Why does NFPA 13 limit the use of ESFR sprinklers in storage occupancies to 46 feet (14 meters)?
Looking for some next-level insight here. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Pete H
6/3/2022 08:10:49 am
If I had to venture a guess:
Reply
Knee
6/8/2022 10:31:52 am
Agree NPFA testing is the limiting factor.
Reply
Anthony
6/3/2022 08:18:40 am
TL;DR: Fire Testing.
Reply
Matt
6/3/2022 08:20:03 am
That is the highest they have performed full scale testing. Also, the highest roof deck / ceiling height I have seen in NFPA 13 is 45 ft.
Reply
Paul Pinigis
6/3/2022 08:20:39 am
It is simply because that was the height of the ceiling of the testing facility.
Reply
Glenn Berger
6/3/2022 08:22:03 am
For storage applications there are too many scenarios that ceiling level sprinklers would need to be tested and approved. Consult a specific manufacturer for limits on their specific sprinklers.
Reply
Dan Wilder
6/3/2022 08:27:18 am
Typically because no one has submitted inputs with revised or added language and testing backup to be considered/added to NFPA and this is likely due to the larger, accredited test facilities not being tall enough to test above that height.
Reply
Franck
6/3/2022 09:31:29 am
Anthony, Paul & Dan gave the most important reasons : Ceiling height of the testing facility and droplet size/penetration.
Reply
David Kendrick
6/3/2022 09:45:18 am
Manufacturers pay the cost of testing their particular products through independent testing labs.
Reply
Jesse
6/3/2022 09:57:36 am
It has everything to do with listing. And listing has everything to do with testing.
Reply
Mark Harris
6/10/2022 11:58:30 am
Well said Jesse. I run into similar questions on watermist systems.
Reply
Raj Patel
2/5/2023 06:33:50 am
I have a hotel... and in the pool area the ceiling is 30 high...
Reply
Paul Pinigis
2/6/2023 07:57:56 am
It depends upon the fuel for the fire. Obviously, the pool will not burn, but materials around the pool will.
Reply
Don Black
11/26/2023 05:07:43 pm
Yes they will. Suggest you consider corrosion resistant sprinkler heads.
Reply