Why Discharge Fire Pump to Water Storage Tank?

12/5/2022

13 Comments

 
I'm looking at a few projects that have fire pumps and above-ground cylindrical storage tanks for fire protection.

Some projects I have seen have recirculation after the fire pump discharge underground and back into the storage tank. Frustrated I can't find much on this in NFPA 22 or elsewhere.

Is this part of a means for freeze-protection, or to keep the water from getting stagnant, or for pump testing (in which case I guess it would have to branch off from the flow meter)?

Or is it likely engineer preference? Is it a military requirement?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Dan Wilder
12/5/2022 07:05:18 am

Environment, reliability, and cost savings.

Yes, any ITM discharge not able to be measured via a test header would need a flow meter. Most of the pumps I do have a pump discharge-flow meter-testing manifold (hose header or back to tank) which also allows the flow meter to be calibrated onsite without having to remove it. The flow meter allows testing without water discharge for a couple years as allowed in NFPA 25.

Sprinkler water is considered non-potable and is not allowed to be discharged into storm drains per the Clean Water Act.

It doesn't deplete a water source needed for firefighting efforts for a monthly/quarterly/yearly test..i.e. lowering the available water for use in an event while it works to refill itself.

Also, water costs so putting it back into the reservoir that it came from saves the owner money.

It would not be helpful for freeze protection due to the non-continuous nature of the testing. Stagnant water isn't an issue but there is a water quality aspect to tanks that need to be addressed. Pumps (protecting industrial properties in my experience but can be for any application) pull from ponds without an issue.

Reply
Franck
12/5/2022 08:22:14 am

Perfect answer, as usual :)

Reply
Jay
12/5/2022 05:52:31 pm

Hi Dan, what do you mean that the Clean Water Act doesn't allow you to discharge sprinkler water into a storm drain? Every main drain test and typical fire pump test (flowing water from the test header) discharges sprinkler water to a storm drain.

Reply
Jay
12/5/2022 05:55:46 pm

Please ignore my previous post.
I completely lost my mind there for a second.

Anthony
12/5/2022 08:06:52 am

Dan hit it on the head. I've done several tank supplied systems recently and in areas that have a well provide the 'maintenance fill' and if you're not testing back into the tank you end up needing to call and pay for and coordinate with a water supplier every time you test the system. That is expensive and annoying.

Reply
Glenn Berger
12/5/2022 08:10:17 am

On projects that I have a water storage tank, I do recirc the fire pump test header back to the tank. In addition to the reasons that Dan mentions, returning water to the tank prevents flooding and damage to landscaping or others in the way of several thousands of gallon of water flow at a significant pressure.

Reply
Jesse
12/5/2022 08:13:02 am

Seems everyone here beat me to it. I always design a re-cirq back to the tank for all the reasons listed above.

Reply
Franck
12/5/2022 08:20:57 am

In Europe, where we are not using test headers but test lines with flowmeter, they have always been designed that way. The main reason at that time was to save money. When you flow test your pump every week and up to 150% every year, you can save a lot of money.
In addition there are all the benefits listed above (flood exposure, environmental impact, waste of valuable resource…)

Reply
Alex
12/5/2022 08:33:05 am

Hi, seems like everyone hit it on the head. Re-cirq back to the tank for testing purposes.

Reply
Anonymous
12/5/2022 11:30:08 am

Thanks all - I guess what I was trying to visualize is that instead of the test loop (though the flow meter) tying back to the immediate suction side of the pump as is typical, I gather it instead routes back to the tank itself,* not both.
*above the water level in the tank

Does NFPA #25 (ed. 2020) 8.3.3.9.2 then allow this method of flowing back to the tank/reservoir to suffice even for the 3rd test, without having to flow hose streams?

Reply
Dan Wilder
12/5/2022 02:15:13 pm

You get 2 years of flow meter usage with no water discharge; the third year requires water flow not recirculation.

If setup correctly, the flow meter loop feeds the discharge piping (either a hose header to ground or back to a water source like a pond or tank).

Something similar to the below (not an endorsement for the site, just a useful visual graphic).
https://www.anvil-fire.com/apps_pump_sizing.html

Reply
Anonymous
12/5/2022 04:00:53 pm

Gotcha. No way around the test header for the 3rd year, and for the other two, flow meter to tank recirc. (We would typically add a normally-closed valve before the test header hose valves).

Joey
7/19/2024 07:36:53 am

In a situation where the fire pump is pulling from a reservoir or water tower. the flow meter can be piped back to the tank (must discharge to atmosphere) This is testing the hydraulic capabilities of the pump as well as the water supply. This arrangement does not require a test header with hose valves.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT