Attached is a sketch of an interesting design issue we’ve been dealing with. We have a convenience stair connecting multiple floors of an office building. With this, we need to treat the opening as an Atrium opening. So we have told the architect that we need a draft curtain with closely spaced heads. The sketch attached shows some limitations that we’ve been given. My question is, how would you suggest we accomplish the required protection given the constraints of this particular stair?
Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Wayne Ammons
12/3/2019 08:50:51 am
What is the code basis for requiring a draft curtain as well as a water curtain?
Reply
12/3/2019 11:14:51 am
Not the OP, so don't know the AHJ requirements/applicable code editions, but I'm going to try to answer this question from an IBC perspective.
Reply
12/3/2019 11:32:50 am
Assuming this opening connects more than 2 floors, and your code analysis is all in order.
Reply
Jonathan Joseph
12/3/2019 12:27:27 pm
You would want to space your standard spray sprinklers to be spaced 6 feet apart and 6 inches off of the soffit all around the opening
Reply
Cliff
12/3/2019 12:35:20 pm
Would it be possible to create a ceiling pocket on the room side of the stair that would give you the 18" required?
Reply
Mike
12/3/2019 06:08:45 pm
Try "stepping " the acoustic panel so it is higher closest to the stairs.
Reply
SFFD Lt. JC
12/2/2020 02:08:00 pm
I'm not sure of the terminology, the design may be called an "Inverted Soffit", "Ceiling Trench", or "Heat Pocketed Water Curtain" (?). The sprinklers are installed in the Fire Rated Trench's (hard lid) above the ceiling. Heat accumulates in the pocket, and should activate the sprinklers simultaneously. I've seen these before at communicating openings, between buildings on the Property line, and around intervening stairs. If the entire depth of 18" can't be above the ceiling, it will reduce the obstruction of the draft curtain below (maybe only 4" - 8"). If it's not be code compliant, it may qualify as a local equivalency. Consult with your AHJ prior to design commitment.