Why Suction of Fire Pump Needs 10 Diameters?

6/29/2020

40 Comments

 
We have a fire pump room which is very constrained. 

NFPA 20 (Edition 2016), A.4.21.1.2 (2) For horizontal split-case fire pumps, there should be a distance of not less than 10 diameters of suction pipe for side connection (not recommended) to the fire pump suction flange.

The main pumps have a capacity of 3000 gpm (two are electrically-driven and two are diesel-driven) with two jockey pumps at 300 gpm capacity. All are in one room. Pumps suction and discharge pipe  size is 12" as per Table 4.27 (a).

In this scenario, what is the meaning of 10 diameters - is it 10 times of suction size diameter of pump (means 10x12= 120") or something else?

Why is this requirement only limited to suction and why not for discharge side as there is tapping for pressure monitoring? Any thought would be much appreciated.

Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
40 Comments
Wayne Ammons
6/29/2020 08:03:44 am

The purpose for the 10x distance is to prevent turbulent flow from entering the fire pump and impeller which can cause wear and cavitation over time. If your suction size is 12 inch, you will need 120 inches from the fitting flange to the pump suction flange or suction fitting flange, depending on the configuration. Figure A.4.15.6 of NFPA 20, 2016 edition shows example diagrams to better explain this.

Reply
Jim Mernickle link
6/29/2020 10:11:07 am

Does the same hold true for all suction pipe sizing's ? So that a 4" feed pipe would require 40" of straight pipe before the pump and no fittings (90's, 45's etc) in that 40" space ?

Reply
Casey Milhorn
6/29/2020 10:28:28 am

So the 10 pipe diameters, from memory, only applies to backflow preventers and fittings that are at a right angle in a horizontal plane to the suction of the pump. If your underground lead-in is lined up with the fire pump and your only change of direction is in a vertical orientation, you can have less than 10 pipe diameters. Vertical changes in direction don't cause nearly the same type of issue as a horizontal change in direction due to the way gravity affects the fluid moving through the piping. Horizontal changes of direction cause the water to rotate and have the possibility for turbulence and air pockets.
If you absolutely have to make a horizontal change in direction, you can always add some vertical piping up and back down to meet the 10 pipe diameter rule.

Louie Lincoln link
6/29/2020 10:46:20 am

10 x the pipe diameter related to the length of the proposed pipe the length has to be at least 1X the diameter of the proposed pipe. I have seen a pump that was piped directly in from the side.
The pump shaved 1/2 of the impeller off. An impeller would cost tn the range of $5K-$20k.

Reply
Thomas Jones
6/29/2020 11:27:19 am

As mentioned, it is for turbulence. One thing I have done in tight pump rooms is create a "n" shape. So from your incoming line go up than change direction down for 10x the pipe diameter.

Reply
Shaikh
6/29/2020 11:43:18 am

If there is case where o & Y gate valve has to be included within this 10 times pipe dia of suction, Do we need to exclude this length of O & Y gate valve.

Reply
Frank link
6/29/2020 04:02:10 pm

SHAIKH, the 10 diameters are measure from the flagelo of the OS&Y Valve to the suction flange.

Reply
Nguyen Thong Nhat
6/29/2020 09:06:43 pm

Disagree, 10 x Diameter requirement apply only for tee and elbow, or any fitting that cause water turbulent in suction pipe, OS&Y valve isn't one of them.

Franck
6/30/2020 02:08:42 pm

If OS&Y valve is provided, no need to maintain this 10 x diameter as there is no obstruction, i.e. no turbulence, within the pipe when the valve is open.
If you have a gate valve (which is normally not permitted per NFPA on suction side... but can still be seen from time to time) or a backflow preventer or any other equipment, then you need to maintain a safe distance of 50 ft, whatever the size of your suction piping.
The 10 x diameter requirement is only for tee or elbow that are horizontally perpendicular to the plane of the fire pump. No need for vertically perpendicular (NFPA 20 has good drawings explaining what is correct and what is wrong).

Frank link
6/29/2020 04:03:36 pm

the Jockey puma shall be 30 GPM not 300 GPM, please check this capacity.

Reply
Sunil kumar
6/30/2020 11:54:42 am

Jockey pumps requirements are based on local client preference, so it is 300 gpm in this case.

Reply
Shahad
10/13/2020 05:03:08 am

Technically, the jockey pump capacity should be less than the flow from any sprinkler head in the system. In the event of fire, Primary fire pump MUST turn on. This is one of the reason why NFPA doesn't mandate jockey pumps to be listed, as its function should be limited to maintain the pressure in the system.

Nguyen Thong Nhat
6/29/2020 08:52:06 pm

...there "should" be... It's mean you can follow or not follow it. Because Fire pump often run in a short time, so, if your pump room is small, you can pass this requirement. You also can find the explain that why it's should be 10x Diameter in ANSI/HI 9.6.6 figure 9.6.6.3.3b

Reply
Nimal Tissa Wijetunga
6/30/2020 07:41:47 am

Disagree. 10 pipe diameter is a requirement as per NFPA and FM Global.

Besides, there cannot be a small pump room and tight space and all these because take the pump orientation and the space requirement for other functions, you never have tight space in the pump room.

Reply
Nguyen Thong Nhat
6/30/2020 09:40:33 pm

Yes, I think there is an error of word in that requirement. it must be "shall" instead of "should", as shown in 4.16.6.3.1 and 4.16.6.3.2 (NFPA 20-2019 ed.). By the way, there are many commercial building having a small area for pump room that seldom seen in industry building, and they also needn't the FM approval.

Franck
6/30/2020 02:10:54 pm

This is a reliability issue.
Many AHJ or Insurance Companies will anyway not accept this wrong arrangement.
I will not for a new installation !
You will have early ageing of your impeller and pump characteristics degradation over a short-medium term.

Reply
koray uluç
6/30/2020 03:01:11 am

The concern for 10 pipe diameter straight line requirement is not turbulence nor cavitation. it is for the differential pressure occurrence on each side of the pump impeller. That is why it is not required for end suction pump but required for horizontal or vertical split case pump only.
Additionally on split case pump installations, elbows that are close to impeller but vertical to impeller shaft are not need to be far away from the suction flange as described on NFPA 20.
While working, continuous pressure difference on sides of the impeller cause damage on impeller bearings.

Reply
Franck
6/30/2020 02:14:11 pm

end suction pumps are normally not allowed by NFPA, only horizontal split case pumps (more robust and more reliable).

End suction pumps are anyway often used in Europe.
I don't think that any of them is UL listed or FM approved (but maybe I am wrong).

Reply
koray uluç
7/1/2020 01:36:32 am

Sorry, but this is a wrong info

Franck
7/1/2020 01:50:43 am

As often, I was too much self confident and the information I put was wrong (end suction pumps can be FM approved and UL listed). Mostly based on my European experience where such pumps are very often provided, and almost never UL listed or FM approved.
Thanks for the correction Koray.

Nithin Babu
6/30/2020 06:58:22 am

If space is constrain in pump room, then the requirement of 10 D can be satisfied by introducing diffuser, i remember victualic offer such diffuser

Reply
Jeva
10/7/2020 07:18:23 am

Hi can I know the type of diffuser.

Reply
Franck
6/30/2020 02:19:28 pm

In addition to all the above comments, your question was also "why we don't have the same requirement on the discharge side ?".
The reason is that on the suction side you create turbulence and differential pressures on the impeller shaft that could deteriorate the pump characteristics over the time.
On the discharge side, you can't damage the fire pump. This is why there is no such requirement for a minimum distance between the discharge side of the fire pump and the backflow preventer, for example.

Reply
Drew Lange link
6/30/2020 04:31:32 pm

The Minnesota State Fire Marshal used to publish a great one-page newsletter named "Quick Response." The June 2008 issue covered Fire Pump Suction Piping Arrangement. It can be found at the link below. Keep in mind the NFPA 20 references were from a previous version of NFPA 20.

https://dps.mn.gov/divisions/sfm/programs-services/Documents/Quick%20Response%20Newleter/QR0608FirePumpsSuctPipe.pdf

Reply
Nimal Tissa Wijetunga
6/30/2020 10:46:29 pm

Within that 10 Pipe diameter distance, only OS&Y Gate Valve is allowed and this 10 pipe diameter is to get laminar flow to the impeller from the suction side and it is definitely a requirement.

Reply
JUHWAN KANG
7/1/2020 01:50:19 am

Could you inform where can I find any clause for that OS&Y Gate Valve is allowed within 10D?

Reply
Franck
7/1/2020 04:31:05 am

NFPA 20 (Last Edition)
§ 4.16.5.1 OS&Y should be provided on the suction side
§A.4.16.5 OS&Y should be located as far as feasible from the flange when suction supply is from public fire main, but there is no strict distance limitation. And no limitation if from a private reservoir.
§ 4.16.5.4 No other valve type or other approved device should be located at less than 50 ft
§ 4.29.3 check valve and backflow preventer are allowed at 10 D (or 50 ft if butterfly valves are isolating the backflow preventer)

The 10 D limitation in § 4.16.6 is for tee and elbows only.

Nimal Tissa Wijetunga
7/1/2020 10:27:15 am

Dear Franck,

Your information above is totally wrong.

Reply
Joe Meyer
7/1/2020 11:21:36 am

Nimal, you need to reply in the correct string and also comment specifically about what your concerns are. This forum is for fostering discussion.

Joe

Reply
Franck
7/1/2020 11:38:56 am

Dear Nimal
I always like to learn from my mistakes (and I make some from time to time)
Could you please give more details on what is wrong on the information?
Many thanks in advance

Reply
cy
7/1/2020 11:19:04 am

You can review the section for suction diffuser, which according to the NFPA 20 ed 2019 is equvalent to the 10 pipe diameter of straight pipe. Bue review the equivalent pressure loss for this device and check with the manufacturer the installation requirements

Reply
Mohammad
2/8/2021 03:38:08 am

Dear gents

the 10 D when will apply ?

As ANSI should be at 40000 GPM and above and its required 5 D not 10D

the NFPA should specify the pump capacity for the 10 D due it is not essay to provide this kind of distance ,and actually will not effect the small pumps

Reply
Ruben
6/25/2021 10:31:06 am

Would the 10 times pipe diameter requirement be applied to vertical inline pumps?

Reply
Todd Delisle
7/23/2021 08:17:15 am

No it would not. (must maintain appropriate size and prevention of trapped air)

Vertical inline pumps utilize a single suction into the 'eye' of the impeller which has a single inlet unlike horizontal split case pumps. HSCs have two "eyes" and utilize a flow splitter in the casing design to guide water into each impeller's eye.

This link previously posted really is great at explaining it!

https://dps.mn.gov/divisions/sfm/programs-services/Documents/Quick%20Response%20Newleter/QR0608FirePumpsSuctPipe.pdf

Reply
Fidencio Gomez
10/27/2022 04:22:29 pm

Todd good afternoon where did you find this at.

Carlos Segura
11/12/2021 11:53:51 am

Regarding suction diameter, NFPA says that on 4.16.3.2 says "The size of that portion of the suction pipe located within 10 pipe diameters upstream of the pump suction flange shall be not less than that specified in Section 4.28." but what happen for the rest of the pipe?, what size I have to choose?, For example a 1500GPM pump according with table 4.28(a) could be connected to a 8" suction pipe, but only for the 10XD pipe portion, right?, sholud the rest of pipe follow the rule of thumb to use a equal or one bigger size pipe than pump suction?

Reply
Wyn Hinkel
12/14/2022 12:05:10 am

Pretty sure the vertical drop is included in the horizontal distance of 10 pipe diameters before suction flange.

Reply
Ozzy
2/21/2024 01:15:31 pm

I agree with you. According to nfpa 20 2019 the 10 pipe diameter requirement includes vertically fed pumps

Reply
Vasanthan
2/10/2023 12:12:25 am

For a horizontal split case pump, 10D straight pipe to be provided for the suction inlet. My design includes a gate valve and strainer in the 10D. Is the strainer allowable in 10D? Unable to find in NFPA 20 any input on this.

Reply
Rahul P S link
7/23/2024 11:51:57 am

Fire tank at 20m height from ground and fire pump room at ground level is possible?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT