Why So Much Sludge in Dry Sprinkler System?

1/21/2021

5 Comments

 
I have a project with a typical compressed air dry sprinkler system in an unconditioned attic space (site is at 44 deg latitude). The system is 22 years old.

Site maintenance person reports that they've had issues with this system for at least 15 years. Frequent and repeated leaks, predominately pin holes in the mains. They try to repair before the system gets wet, although not always in time.

They recently replaced a 3 inch main and found that it was about 30% filled with sludge. Sludge was dark brown, almost clay like, sludge.

Any thoughts on how such a large volume of sludge can accumulate in a dry system? 

Thanks in advance.

​​​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Dan Wilder
1/21/2021 09:21:08 am

This is gong down the road of corrosion and/or MIC.

Essentially, the air compressor is taking ambient air (and humidity) and pumping it into the system. This air then condenses via temperature gradients across different areas of the system combined with the the initial air introduction (typically warm air due to the action of the air compressor being warm from normal usage).

It sounds like there have been system trips in the past along with (hopefully) inspections per NFPA 25. The combination of moist interior pipe conditions and the introduction(s) and subsequent inability to drain 100% of the water creates these colonies of aerobic/anaerobic bacteria throughout the piping system. Even with the water being introduced quickly, there is no "flushing" type water velocities through most of the system (you may find clean pipe close to the riser, but as the distance increases, I would expect more obstructions) and this is the result - obstructed pipe.

I would recommend a very in depth 5 year inspection, then flush of the entire system, sample drop inspections to verify if there are the same conditions in the smaller drops to start. Verifying correct sloping of the pipe and additional aux drain locations as needed would also be recommended.

Afterwards, integration of N2, Dry Air, or other mitigation and prevention applications to prevent further issues needs to be implemented.

Personally, my company has performed several N2 installations for both wet and dry systems with short term success (up to 5 years worth of mitigation). I say short term because we are still monitoring the sites. The number of leaks and false trips has been greatly reduced (and nearly eliminated the further we get from the install date) and we are now dealing with fixing the already caused damage so it's not just a install and everything is going to be fine fix. Our typical approach is putting out the process, timeline, and costing. There is a large up front investment and not everyone is on board, especially tenants in rentals that will be out of the building in 1-5 years but are tasked with building maintenance & repair.

Potter, ECS, Southtek, General Air, Tyco all have methods available.

Reply
Jesse
1/21/2021 09:30:32 am

Its probably all related.Typically, the overall cause is the combination of water, metal, and the oxygen in the air, The overall corrosion may be MIC, galvanic, or electrochemical.

The buildup of corrosion of the inner pipe wall is what's causing the sludge, and also causing the pin hole leaks. A dry systems is never really dry. There will be some residual water in there from the hydro testing, flow testing, trip test, etc. And this water very commonly has micro-organisms in it. These organisms can be acid producing bacteria, sulfer reducing bacteria, or iron related bacteria. They will wreak havoc on internal piping. The presence of these bacterium coupled with the oxygen in the air will keep eating the inner wall of the pipe.

Inevitably, the pipe will need to be replaced. And I'd consider introduction of high purity nitrogen into the system. It won't reverse the corrosion but will inhibit it further.

Reply
Franck
1/21/2021 10:14:44 am

You can also provide auxiliary drains to try to remove as much as possible water accumulation in the piping (they normally accumulate at the lower parts).

This will not fully solve the corrosion issue but will enable to gain some time.

Auxiliary drains (also called Low-Point Drains or Drum Drips) are required for each section of trapped pipe in a Dry or Pre-Action Fire Protection System.

The purpose of the auxiliary drain is to collect the moisture that condensates from the pressurized air in the system and minimize loss of air pressure during the maintenance of the systems.

Auxiliary drains located in areas subject to freezing should be accessible (approx. 2.1 m (7 ft) above the floor, to which a hose can be connected to discharge the water in an acceptable manner).

When the quantity of trapped water is less than 20 l (5 gal.), the auxiliary drain should consist of a valve not smaller than 15 mm (1/2 in.) and a plug, or a nipple and cap.

When the quantity of trapped water is more than 20 l (5 gal.), the auxiliary drain should consist of 2 valves of 25 mm (1 in.) and one 50 mm x 300 mm (2 in. x 12 in.) condensate nipple or equivalent and accessibly located.


To avoid water being trapped at the location of the test valve once the system is back into operation after a full trip test (water moisture condensing on the pipe and being chased to the far end of the system), 2 valves can be provided (drum drip leg arrangement). Such arrangement can be found in NFPA 13.

I have seen systems, when performing the full trip from the ITC, where air was "chased" through the "sprinkler opening" and you could hear the water pushing the air... until the orifice was completely blocked by sludge (as well as the last portion of the pipe). No water going out at all !
In case of fire, this means that some of the sprinklers will not operate and this is a critical situation.

Reply
Jim
1/21/2021 11:49:08 am

I am in agreeance with comments thus far. I've also run across a few instances where the installing contractor did not pitch/slope the pipe in accordance with NFPA 13 causing trapped water in many areas throughout the system. Overtime these typically will be the first areas to fail.

Reply
Phil W
2/4/2021 11:35:54 am

In the UK we are mandated to use hot dipped galvanised pipe (not sure of NFPA requirements) but not everybody is convinced of the absolute effectiveness of reducing pin holes in future; I'd say if is certainly better than an plain internal pipe finish. Not certain of how this might inhibit organic matter developing; N2 is not a normal method in the UK (nor mandated) and so we would always use a compressor with a good quality de-humidifier and be sure to blow out any residual water over a period of weeks (I think you will find this process is described in some of the DPV manufacturers literature. For best results I would say N2 and hot dipped galvanised pipe is about the best you can do, coupled with regular internal inspections at random locations and especially at terminal ranges,

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT