MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

What Defines a FA Selective-Evacuation Zone?

4/9/2024

6 Comments

 
Sometimes we would not want to evacuate entire buildings in a fire alarm condition, even outside of healthcare facilities.

If a fire alarm is programmed to evacuate only "affected" areas, what defines the boundaries of the affected area?

What building features are required to implement a defend-in-place strategy, in a large Industrial Facility F-1?

Where can I find the specific rating requirements for the fire and smoke barriers separating "affected areas"/zones?

Looking to understand this concept and the requirements around it better; thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
4/9/2024 02:02:36 pm

Not my field so I doubt I'll be of much help, but here's what I got:

From NFPA 101 (2018 Edition)
9.6.3.6.2 Where total evacuation of occupants is impractical due to building configuration, only the occupants in the affected zones shall be initially notified, and provisions shall be made to selectively notify occupants in other zones to afford orderly evacuation of the entire building, provided that such arrangement is approved by the authority having jurisdiction

A.9.6.3.6.2 To approve an evacuation plan to selectively notify building occupants, the authority having jurisdiction should consider several building parameters, including building compartmentation, detection, and suppression system zones, occupant loads, and the number and arrangement of the means of egress.

In high-rise buildings, it is typical to evacuate the fire floor, the floor(s) above, and the floor immediately below. Other areas are then evacuated as the fire develops.

--

Okay, let's dig into that annex. Compartmentation seems obvious as a method to identify separate zones, as do separate floors.

Detection and suppression zones work for our field. Suppression zones sound like individual sprinkler systems. So area under the control of the same sprinkler riser and/or control valve assembly sound like they would be one zone.

Same for areas controlled by the same fire alarm detection/notification assemblies. But as stated, that is not my field so I'm not sure how to break that up and the few class notes I've kept of the basics aren't pointing me in an obvious direction.

Reply
Brett
4/10/2024 10:27:32 am

Thanks for that. I've been finding a lot of the same. Nothing specific, i.e. specific requirements to define a zone.

The intention would be to continue operations in all "unaffected areas," rather than shutting all operations down. Especially if it's not a critical threat to the entire building or false alarm.

Unless it's just up to the AHJ, I'm assuming there's likely a definition for what the barrier must be, to consider an area "separate" from the affected area, and protected well enough to continue operations.

Reply
Glenn Berger
4/10/2024 06:34:43 pm

IMO, would require horizontal fire barriers at a minimum. Look at design criteria / solutions used at hospitals (specifically patient rooms, where there is insufficient staff to evacuate everybody).

Reply
Todd E Wyatt
4/12/2024 02:21:52 pm

SUMMARY
Fire Alarm (FA) “zones” are typically separated by 1-Hour Smoke Barriers (1SB) in Group I Institutional Occupancy Classifications (OC).
Recommend discussing this “defend-in-place” scenario with the AHJ (e.g. Fire Marshal) as it is not specifically prescribed by the scoping Code (e.g. IBC-2021).

EXPLANATION
The “defend-in-place” scenario for a Group F-1 Moderate-hazard Factory Industrial OC may require AHJ approval even if a Fire Alarm & Detection System is not required per IBC-2021 907.2.4 Group F (see REFERENCES below).

This modified “occupant notification” for a Group F-1 is based on ones for Group I OCs (e.g. Hospitals, Nursing Homes, Correctional Facilities) which is based on trained personnel assisting occupants to a safe, adjacent Smoke Compartment (SC) that is protected by 1SB. SCs have additional egress requirements so that occupants that are (temporarily) evacuated horizontally to a SC have a Means of Egress to an Exit without egressing through the SC that has the fire emergency. Since this Group F-1 building may not have “trained personnel assisting occupants to a safe, adjacent SC”, you may get push back from the AHJ.

Q1 : What defines the boundaries of the affected area?
A1 : The scoping Code (e.g. IBC-2021) references “notification zones” (An area within a building or facility covered by notification appliances which are activated simultaneously.) but does not prescribe how these NZs are to be separated from one another.

The FA could annunciate per (1) of (4) initiating devices (Manual fire alarm boxes, Automatic fire detectors, Automatic sprinkler system waterflow devices, and/or Automatic fire-extinguishing systems). Because some of these could be observed by the occupants (e.g. manual fire alarm box), occupants would have an “expectation” of their function and of the FA. For instance, even if a building is not required to be protected by an automatic sprinkler system (ASPS), the installation of visible ASPS heads that are not functional is not permitted since the occupants have an “expectation” that the building is protected by an ASPS.

Reply
Todd E Wyatt
4/12/2024 02:22:19 pm

REFERENCES
IBC-2021
Chapter 9 Fire Protection and Life Safety Systems
Section 907 Fire Alarm and Detection Systems
907.2 Where Required—New Buildings and Structures
907.2.4 Group F
A manual fire alarm system that activates the occupant notification system in accordance with Section 907.5 shall be installed in Group F occupancies where both of the following conditions exist:
1. The Group F occupancy is two or more stories in height.
2. The Group F occupancy has a combined occupant load of 500 or more above or below the lowest level of exit discharge.
Exception: Manual fire alarm boxes are not required where the building is equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1 and the occupant notification appliances will activate throughout the notification zones upon sprinkler water flow.
907.4 Initiating Devices
Where a fire alarm system is required by another section of this code, occupant notification in accordance with Section 907.5 shall be initiated by one or more of the following. Initiating devices shall be installed in accordance with Sections 907.4.1 through 907.4.3.1.
1. Manual fire alarm boxes.
2. Automatic fire detectors.
3. Automatic sprinkler system waterflow devices.
4. Automatic fire-extinguishing systems.

Reply
Author
4/12/2024 04:05:56 pm

Thank you for all of that information. It is helpful.

More additional context may be helpful for further discussion...

This occupancy is F-1.
Fire suppression and fire alarm are in the design.
Voice evac system is included.
Areas do included rated barriers and horizontal exits.
There will be trained staff on site 24/7 to assist with evacuation procedures.
The FD is nearby.

This inquiry is mainly to define what is an adequate barrier for a "separate compartments" that allows for partial evacuation (1hr, 2hr 3hr). The fire alarm is capable of providing different messaging instructions for occupant actions.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT