MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Swap Smoke Alarms with System Smoke or A/Vs?

11/29/2024

2 Comments

 
I have an R-2 convent with existing 120v smokes in the sleeping areas and they are installing a new FACP including low frequency notification in the sleeping areas.

I’ve read the commentary for IBC 907.5.2.3.3.

Would you say based on this section that they would need to either replace the existing 120’s and install system smoke detectors, or change the existing 120’s to a combo audio/visual model?

I'm trying to determine if the intent behind this is that the existing 120v smoke alarms now would also be required to activate visible signaling as well. 

​Appreciate your input!

Moderator: Link Directly to IBC 2021 907.5.2.3.3


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Duct Detector in Supply (72) or Return (IMC) Duct?

11/25/2024

11 Comments

 
NFPA 72 (2016) Section 17.7.5.3 says a duct smoke detector is required in the supply air duct; on the other hand, the IMC (2020) Section 606.2.1 says a duct smoke detector is required in the return air duct.

Which should I follow?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Where is Detection for a 5-Level Deluge System?

11/20/2024

4 Comments

 
For a deluge system with pilot sprinkler detectors in a column (5 levels), where is the pilot line required?

​At what levels do we need detection?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

NFPA 72 Limits for Beam Detector Environment?

11/8/2024

3 Comments

 
Does NFPA 72 (or other standards) have any limit for the environment in which the beam detector is allowed to be installed?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Reliability, Variety of Concealed FA Appliances?

10/25/2024

11 Comments

 
Concealed Fire Alarm Devices: I am looking into specifying concealed fire alarm devices for a project. I have two major questions:

1. Are concealed fire alarm devices reliable?

I have heard second-hand that concealed fire alarm devices do not always function.

2. Are there a variety of manufacturers? I did a quick Google search and have only been able to find one manufacturer.

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Automatic Detection for Group M Tenant Space?

9/26/2024

4 Comments

 
Does a sprinkled tenant space Group M with an occupant load of 51 and sprinklers separated by fire-rated walls from the rest of the mall need automatic fire detection?

I think a pull station or the flow switch to active the notification would be enough. The existing plans show detection in the main sales area, in the electrical room and where the power supply for the NAC is located.

According to my analysis the only mandatory detector should be the one in the power supply room. Wouldn't you agree?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Clean Agent Alone Need Supervising Station?

9/9/2024

9 Comments

 
Are stand-alone clean agent systems required to be monitored by a supervising station or constantly attended location?

I am reviewing plans for a small, remote equipment shed that is equipped with a clean agent suppression system. The building is remote enough and small enough that IBC wouldn't require a fire alarm or sprinkler system.

The designer claims that it doesn't have to report out, but I think they're wrong. I think this would fall under the IBC 907.3 requirements for a dedicated function panel, which still requires supervision of the detectors at a "constantly attended location."

Since the building isn't constantly attended, it would have to dial out to the central receiving station, not just to some guy's email.
From what I've gathered, a full-blown FACP wouldn't be required, but a dedicated panel to dial out would be.

What is your take on this? 

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

One Detector for Elevator Recall and Door Holds?

9/6/2024

5 Comments

 
Suppose you have a small enough elevator lobby with hold-open doors.

​Could you use one detector to activate both recall and door closing, so long as you comply with the spacing requirements for both the doors (based on ceilings) and distance to the elevator(s)?

I don't see why you couldn't if you have an intelligent system that could achieve this through programming, and I don't see anything in NFPA 72 that would prohibit this either.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Smoke Req'd to be Centered on Elevator Door(s)?

8/30/2024

3 Comments

 
Is it mandatory for a smoke detector to be installed directly in front of a single elevator, at the center of the elevator door, for elevator recall?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Is Electronic Monitoring for Sprinklers Required?

8/27/2024

11 Comments

 
I have an older class B Mercantile space that is sprinklered but not alarmed. The last tenant was a large pharmacy chain that monitored their own fire alarm or sprinkler systems. When they left they removed the alarm panel.

The tamper and flow switches are still there, as well as an exterior electronic flow bell.

Does this sprinkler system require electronic monitoring?

Currently they have nothing monitored. I would like it to be monitored, but need something to back me up. We adopted the 2021 I-Codes and 2015 NFPA 101 (Statewide).

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Swap Heat for Smoke in Nonsprinklered Building?

8/13/2024

11 Comments

 
Hi, I am a Fire Alarm system installer and have been active for 25 years.

I am writing today because the change from the UBC to the IBC, or some other change that I am unaware of, has removed the requirements to do anything in an existing un sprinklered building in Washington state.

Looking at the requirements for E occupancy, specifically for a sprinklered building, it says to install heat detectors in most locations. There is no guidance for what to do in an existing non-sprinklered building. This has led some to remove smoke detectors from projects and install only heat detectors other than the one for the panel and power supplies, treating sprinklered buildings and non-sprinklered buildings the same.

I am alarmed by this and think it’s a mistake we will regret. On a sprinklered building, you have suppression, so the fire will likely be in a controllable state when first responders arrive. It makes sense that early warning would be redundant, other than areas like exit pathways or sleeping areas where someone could be overcome with smoke or the exit path may be blocked. Early warning devices are necessary in those cases. If we get the people out safely, then the firemen don’t need to go in. Early warning devices achieve that.

But on a non-sprinklered building there is no suppression. Heat detectors do not go into alarm until the fire reaches them, they are mounted on the ceiling so the walls and building will be on fire before they activate. Smoke detectors will go off when the fire is smoldering getting the first responders on the way before the building is on fire. Oh, and getting the people out of the building before it’s on fire, one of my personal favorites.

My goals, 1. I wanted to add some beam smoke detectors over the gym floor area and some smoke detectors over the stage due to the large amounts of fabric. 2. I intended on replacing all the devices on the permitted installation with like for like. Resulting in smoke detectors in the areas that currently have smoke detectors.

Both of my submittals (to the architect) showing smoke detectors were rejected and I was instructed to show heat detectors. I have no way to argue for the smoke detectors, there is no guidance I can find. We are removing all the life safety out of the life safety systems.

Is there something I am missing, is there a way I can fight to get smoke detection in the halls and classrooms that do not have an exit doors?

I looked at the 2021 IFC chapter 11, specifically 1103. I hoped I had found my solution but reading it more carefully, I see the intent of that statement is the table. I can’t find anything on that table that will keep the early warming detection in the life safety system. I know the goal is to reduce false alarms. Smoke detectors have a bad reputation for unwanted alarms. On this project they were suffering from false alarms. That is the reason they are wanting to eliminate smoke detectors. With in a half hour of being on site the existing system went into alarm. I viewed the point, found out it was a 135 fixed temp heat installed in an attic that was at 150. So Heat detectors false alarm as well when incorrectly applied to the environment or poorly maintained.

​Are we going to regret this or am i just an old man with old ways of doing things?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

How to Get Zone Data from Multiple FA Vendors?

7/25/2024

7 Comments

 
We were looking to tie multiple fire alarm systems together from various vendors such as Honeywell, Siemens, Notifier, intermesh, etc. The end goal is to bring all the zone data for a building to a Siemens Desigo Fire Server.

Currently, the
Monitoring-Only Solution Assembly (MOSA) ring will not accommodate the Honeywell, Notifier, or other non-Siemens panels to bring in a complete data stream in. We are limited to the standard supervisory signals for trouble, alarm, duct detectors, pull station, and smoke detectors as a limited set of data.

Does anyone have an interface that would bring
multiple data points from other vendors' fire alarm panels to the Desigo front-end?

Siemens and Honeywell do not support each other’s components. The MOSA ring is a Siemens product. A 3rd party would be required to facilitate the interface panel.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Can Buildings Share Fire Alarm, Sprinkler System?

7/22/2024

9 Comments

 
Can we connect 2 or three buildings to the same fire alarm system? What about sprinkler?

What code basis (IBC or NFPA 13/72) would allow or disallow multiple buildings on the same system?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Do Multiple Small AHUs Require Duct Detectors?

7/19/2024

5 Comments

 
If you have an open office area with (2) AHUs, each AHU supply fan provides 1,500 cfm of supply air and return air that is fully ducted and has no common plenum.

Would duct detectors be provided on the supply side of each AHU?

Do you combine the "CFM" since both units serve the same area?

If not, would you ever cumulatively add multiple units of CFM?

This has been an ongoing question as each of our AHJs sees it differently.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Mass Notification Need Smoke Detector at Panel?

7/4/2024

6 Comments

 
Does a standalone mass notification system (MNS) require a smoke detector in front of the panel for a drug reduction facility?

The facility is 2,100 sqft and houses a minimum of 11 persons. Basically a drug testing and counseling facility. No Fire Alarm required for the building; being governed by UFC 3-600-01 for the US Air Force.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

How to Space Smoke Detector Above a Ceiling?

6/24/2024

2 Comments

 
What are the requirements for installing a smoke detector above a suspended ceiling?

Is it simply the same spacing rules as if the smoke detector were below the ceiling?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Address FA & FP for Fixed Airplane Inside Facility?

6/14/2024

10 Comments

 
We have an airline opening a training facility in our jurisdiction. The building is fully sprinklered and has a fire alarm.

They wish to install a static airplane fuselage for training airplane cabin personnel. This would be a functioning fuselage with standard airplane doors with ramps.

Has anyone had an experience with this?

This is a fully sprinklered building so our thinking is the fuselage needs sprinkler coverage inside. Is this correct?

This building has a fire alarm system so our thinking is the fuselage needs notification devices. Is this correct?

The fuselage doors do not meet the code requirement for egress doors (locks, swing, etc), how is this addressed?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Fire Alarm Req'ment for Outdoor Li-ion Storage?

5/21/2024

7 Comments

 
From the 2023 Edition of NFPA 855, Section 14.6.4 "Outdoor storage areas with an aggregate area greater than 400 sqft (37.1 sqm) shall be provided with a fire alarm system activated by a radiant-energy detection system with occupant notification installed in accordance with NFPA 72."

How do you interpret this requirement if there is outdoor storage of Li-Ion batteries without any sort of structure and 300' from any building, and there are no occupants to notify?

​Thanks for your help!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Security Grill Required to Open Under Fire Alarm?

5/13/2024

7 Comments

 
Does a security grill utilized in school corridors required to be tied into the fire alarm?

If so, the concept should be that the grill in the closed position should return to the open position when fire alarm is activated, correct?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Must Fire Alarm Stay Active During Renovation?

5/7/2024

12 Comments

 
Is there any code that requires that fire alarm coverage be provided in areas that are in the process of major modifications, including asbestos abatement work?

We have a project which will undergo major asbestos abatement and are getting pushback that the fire alarm system must remain operational in the space during the renovation work.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

How to Calc Performance-Based Visual Coverage?

4/11/2024

2 Comments

 
Looking to learn more about NFPA 72-2019 18.5.5.7 Performance-Based Alternative for visible notification.

Currently have a single 95cd wall-mounted horn-strobe approximately centered in an club office room that is approximately 41-ft by 34-ft, ceilings at 11-ft. The is a wall on the far end that is about 10-ft and 9-ft off the back wall and full height.

Table 18.5.5.5.1(a) is based off direct line of sight is my understanding, but would give a maximum room size of 50-ft x 50-ft.

Are there any resources available to help understand how to quantify the that 0.0375 lumen/ft
² of illumination is met from reflection of surfaces behind the wall?

​I'm sure there are more inputs that are needed but just looking to get started at how to attack the problem. Thanks in advance


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
2 Comments

What Defines a FA Selective-Evacuation Zone?

4/9/2024

6 Comments

 
Sometimes we would not want to evacuate entire buildings in a fire alarm condition, even outside of healthcare facilities.

If a fire alarm is programmed to evacuate only "affected" areas, what defines the boundaries of the affected area?

What building features are required to implement a defend-in-place strategy, in a large Industrial Facility F-1?

Where can I find the specific rating requirements for the fire and smoke barriers separating "affected areas"/zones?

Looking to understand this concept and the requirements around it better; thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Is a Partial Fire Alarm for F-Occupancy Allowed?

12/12/2023

7 Comments

 
Fire alarm question for an ICC state that adopts 2012 IBC/IFC & NFPA 72, 2010 edition.

I have an existing mixed use F-1 & S-1 occupancy. This building was originally built in 1910 with two additions over the years. The building sustained fire damage a year ago and is undergoing repairs, no additions, just repairing fire damage that was quite extensive.

The building is not sprinkled (not required when built). They had a partial alarm system installed about 35 years ago.

The insurance will cover the cost to repair/replace the partial system only, which will require a new FACP, wiring and initiating devices. Insurance will pay for a new system to cover the entire building, if required by code.

We cannot find anything in NFPA 72 that requires the entire building to have alarm coverage. There is no requirement in the IBC for F occupancies (single story, grade level) to have an alarm system.

We do see where non-required systems shall be allowed to be partial.

The question is, since this alarm system is being modified, is there any requirement for the entire building to be alarmed in NFPA 72?

The AHJ would also like to see the entire building to be alarmed, but doesn’t think he can require it by code since it would technically be a non-required system per the IBC.

The only thing he could think of was the requirement for manual pull stations at each exit since the building is not sprinkled. Any thoughts?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Detector for Machine Room Less (MRL) Elevator?

12/6/2023

9 Comments

 
We have a passenger elevator that is a traction, machine room-less (MRL). 

Under NFPA 13, 2013 Edition, Section 8.15.5.2, a 'sprinkler shall not be required for enclosed, non-combustible elevator shafts that do not contain combustible hydraulic fluids.'

NFPA 72, 2013 Edition, Section 21.3.6 states that 'smoke detectors shall not be installed in unsprinklered hoistways unless they are installed to activate the elevator hoistway smoke relief equipment.'

I believe these would apply to this elevator.

Does the elevator only require lobby smoke detectors, including first floor for recall and second floor for alternate recall?

Is a smoke detector actually required within the shaft?

This is my first MRL elevator and I want to make sure we cover everything that's required.

I would appreciate you views on this, thank you!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Interior Horn/Strobes Required for Retail Tenant?

11/27/2023

7 Comments

 
Fighting with myself this morning on whether interior horn/strobes are required for a project going on in my jurisdiction.

It's a 14,000 sqft tenant space in a sprinklered strip mall. The landlord fire alarm panel only monitors sprinkler system and three duct detectors.

Under the 2018 IBC / IFC, no manual fire alarm system is required. Section 907.2.7.1 adds confusion for me regarding occupant notification. It allows an exception for a constantly attended locations to provide instructions in the event of alarm activation from manual pull OR waterflow.

Given no constantly attended location exists, would the sprinkler system in this case require interior horn/strobes within the tenant space?

The exterior bell is on the rear of the building with a landlord maintenance space in-between.

If there was a sprinkler flow in the adjacent tenant space, how would the space in question be notified to evacuate?

The architect on the project feels nothing is required inside the space. Maybe I'm taking a common sense approach to this but want to be sure I have code to back me up in requiring interior occupant notification. This is for a discount retail tenant.

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
<<Previous
Forward>>
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top May '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT