"Buy American" with Only International Options?

8/5/2022

10 Comments

 
For domestic (US) military work, we're generally required to comply with the Buy American Act. 

However, our fire alarm manufacturer's batteries (every listed brand) is sourced internationally. 

Is there some waiver to this requirement for specifically-sourced pieces of equipment? 

Or is there some third-party battery manufacturer that's accepted outside the listing?

I'm wondering how others deal with the Buy American requirements when it doesn't appear we have any options. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
M. Newell
8/5/2022 08:11:37 am

I have also wondered about this while working on projects side by side the fire alarm contractors. We seem to be required to adhere to the specification on domestic specified projects. But it seems like a lot of the FA components come from outside of the US. I am curious how others are getting around this or how they are heading it off.

Reply
Glenn Berger
8/5/2022 08:18:37 am

You need to understand what are the requirements to comply with the BAA. By America does not specifically mean Buy USA products. The BAA changes with every presidential administration, it seems.

Reply
Blaine Parkerson
8/5/2022 08:38:34 am

Glen is spot on. It gets complicated when you look at it as if the government is really buying a building of which the components must reach the threshold of 55%.

It gets more complicated since the battery may be allowed as part of the 45% of foreign sourced in the alarm system purchase; but the govt couldn’t then buy just a replacement battery since that would be a separate purchase and would be over 45%.

There’s also allowances for price and availability that come into play.

My advice is to try to talk to the Contracting officer who has the warrant and the obligation to comply with FAR and DFAR.

Reply
LC
8/5/2022 09:22:03 am

I have found that some other countries are also acceptable under the BAA.

DW
8/5/2022 08:23:37 am

I think the 2nd provision of the act "the items to be procured or the materials from which they are manufactured must be present in the United States in sufficient and reasonably available commercial quantities of a satisfactory quality." would nullify needing to find an American manufacturer. If the batteries are only made over seas then I don't see a sufficient and reasonably available quantity to use but foreign manufactures. Just my thoughts though.

Reply
Gregory
8/5/2022 08:32:33 am

If you can make their products and systems work for your location, then Kingfisher is an all-American brand... Lowell, Massachusetts

https://www.kfci.com/company.html

Reply
David Williams
8/5/2022 09:04:36 am

Running into this with SS riser assemblies as the contractor on the job says no Buy American compliant product is available. (Allowing MJ to keep the job going as the SS riser is only a preference on this job.)

Reply
Mike
8/5/2022 09:23:35 am

There are waivers available.

As for the batteries, you could say they are a part of an assembly, the panel, that is comprised over over 50% USA products.

Reply
Gregory
8/6/2022 09:18:58 am

To answer your battery question specifically and provide you with battery solutions; the following is a website that lists USA manufacturers of batteries.

http://energy.sourceguides.com/businesses/byGeo/US/byP/batP/batt/btora/bType/leadacid/byB/manufacturers/byN/byName.shtml

EaglePicher Technologies, LLC - B & B Battery (USA) Inc. - C&D Technologies, Inc. - East Penn Manufacturing Company, Inc. - Uniross Batteries Corp - NRG Power Solutions - MK Battery Co. - Yuasa Battery, Inc. - Power Battery Company Inc. - Exide Technologies - etc. etc. etc. (the list is fairly long)

I have used Yuasa in fire alarm panels at federal locations that required made in the USA. That was typically test and maintenance (i.e. replacing batteries). However, it would not be unheard of to place within your bid / specification package a requirement that Yuasa or other comparable battery on the list be used. With fire alarm panels, it is about the voltage and with an amp-hour rating sufficient to cover the battery calculation for the alarm load. For both the FACP manufacturer and the end user (owner) the battery manufacturer is not so much of a consideration as is the size (LxWxH), terminals, and cost. If the battery is too large to fit in the panel or requires additional connectors to match the battery terminal, that is something that the FACP manufacturer is considering as a part of production.

From NFPA 72 2022 Edition there is not any preferred manufacturer language. Section 10.6.10 does identify a NRTL requirement, but I believe a UL listing will cover that. It's been some time since I had to vet a Yuasa for an FACP but likely it will still make the grade for a fed-gov project.

In the other sections of NFPA 72, batteries are described from the perspective of performance. In reading your FACP manufacturers literature and cut sheets for the panel, it may or may not have a battery manufacturer listed. I will guess that it does not, but rather will indicate features like "gel cell, lead acid with F2 terminals, etc.". That should give you the ability to add to your specification document, requirements for battery manufacturer that match the buy USA requirement.

10.6.7.3 * Secondary Power Supply for Protected Premises Fire Alarm Systems and Emergency Communications Systems.
10.6.7.3.1 The secondary power supply shall consist of one of the following:
(1) A storage battery dedicated to the system arranged in accordance with 10.6.10
(2) An automatic-starting, engine-driven generator serving the branch circuit specified in 10.6.5.1 and arranged in accordance with 10.6.11.3.1, and storage batteries dedicated to the system with 4 hours of capacity arranged in accordance with 10.6.10

10.6.10 * Storage Batteries.
10.6.10.1 Marking.
10.6.10.1.1
Batteries shall be marked with the month and year of manufacture using the month/year format.

10.6.10.1.2
Where the battery is not marked with the month/year by the manufacturer, the installer shall obtain the date-code and mark the battery with the month/year of battery manufacture.

10.6.10.1.3 *
Effective January 1, 2024, rechargeable batteries for the secondary power supply used in control units, devices, and accessories shall be listed or component recognized by a nationally recognized testing laboratory.

Reply
Albert
8/16/2022 09:41:24 pm

This should be brought to Elons attention.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT