Is FA "Common Use" Any Room with Two People?

7/28/2022

8 Comments

 
I'm in Code Enforcement in New York. I've never been completely comfortable as to where strobes are required in "common use and public use" areas.

I'm not talking about the obvious locations such as open areas, corridors , restrooms, conference rooms, etc. I'm talking smaller enclosed rooms such as offices, pantries, copy rooms, file rooms etc.

The definition of "Common Use" in the New York State Building Code is "Interior or exterior circulation paths, rooms, spaces or elements that are not for public use and are made available for the shared use of two or more people".

With respect to rooms, does "shared use of two or more people" relate to stations, desks, cubicles, etc, where people normally sit and/or work?

Or does it mean any space where at least two people can be in the room at the same time for any duration?

Another example is a doctor's office that has exam rooms that is classified as a Group B occupancy. The patient and medical professional can be in the room, or the patient can be alone for a period of time.

Should we consider exam rooms as public space?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
7/28/2022 07:21:10 am

"With respect to rooms, does "shared use of two or more people" relate to stations, desks, cubicles, etc, where people normally sit and/or work?"

Certainly does, in my opinion.

"Or does it mean any space where at least two people can be in the room at the same time for any duration?"

Depends. Just because two interns at a hospital might hang out in a supply closet together, the supply closet still isn't a "common use" room. However just because an office is only designed for one main work desk, the moment that they've put that second chair on the other side of the desk for someone else to sit in when talking to the person behind the desk, now it's a "common use" room. It's more is the room intended for two people, but if it is intended for two people, that intent can apply to any duration. In my opinion.

"Should we consider exam rooms as public space?"

No, as you've established in the definition of common use rooms, the words are "spaces or elements that are not for public use". While "Public Space" is not identified, "[BE] PUBLIC-USE AREAS. Interior or exterior rooms or spaces that are made available to the general public." is included in the code. Since an exam room is still a room the patient has to be admitted into or allowed within, that exam room is certainly not a public space. In my opinion.

Reply
chad
7/28/2022 08:07:56 am

I have a building code official that interprets that anywhere the public could be in a public space and we have to mandate a strobe in every office unless there is a large glass sidelight or the door is glass and a strobe is outside it.

Its a bit draconian but if you rear the definition it fits.

For your example- I see exam rooms where the use in transient as a public space. Those areas are clearly occupied by the general public at some point and it can be more than one, IE- child/parent. Despite that not being a freely accessible space you just walk into.

Reply
DW
7/28/2022 08:33:39 am

I usually look at the occupancy loads of rooms if provided. If the room has a occupancy of 2 or more I try to provide strobe coverage. I typically see doctors offices with strobes in the exam rooms, and have done a couple of jobs where we did install strobes in those rooms. I personally feel the code isn't 100% clear on the matter, but if I provide coverage in rooms with 2 or more people in the occupancy load I feel I'm covered by the public/common use rules. I have had an AHJ require a strobe in a room with an occupancy of 1 due to the size, but that seemed to be a one time thing.

Reply
Craig
7/28/2022 09:02:54 am

When I am trying to figure this our or try to have a conversation about these "Common use areas" I like to simply lay the facts out so the person I am having a discussion with can come up with their own interpretation on this. The definition of Common Use uses the word "shared use" of two or more versus the "occupant load" of two or more. That being said I think this code is written to leave it up to the AHJ on how they want to enforce this. I have taken snips of the IFC Handbook on the code and definition to help show the intent. The "Diamonds" are the explanatory material, always use the handbooks folks! It provides very valuable information.

907.5.2.3.1Public use areas and common use areas.
Visible alarm notification appliances shall be provided in public use areas and common use areas.
Exception: Where employee work areas have audible alarm coverage, the notification appliance circuits serving the employee work areas shall be initially designed with not less than 20-percent spare capacity to account for the potential of adding visible notification appliances in the future to accommodate hearing-impaired employee(s).
❖ Visible alarm notification appliances must provide coverage in all areas open to the public (use areas) as well as all shared or common use areas (e.g., corridors, public restrooms, shared offices, classrooms, medical exam rooms, etc.). Areas where visible alarm notification appliances are not required include private offices, mechanical rooms or similar spaces. The intent with this section is to replicate the provisions included in the Americans with Disabilities Act Standards for Accessible Design.
The exception allows employee work areas to provide only for spare capacity on notification circuits to allow for those with hearing impairments to be accommodated as necessary. This spare capacity is intended to eliminate the potential for overloading notification circuits when a hearing-impaired person is hired and needs to be accommodated, but reduces the initial construction cost as such alarm notification appliances may not be necessary in every situation.


COMMON USE. Interior or exterior circulation paths, rooms, spaces or elements that are not for public use and are made available for the shared use of two or more people.
❖ Some buildings include areas that are restricted to employees only or where public access is limited. Common-use spaces may be part of employee work areas but do not include public-use spaces. Any space that is shared by two or more persons, such as copy areas, break rooms, toilet rooms or circulation paths, are common use areas. A grade school classroom would be another example of a common-use space (see also the commentaries for the definition of “Public-use areas” and “Employee work area”).

EMPLOYEE WORK AREA. All or any portion of a space used only by employees and only for work. Corridors, toilet rooms, kitchenettes and break rooms are not employee work areas.
❖ An employee work area is different in an office versus on a factory line. An employee work area will most likely expand past the station or desk where an employee performs his or her job. An employee work area could include common use spaces, but not public use spaces. Depending on the duties of the employee, it may also include copy areas, stockrooms, filing areas, an assembly line, etc. (see also the commentaries for the definitions of “Common use” and “Public-use areas”).

PUBLIC-USE AREAS. Interior or exterior rooms or spaces that are made available to the general public.
❖ This term is utilized to describe all interior and exterior spaces or rooms that may be occupied by the general public for any amount of time. Spaces that are utilized by the general public may be located in facilities that are publicly or privately owned. Examples include the lobby in an office building, a high-school gymnasium with assembly seating, an openair stadium, a multipurpose room, an exposition hall, a restaurant dining room, a health club, etc. (see also the commentaries to the definitions of “Common use” and “Employee work area”).

Reply
Manny Rios
7/28/2022 12:29:38 pm

YES.
In our jurisdiction we deal with schools and associated support buildings. In compliance with the current code requirements the designers/AHJ have determined that all occupied areas shall have a notification device. In some smaller areas that are occupied by a least one person, a device needs to installed outside the door leading to said area and the doors left open.

Reply
sean
7/29/2022 05:31:46 am

Public - store front areas, anywhere you would have people come in by invitation

Work area - think private office

common area - copier room, warehouse, corridors that are in an employee only area, etc

Reply
Cory
7/29/2022 08:27:14 pm

I do not provide a strobe in a single person office if there is a chair or 2 across from the desk as the main use is single person office and multiple people are usually there for short periods. However, if a second desk and/or computer is provided, then it becomes a 2 person office in my opinion, requiring a strobe. Just my interpretation and i have never been challenged on it. I do not base it on the size as i have seen some executive offices that are single person and large and smaller intern offices with 2+ persons in it.

Reply
Jason Lupa, PE link
3/19/2025 04:13:15 pm

In a clinic (IBC occupancy Group B), visible notification appliances (strobes) are required in patient exam room since these spaces are common areas per both ADAAG 4.28.1 and IBC [2021] 907.5.2.3.1.. It is impossible to predict if the occupant will be hearing impaired. Patients, clinical staff and after-hours support staff (maintenance/ cleaners) are responsible for their own evacuation.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT