MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Smoke Detector at Elevator Door & at Ceiling?

9/21/2021

7 Comments

 
A project I'm on has a lobby area with a 35-foot tall ceiling next to the elevator door. 

NFPA 72-2010/2013 Section 17.7.3.1.3 and 17.7.3.1.4 allows a smoke detector within 60-inches of the top of each elevator door to protect the opening. This can be used for elevator recall.

In addition to this smoke detector, do I also need one at the ceiling (35-feet) for normal coverage?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Alex Riley
9/21/2021 07:28:23 am

Hi Anonymous,

Great question. I’m having trouble finding a code section to back my claims completely, but here’s what I got:

NFPA 72 (2019) 17.7.3.1.1 states that “the location and spacing of smoke detectors shall be based upon the anticipated smoke flows due to the plume and ceiling jet produced by the anticipated fire, as well as any pre-existing ambient airflows that could exist in the protected compartment”.

NFPA 72 (2019) 21.3.5.1 and 21.3.5.2 state that a smoke detector must be located within 21 feet of the centerline of each elevator door, and for ceiling configurations exceed 15 feet in height, the design shall follow Chapter 17. Section 17.7.3.1.3 states that if the “intent is to protect against a specific hazard”, smoke from an elevator for elevator recall, “detectors shall be permitted to be installed closer to the hazard in a position where the detector can intercept the smoke”.

From both of these code sections, I believe that for your situation, you are required to install smokes above the elevator for recall, and additional smokes at the ceiling to protect against the anticipated smoke flows due to the possible plume form a fire originating within the lobby.

Looking forward to seeing what everyone else digs up.
Alex

Reply
Dan
4/2/2025 12:16:18 pm

The additional smoke detector for the high ceiling area would be located on the wall within 5' of the centerline of the elevator door?

Reply
schulman
9/21/2021 08:10:06 am

I agree with Alex but not based on the code.
Seems like two covers the space better AND provides for the specific elevator shaft coverage. I'm not trying to save money on Fire Alarm systems. Pretty sure the AHJ isn't going to be upset with "possible additional coverage".

Reply
DL
9/21/2021 08:28:50 am

NFPA 72:17.4.7
States that if the intent is to initiate action when smoke or fire threatens a specific object or space, the detector shall be permitted to be installed in close proximity to that object or space.

A17.4.7
This sections indicates that areas that do not require full area protection but do require detection can have coverage within close proximity to protect against fire or smoke. Elevator lobbies with ceilings greater than 15' allow for the detector to be within 60" of the top of the elevator.

Reply
DTW FPE link
9/21/2021 02:22:38 pm

In the early days of elevator recall it was not uncommon to install the smokes just above the elevator door opening as the idea was to protect the elevator shaft from ingesting smoke if it were to open in a smoke filled lobby. While more detectors might be better for finding smoke in a lobby, it doesn't help the function of the elevator lobby detector.

Also, who would want to be the one servicing a detector 35 feet in the air? In the end it might end up being a beam detector from a servicing and coverage aspect...not a inexpensive solution.

Reply
Shafi Sneha link
12/23/2021 01:26:31 am

Thank you for sharing this information. This is very useful.

Reply
Jason Lupa, PE
8/24/2022 10:18:11 am

For lobby ceiling configurations exceeding 15 ft in height or that are other than flat and smooth, detector locations are determined per NFPA 72 Chapter 17. The detector should be within 60" of the top of each elevator door opening to protect the opening, typically mounted on the wall. This is allowed because it is not being used for general detection, but rather, for the protection of the opening.

The IBC references NFPA 72. Chapter 21.3.5 references Chapter 17 for proper detector placement in elevator lobbies which have ceilings exceeding 15’. NFPA 72 [2016] 17.7.3.1.3 & 17.4.8 states: “If the intent is to initiate action when smoke/fire threatens a specific object or space, the detector shall be permitted to be installed in close proximity to that object or space.” The Annex adds: When specific objects or spaces are threatened by smoke or fire, such as at elevator landings that have high ceilings in excess of 15 feet, detection should be placed on the wall above and within 60 inches from the top of the elevator doors. This allows the detector to be located where it may be readily installed, tested and serviced while also providing the necessary smoke detection coverage for the landing. For multiple elevators utilizing wall-mounted detectors, each door opening must be within 5ft of a detector, measured horizontally (perpendicular to the doorway) per Chapter 17.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT