Looking for some back history here - why is heat sensor detection temperature 57 degrees C?
On what basis was sprinkler temperature determined to be 68 degrees C? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Alex
1/4/2023 06:02:52 am
Complete assumption here, but I would assume it is based on testing/calculations between the RTI of a sprinkler and the thermal lag of a heat detector.
Reply
Dan Wilder
1/4/2023 07:45:40 am
For the sprinkler side of things:
Reply
Anthony
1/4/2023 08:20:03 am
This.
Reply
Todd E Wyatt
1/4/2023 08:39:19 am
2022 NFPA 13 Standard for the Installation of Sprinkler Systems includes the following references to “68 degree C” temperature-rated sprinklers :
Reply
Franck
1/4/2023 09:20:49 am
57 degrees C is for heat fire detection devices, not sprinklers. This is why you won't find it in NFPA 13.
Reply
Todd E Wyatt
1/5/2023 08:45:08 am
NFPA 204 references 68 degrees C (see 9.2.5.4.3.2) but it does not reference 57 degrees C.
Franck
1/4/2023 09:26:26 am
Sometimes, the answer is... Why not ?
Reply
Pete H
1/4/2023 11:32:30 am
I'm pretty sure it's based in having temperatures high enough to prevent false trips/releases, and then what matches the mechanism that allows the release of water (for sprinklers) or sets off the detection (for heat detectors) such as fusible links or glass bulbs.
Reply
James E. Art, Fire Protection Engineer
1/4/2023 12:54:37 pm
Standard Accepted Practice
Reply
Dave L.
1/4/2023 01:09:11 pm
Following up on Mr. Wilder, for fire sprinklers, since the earliest development of solder-type sprinklers, a sprinkler temperature of around 160°F (71°C) was deemed safe from accidentally fusing or softening as long as room or ceiling temperature did not exceed 100°F (38°C).