MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Which Detectors Should Close a Fire Rated Door?

9/30/2021

11 Comments

 
I have a fire wall on a two-story building providing separation for purposes of having two control areas.

There is a small roll-up door on the 2nd floor (in the main egress corridor of the building) in the firewall that can be opened to bring up items from the 1st floor to the 2nd through a lift from the 1st floor.

Is it code compliant to only have smoke detectors in the immediate area of the roll-up door (on each side) trigger the fire pin that closes the door, or, does every single smoke detector (it's a large building) need to trigger the roll-up (fire) door to close?

I am not finding a concrete code section (IBC or NFPA) that all detectors need to trigger the roll-up door to close.

Again, it's a very large building with many detectors. Thanks in advance for any answers/feedback.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
DS
9/30/2021 08:11:30 am

Try 101:7.2.1.8.2 and 72:17.7.5.6.

I read that only the smoke detector for door release has to release the door. This is an emergency control function. See also 101:9.6.5. It is similar to elevator recall detectors, or duct detectors.

Reply
schulman
9/30/2021 08:13:02 am

" (in the main egress corridor of the building)"
you've got me confused - wondering if others are ...

i'm trying to picture this rolling door shutting and closing off the main egress corridor ... ? sounds wrong ..does it have a panic-bar man-door in it ?

is it "on the SIDE WALL of the corridor closing off the "lift shaft" FROM the corridor ?
or maybe it closes off the lift shaft by shutting a small vestibule FROM the corridor ?


Anyhow ... if it's a rated / required fire door, regardless of which smoke sets off the alarm, the door should shut as should all "held-open" fire doors throughout the building...
should be activated by the fire alarm panel ?

Reply
Jake link
9/30/2021 08:14:47 am

Try looking at Section 4.7 (In 2019 ed) of NFPA 80 - it discusses actuation mechanisms, and may have some additional insight for you there. I don't see anything that would necessarily prohibit all devices activating the mechanism, as long as the device placement is in accordance with NFPA 72 for the door releasing. At the same time, NFPA 80 permits fusible links to be used as well, so not necessarily having to be an electronic device.

Reply
Jack G
9/30/2021 08:21:34 am

I ve used fusible link mechanisms on those type doors. Work fine.

Reply
Alex
9/30/2021 12:46:48 pm

I've used fusible link mechanisms as well. That is a possibility

Reply
Rich Mercer
9/30/2021 08:28:53 am

Not sure if your construction code has any caveats on the issue, but check out NFPA 72(2017) 17.7.5.6 Smoke Detectors for Door Release Service.

Reply
Todd Wyatt
9/30/2021 09:04:19 am

Per the 2021 IBC, the fire-resistance rated (FRR) assembly that protects Control Areas on Story 2 would be a 1-Hour Fire Barrier (1FB) per Table 414.2.2. The "roll-up door" in the 1FB is a fire door assembly (FDA) that is required to have a minimum 0.75-Hr rating. Fire doors are required to latch and to be self-closing or automatic-closing in accordance with NFPA 80.

If the FDA is automatic-closing, it is permitted to have hold-open devices as long as they "automatically close by the actuation of smoke detectors in accordance with Section 907.3 or by loss of power to the smoke detector or hold-open device" (IBC 716.2.6.6). If this "roll-up door" is a actually a "rolling fire shutter", it too is required to include an approved automatic-closing device.

NFPA 80 (2019) is the reference standard per the 2021 IBC. NFPA 80 has chapters for Vertically Sliding Fire Doors (10), Rolling Steel Doors (Ch 11) and Fire Shutters (12) that will include the requirements for their self-closing or automatic-closing although it does not specifically address smoke detection locations for smoke-activated doors.

2021 IBC 716.2.6.6 Smoke-activated doors references 907.3 for the installation of smoke detectors for these types of doors. 907.3 references NFPA 72 for the locating smoke detectors. NFPA 72 (2019) includes "Figure 17.7.5.6.5.1(A) Detector Location Requirements for Wall Sections" that identifies the prescriptive requirements for smoke detector locations.

Without knowing your project's specific conditions, I am unable to give you a definitive answer but hopefully this NFPA 72 reference will enable you to determine the requirements.

Reply
Franck
9/30/2021 09:05:38 am

Unless your AHJ has a different requirement, you can do both.
Most common situation is to have smoke detectors on each side to operate the door
But you can also operate it from any of the smoke detectors provided in the rooms on both side (in that last case, this would close the door even if the smoke is detected far away from the opening, which could be a good or a bad thing).

Take it with another configuration : if your building was sprinkler protected, you would probably use the smoke detectors provided close to the door (both sides) to close it, not the sprinkler system.

Reply
Jeff Carbine link
2/23/2022 06:27:33 am

I found it interesting when you said the firewall that may be opened to transport objects from the first to the second story through a lift from the first. I used to think differently about it not until you explained it briefly and it really got my attention. What you said about the fire door was really interesting to me.

Reply
Mia Evans link
5/27/2022 05:55:50 am

It's interesting to know that the door has to be code-compliant to ensure that it can have smoke detectors when they are roll-up types. I will share this information with my brother so that he will have an idea because he plans to get a fire door installation service this year. It's because the house he moved into has had issues of wildfire in the location before.

Reply
George lewis
7/5/2023 10:21:33 am

Can you put a Detex eax 500 on a fire door?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT