We have a project for an NFPA 11 foam system. The foam system is used to protect oil storage tanks at different terminal facilities.
Under Chapter 12 of NFPA 11 (2021 Edition), who is the party that inspects and signs off on these systems as the AHJ (Authority Having Jurisdiction)? Is it the local jurisdiction's fire marshal, the facility's insurance company, or the facility itself? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Pete H
11/4/2021 06:51:21 am
Just going to hazard a guess to be taken with a grain of salt: it would vary from state to state. Has your state adopted NFPA 11? Has your local fire marshal adopted NFPA 11? If yes to both, then your local fire marshal would be the AHJ. If yes to the state but not to the locality, a state fire marshal would be the AHJ. If no to both but the system is a requirement from the insurance company, the insurance company is the AHJ. If it is for a federal facility, a federal AHJ might be involved.
Reply
Anthony
11/4/2021 08:19:59 am
The AHJ is the person in charge of the people who show up to put the fire out.
Reply
Alex
11/5/2021 07:11:14 am
Hi Anthony,
Reply
Glenn Berger
11/4/2021 08:25:24 am
Dependent on the location and the user, it could be anybody that you list, and that I will add the Owner's Fire Protection Engineer or Safety Engineer.
Reply
Robert Kluck
11/4/2021 09:12:02 am
While the true Authority having Jurisdiction , in the legal sense, is the Local Authority signing off on the project permits, I think a case can be made that both (Town and Insurer) have authority, and facility. Think of it this way:
Reply
11/4/2021 09:17:44 am
Having done FP design work at LNG, oil terminals, and oil pumping stations I note that interstate facilities are often under a State's Office of pipeline safety delegated from the Federal CFR regulations. The local fire departments have some say since they have to fight the fire.
Reply
Joshua Freedman
11/4/2021 11:34:10 am
As an insurance inspector, I have to say the AHJ can be multiple parties. I have been involved in several projects where there were multiple AHJs. The Fire Marshal will have to sign off on projects, but sometimes the City has looser requirements than everything considered under NFPA or FM and will make allowances, but if their insurance isn't satisfied with the plans, they may have to do additional things which they will be upset were not considered under the original project. I have been involved in projects where I have been ok with less than the City, and also, conversely, required more than the City was. Making changes during the planning phase is a lot more cost effective than starting the engineering and permitting process all over again. If I were you, I would submit plans to the Fire Marshall as well as their property, liability, and work comp coverages (hopefully all the same provider) to make sure everyone is ok with it and you can explain to your client how you are providing them high level service.
Reply
11/4/2021 11:52:33 am
In the NFPA 72 (for fire alarm systems – I assume that other code publications are similar), under the definitions in the front of the Code Book, the list basically that there is an AHJ. But when looking in the back of the same Code Book, in the Annex or Appendix, the NFPA goes into more detail about what the mean.
Reply
Jesse
11/4/2021 04:19:59 pm
It could be an all-of-the-above thing. Not sure where this is, but in Texas we have overlapping AHJs in which there are municipalities and quasi-municipalities that are separate, yet equal political subdivisions. So we have many projects that have multi permits required.
Reply
Mike
11/5/2021 06:07:18 pm
Depending on your jurisdiction, sometimes fire protection piping is considered Process Piping and only goes through the refiners engineers. But the same facility goes through another jurisdiction which requires City Fire Department Approval.
Reply