Can someone explain the need for fire suppression inside a stainless steel box that is considered confined space and is typically operating at minus 40 F?
Our local AHJ is suggesting that we need fire sprinklers inside our spiral freezer. However, I am at a loss of any scenario in which anything is combustible inside this environment. It's either operating at minus 40F or its not, and all electronics (motors etc.) are located outside the box. Its not meant to be occupied by personnel, hence the confined space. So why on earth would we need fire suppression? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Alex
11/21/2022 05:05:48 am
I don’t believe you would require protection within the freezer. To me, it would be considered an unoccupied piece of equipment.
Reply
Glenn Warga
11/21/2022 08:09:02 am
We have had to sprinkler these if the belt is plastic. FM had some data that indicated if the plastic belt catches fire it can turn into an uncontrollable situation. If the belts are stainless steel then we have not had to sprinkler based on non-accessible, non-occupiable space, non-combustible space. 2022 NFPA has updated verbiage to support this.
Reply
chad
11/21/2022 08:28:59 am
Soooooo true, its a nightmare to extiguish combustible conveyor belt fires. The literally spread themselves.
Reply
Glenn Berger
11/21/2022 08:18:13 am
The issue with many built-in place large refrigerators and freezers is not when they are in use, but when they are down for maintenance. If your application is not for a walk-in type unit, then you can make the point of not requiring an installed fire sprinkler system.
Reply
chad
11/21/2022 08:27:39 am
I would kindly ask for a code reference. I think its a broad brush the AHJ is painting. I will admit that my fellow AHJ's sometimes are a bit foolish when pushing for "total" coverage.
Reply
Jesse
11/21/2022 09:56:22 am
I've been down this road numerous times, as the IFD AHJ, Insurance loss control engineer and the designing engineer.
Reply
Anthony
11/22/2022 07:29:16 am
Food for thought on this conversation:
Reply
Bill
11/23/2022 10:56:02 am
Spiral freezers in food industry have a heavy fire loading from the combustible conveyor belts, which are not fire-retardant treated plastics. Many of these freezers are large areas, which are occupiable for maintenance and firefighting. Insurance industry has paid many large claims for fires in spiral freezers, most caused by Hot Work, but the smoke contamination from uncontrolled (non-sprinklered freezer) fire closes the plant for months.
Reply