Survivability for Elevator Landing Comm. System?

7/20/2022

7 Comments

 
A question came to me about the survivability requirements for an elevator landing communication system required by 2018 IBC 1009.8/NFPA 101 7.2.12.1. 2016 is the applicable NFPA 72 edition.

The designer is arguing that since NFPA 72 Section 24.3.13 doesn't call out "elevator landing communication systems" by name that it falls under Section 24.3.13.12 and requires a risk analysis. They did note that the 2019 edition "clears up some confusion" but don't mention that the 2019 edition modifies section 24.3.7.2 to reference "elevator landing communication systems" and refer their design to the area of refuge/rescue assistance section 24.10 along with stair communication systems.

The 2016 edition of 24.3.7.2 just references "elevator emergency communication systems, section 24.11" which is pretty clearly about the in-car call systems, not the systems required at the landings by IBC/101.

Now I've done my homework, its pretty clear that from 2016-2019 NFPA wants elevator landing communication systems to meet the same requirements as an area of refuge communication system, and from 2019-2022 its explicitly clear that the elevator landing communication systems need to be robust; further more the commentary language of the IBC, NFPA 101 and NFPA 72 for the elevator landing and area of refuge communication systems all pretty much say the same thing that non-self-evacuating occupants needs a reliable means of communication for the duration they remain in the building, so the two systems would need to function the same.

My problem is that for the 2016 edition this is all implied and implicit language.

I am very confident that elevator landing systems require the same survivability as area of refuge systems but can't find an explicit code reference to support it. Is there a section/commentary section/something I'm missing?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Mitchell O
7/20/2022 10:55:34 am

While I agree that 2019 adds elevator landing communication systems whereas 2016 did not specifically reference that type of system, did the survivability requirements change for that system from 2016 to 2019? (2019) 24.3.7.2 does add occupant evacuation elevator lobby communication systems and points to you Section 24.10, however, 24.10 doesn't appear to speak directly to the requirements for survivability.

Survivability is required by (2019) 24.3.14 and the language under section 24.3.14.10 for elevator emergency communication systems is unchanged from 2016 to 2019 that requires Level 0 through 3. Also somewhat interest that 2019 removed 24.11 for elevator emergency communication systems.

Not sure I have an answer but just workshopping here in an attempt to help. If the designer feels under 2016 this falls back on risk analysis, what is their justification via that risk analysis that the elevator emergency communication systems requires less survivability than an area of refuge?

Reply
OP
7/20/2022 12:50:06 pm

They didn't put one in the RFI or any justification, their position was level 1 was sufficient.

I would argue that the survivability requirements didn't change since I believe elevator landing systems fall under area of refuge. The use of the systems are the same and the language in the appendix/Handbook editions make that pretty clear.

I would also argue that an elevator landing system and an elevator emergency communication system are two different system; one is in car for occupants trapped in the elevator and the other is for the lobby for occupants who cant self evacuate the building.

Something interesting I found was that NFPA 101 pretty much has the same requirements as the IBC but it doesn't call it a "elevator landing communication system," it just calls it a two way communicator in an area of refuge. To me that solidifies that NFPA intents for all the two way communication systems for non-self evacuating occupants to fall into the same requirements and the change from 2016 to 2019 was to ease the confusion with the language in IBC. The 2022 edition adds more updates for the elevator landing system as well, very similar to area of refuge requirements and its given its own section.

Reply
Todd E Wyatt
7/21/2022 11:18:56 am

The adopted Code (2018 IBC) is the scoping document that identifies IF an Emergency Communications Systems (ECS) is required for a Project.

Per 2018 IBC Ch 30 Elevators & Conveyance Systems, it references the following "two-way communication" :

3001.2 Emergency Elevator Communication Systems for the Deaf, Hard of Hearing and Speech Impaired
An emergency two-way communication system shall be provided that:
1. Is a visual and text-based and a video-based 24/7 live interactive system.
2. Is fully accessible by the deaf, hard of hearing and speech impaired, and shall include voice-only options for hearing individuals.
3. Has the ability to communicate with emergency personnel utilizing existing video conferencing technology, chat/text software or other approved technology.

3008.6 Occupant Evacuation Elevator Lobby (Not applicable?)
3008.6.6 Two-Way Communication System
A two-way communication system shall be provided in each occupant evacuation elevator lobby ...

Per the scoping Code, it states that “emergency two-way communication system shall be provided.”

The 2018 IBC Ch 30 does not specifically reference 2016 NFPA 72 as the reference standard for the design, installation, maintenance, and testing of the “emergency two-way communication system”. NFPA 72 is referenced in 3005.5 Shunt Trip and in 3007.7. Elevator System Monitoring.

Per the 2018 IBC Ch 35 Referenced Standards, 2016 NFPA 72 is referenced per the following sections : 407.4.4.3, 407.4.4.5, 407.4.4.5.1, 901.6, 903.4.1, 904.3.5, 907.1.2, 907.2, 907.2.6, 907.2.9.3, 907.2.10, 907.2.12.2, 907.3, 907.3.3, 907.3.4, 907.5.2.1.2, 907.5.2.2, 907.5.2.2.5, 907.6, 907.6.1, 907.6.2, 907.6.6, 907.7, 907.7.1, 907.7.2, 911.1.6, 917.1, 2702.2.4, 3005.5, 3007.7.

The 2016 IBC also references ASME/A17.1—2016/CSA B44—16 Safety Code for Elevators and Escalators and A17.7—2007/CSA B44—07(R2012) Performance-based Safety Code for Elevators and Escalators.

The 2019 edition of the ASME/A17.1 CSA B44—16 Safety Code for Elevators and Escalators states the following :
NONMANDATORY APPENDIX V
BUILDING FEATURES FOR OCCUPANT EVACUATION OPERATION
V-1.l Occupant Evacuation Operation.
(c] An emergency voice/alarm communications system meeting the requirements of NFPA 72 is provided to inform occupants on each floor of the current situation and actions to take in an emergency. The announcements should include information about whether or not the elevators are available.

Reply
OP
7/21/2022 12:27:49 pm

Thats for the in car system, what I'm talking about is the at-landing system thats required if there are no areas of refuge.

Reply
Mitchell O
7/21/2022 11:19:29 am

I agree with your stance that it all seems logical and "makes sense" but I am not sure the code path is there in 2016. If the entire question is about survivability, this appears to come down to NFPA 72 (2016) 24.3.13 and elevator landing communication system are not mentioned. You noted above that you feel that elevator landing communication system are different than elevator emergency communication system (which is noted in 24.3.13.10). So it seems that 24.3.13.12 would be applicable as "all other emergency communication systems" and require a risk analysis.

Reply
OP
7/21/2022 12:42:36 pm

Something I noticed after my original post was that NFPA 101 doesn't use the same language as the IBC for these systems. In jurisdictions where IBC CH10 isn't adopted and NFPA 101 is used, or where 101 and IBC are adopted concurrently I think the language of NFPA 101 is pretty clear that an elevator landing communication system is the same as an area of refuge communication system in NFPA's eyes.

Reply
Mitchell O
7/21/2022 12:52:21 pm

Just reading NPFA 101 now, I agree, that it speaks to elevator landings requiring two-way communication systems under the area of refuge section. If NFPA 101 was the governing code, this would simply require that such a system be installed. It would be up to NFPA 72 to provide the specifics of how it gets installed, which still brings you back to the survivability section of 72 where it lists area of refuge separate from anything elevator related.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT