The 2019 Edition of NFPA 1221 (Standard for the Installation, Maintenance, and Use of Emergency Services Communications Systems) Section 4.5.2 requires that communication centers "be provided with an automatic fire detection, alarm and notification system in accordance with NFPA 72."
But what constitutes "automatic fire detection?" I'm thinking this is alluding to wanting full smoke coverage of the area/space but the language of "fire detection" seems intentionally vague. A supervised automatic suppression system would meet this definition I think; its seems excessive to think a constantly attended room with fully sprinkler coverage would also require full smoke detection. Is there some other guidance I need to consider here? Is this defined elsewhere? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Dan Wilder
4/20/2022 08:16:47 am
The Glossary of Terms NFPA puts out can be helpful (most times) in trying to define terms, especially across different documents. They tend to leave things vague enough to allow interpretation but provide enough information to give "Intent"...
Reply
franck
4/20/2022 09:15:36 am
you’re right : sprinkler protection that send an alarm to a constantly attended location is also considered as a fire detection.
Reply
Jesse
4/20/2022 10:06:19 am
Dan and Franck are right. I always wondered why so many things in all of the NFPA standards were so vague. It would frustrate me to no end. But, shortly after my first committee meeting on my first technical committee I figured it out. Many times the standards are intentionally vague. A lot of times its to allow the AHJ to fill in the blanks.
Reply
Jack G
4/20/2022 10:15:59 am
Dont look into the question.
Reply
Glenn Berger
4/20/2022 12:06:35 pm
While sprinklers are a valid form of automatic fire detection; you need to consider do you want water flow to be your first indication of a fire condition. You can use a step approach of smoke detection (air sampling then spot type), heat detection (rated at a temperature below sprinkler activation, and then sprinklers.
Reply
A simple way of understanding it is to compare it to a Manual Fire Detection system.
Reply
shahzad Akhter
9/7/2023 06:00:05 am
Is there any standard that provide any guide lines that where we should have automatic detection and where there should be manual detection.
Reply