Pathway Survivability Only Apply to ECS?

8/24/2023

6 Comments

 
In NFPA 72, does Pathway Survivability apply only to Emergency Communication systems?

In the 2019 Edition of NFPA 72, Section 12.4 stipulates required protection regarding various levels. Section 24.3 Pathway Survivability defines requirements for different levels of declaration. Chapter 12 applies for all fire alarm wiring.

However, the title of Chapter 24 is for Emergency Communication systems. Does pathway survivability apply only for Emergency Communication systems only?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe​
6 Comments
Pete H
8/24/2023 07:17:44 am

Please forgive my confusion, but NFPA 72 pertains to National Fire Alarm and Signaling Code. I'd think anything in NFPA 72 is emergency communications, because it's part of the fire alarm and signaling.

Reply
DS
8/24/2023 08:12:39 am

The section of NFPA 72:24.3 is addressing all emergency communication systems. This could be two-way wired in-building communications system, emergency voice/alarm communication system, mass notification, area of refuge, and elevator communications system.

Reply
Donovan
8/24/2023 08:52:23 am

Long and short of it yes, but if you use a control module or interface the SLC into the notification, your SLC loop now has to be 2 hour as well.

Reply
Todd E Wyatt
8/24/2023 09:35:36 am

SUMMARY
The 2021 NFPA 72 requirements for "Pathway Survivability" of the Emergency Communications Systems (ECS) per Chapter 24 are only applicable to those systems.

2021 NFPA 72
Chapter 24 Emergency Communications Systems (ECS)
24.1 Application.
24.1.1
The application, installation, and performance of emergency communications systems and their components shall comply with the requirements of this chapter.
24.1.2*
The requirements of this chapter shall apply to emergency communications systems within buildings and outdoor areas.

Refer to 2021 NFPA 72 Chapter 12 Circuits and Pathways 12.4 Pathway Survivability" which then states, "All pathways shall comply with NFPA 70."

2021 NFPA 72 references the 2020 edition of NFPA 70 which includes (15) references to "SURVIVABILITY".

EXPLANATION
2021 NFPA 72 defines "Pathway Survivability" as follows :

3.3.206 Pathway Survivability.
The ability of any conductor, optical fiber, radio carrier, or other means for transmitting system information to remain operational during fire conditions. (SIG-ECS)

ENHANCED CONTENT
Pathway survivability levels are described in Chapter 12. The survivability levels required for ECSs are in Chapter 24. The performance operational goal is described in 24.4.8.6.1. Where the evacuation or relocation plan in a building calls for partial evacuation, the goal is for the communications systems above and below the fire floor (e.g., in a high-rise) to continue to operate during a fire to allow the fire ground commander the ability to communicate with the occupants in those areas.

NFPA 72 Chapter 24 Emergency Communications Systems (ECS)" covers the requirements for the installation and performance of emergency communications systems (ECSs) for in-building fire emergency voice/alarm communications systems (EVACS) and other communications systems such as mass notification systems (MNSs) and paging systems used for emergency purposes. NFPA 72 is the referenced standard

The scoping Code (e.g. 2021 IBC) for these ECS are determined by the building's Occupancy Classification(s) (OC) per Chapter 9 Fire Protection and Life Safety Systems. This chapter includes (3) references to "SURVIVABILITY" :

Section 909 Smoke Control Systems
909.20 Smokeproof Enclosures
909.20.7 Ventilating Equipment
Exception:
1. ​Control wiring and power wiring located outside of a 2-hour fire barrier construction shall be protected using any one of the following methods:
1.1 Cables used for SURVIVABILITY of required critical circuits shall be listed in accordance with UL 2196 and shall have a fire-resistance rating of not less than 2 hours.

Section 913 Fire Pumps
913.2 Protection Against Interruption of Service
913.2.2 Circuits Supplying Fire Pumps
1. ​Cables used for SURVIVABILITY of circuits supplying fire pumps shall be protected using one of the following methods:
2. Cables used for SURVIVABILITY of required critical circuits shall be listed in accordance with UL 2196 and shall have a fire-resistance rating of not less than 1 hour.

The scoping Code then references the applicable Standard (e.g. 2019 NFPA 72 in this case). NFPA 72 is only part of the Code "to the prescribed extent of each such reference" :

2021 IBC
Chapter 1 Scope and Administration
Section 102 Applicability
102.4 Referenced Codes and Standards
The codes and standards referenced in this code shall be considered to be part of the requirements of this code to the prescribed extent of each such reference and as further regulated in Sections 102.4.1 and 102.4.2.

Reply
Robb K
8/25/2023 12:02:43 am

this may help . https://www.nfpa.org/News-and-Research/Publications-and-media/NFPA-Journal/2020/September-October-2020/In-Compliance/NFPA-72

Reply
robb k
8/25/2023 12:08:22 am

https://www.nfpa.org/News-and-Research/Publications-and-media/NFPA-Journal/2020/March-April-2020/In-Compliance/NFPA-72

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT