical Code. 606.2.1 has an exception that does not require duct detection in units that equal to or less than 2,000 CFM.

Reply
Jesse
5/17/2023 08:07:36 am

Did he provide a code reference?

Reply
Scott McCormick
5/17/2023 08:16:12 am

Duct detectors are the most common device installed wrong 98% of the time. I would ask the Enforcement Agency for a Code Section.

I’ve had engineers argue with me about a Big Box Store whose RTU was more than 2,000 CFM and I stated that the duct detectors are not required. There was no duct work and was totally impossible to spread smoke beyond the 4 walls. The answer was “what if the next inspector required it?” It has nothing to do with feeding oxygen to a fire.

Reply
SCHULMAN
5/17/2023 08:40:14 am

I would contact the design team (Mechanical Engineer and Architect) and get a read on the Life Safety approach to the design - they may be using an obscure exception in the code that could trigger the requirement. I've not gotten anywhere asking Inspectors to provide me with code references ...

Reply
Fire Inspector AHJ
5/17/2023 09:46:48 am

They are requiring it because it is a shared space with over 2,000 CFM. The smaller units combined, feeding one space, would trigger a global shut down of all of the units at once.

2012 IMC (sorry I only have an old Mechanical code for reference) Section 606.2.1- Return air systems. Smoke detectors shall be installed in return air systems with a design capacity greater than 2,000 cfm (0.9 m3/s), in the return air duct or plenum upstream of any filters, exhaust air connections, outdoor air connections, or decontamination equipment and appliances.

The argument is that it says "return air systems". The units combined are one system for that space. Just like smoke detectors are part of one fire alarm system, or individual sprinklers are part of one fire sprinkler system. Combined, they are required for that space to work together to provide enough CFM for that area. So, (x4) 600 CFM units serving one room move the same amount of air as one large unit of 2400 CFM in the same room. The same consequences result and therefore a global shutdown of all 4 units is required.

California is a bit clearer on this subject in their amendments, but the rule still applies industry wide in my opinion. I hope this helps.

Reply
Douglas Krantz link
5/17/2023 03:33:42 pm


From the NFPA 72 Code 2016 Edition, under the heading "3.2 NFPA Official Definitions":

"3.2.2* Authority Having Jurisdiction (AHJ).

An organization, office, or individual responsible for enforcing the requirements of a code or standard, or for approving equipment, materials, an installation, or a procedure."

Official Appendix in the NFPA 72 Code:

"A.3.2.2 Authority Having Jurisdiction (AHJ).

The phrase "authority having jurisdiction," or its acronym AHJ, is used in NFPA documents in a broad manner, since jurisdictions and approval agencies vary, as do their responsibilities. Where public safety is primary, the authority having jurisdiction may be a federal, state, local, or other regional department or individual such as a fire chief; fire marshal; chief of a fire prevention bureau, labor department, or health department; building official; electrical inspector; or others having statutory authority. For insurance purposes, an insurance inspection department, rating bureau, or other insurance company representative may be the authority having jurisdiction. In many circumstances, the property owner or his or her designated agent assumes the role of the authority having jurisdiction; at government installations, the commanding officer or departmental official may be the authority having jurisdiction."

The published commentary of the Handbook (found in the NFPA.ORG website, right next to the NFPA 72 Codebook) from the writers and editors of the NFPA Code, goes this way:

"Any given physical property may have multiple authorities having jurisdiction, who may be concerned with life safety, property protection, mission continuity, heritage preservation, and environmental protection. Some authorities having jurisdiction may impose additional requirements beyond those of the Code. If requirements for the installation of a specific fire alarm system conflict, the installer must follow the most stringent requirements."

In essence, the Inspector, having a more stringent requirement for duct detectors than listed in the code, has the last say in this.

Of course, pointing out exactly what the NFPA 72 Code says may help change the mind of the AHJ, and the AHJ may then decide to go with the NFPA 72 Code. However, in the final analysis and according to the NFPA, if the AHJ has a better idea, the AHJ can overrule the NFPA Code.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT