MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Where is "Bottom of Riser" for 7-Story Building?

4/17/2023

24 Comments

 
I'm working on an existing system in a seven-story building. There is an existing pump and piping which snakes its way through the building.

There is a pressure gauge at the inlet and outlet of the pump, but none afterward until 200' away from the pump room. The pipe branches off with a zone valve assembly with pressure gauge serving that floor area, and then upwards through the remaining floors with no gauge.

Zone valve assemblies with gauges are located on the floors above.

Now for my question - when performing hydraulic calculations, where would you indicate the "bottom of riser"?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
24 Comments
Glenn Berger
4/17/2023 08:09:43 am

Typically the base of the riser is where the water supply enters the building.

I am curious to know - - you stated that the existing piping "snakes its way through the building." Does this mean prior to the fire pump and just the existing configuration in general? Regardless you need to insure that all piping and fittings are included in the calculations from the conducted hydrant flow test to the most remote hydraulically demanding area.

Reply
OP
4/17/2023 09:30:55 am

The service comes into the building and runs for more than a hundred feet before the DCVA, then probably around 75 feet to the pump inlet, then the 200 feet stated earlier begins.

My calculations do take into account this piping as well, with information based on previous calculations.

Reply
Josh
4/17/2023 08:13:49 am

I'm with Glenn here. Typically I consider the base of the riser to be a standard 3' - 5' below where the base of the riser is from the supply in calcs to be safe. The frost lines I mostly work in are pretty shallow so it typically covers that too.

Reply
Eric R
4/17/2023 08:20:55 am

So going by the book, NFPA 13 considers each zone control assembly as the starting point for a "sprinkler system" assuming they have a control valve, gauge, flow-switch, and drain. If that is true then by the book you are required to hang a hydraulic placard at that location and that location would be your base of riser point.

In my opinion this is not a good policy as there is generally no test equipment to verify the hydraulic design installed at these zone controls, so having a placard that tells you the characteristics at that point is basically useless. My opinion is that your base-of-riser would be the outlet flange of the fire pump as it allows you to easily validate that any design changes you have made actually work.

In this case you would still want to hang a new hydraulic placard at the zone control for the system you modified to be in compliance with NFPA 13, and make sure to include a note on the placard stating that the flow and pressure on the placard are based on the fire pump outlet.

Reply
Dan Wilder
4/17/2023 08:30:28 am

Definition of a sprinkler system within 13

3.3.216* Sprinkler System.
A system, commonly activated by heat from a fire and discharges water over the fire area, that consists of an integrated network of piping designed in accordance with fire protection engineering standards that includes a water supply source, a control valve, a waterflow alarm, and a drain.

So the BOR of an individual system (which is what is typically calc'd) is that control valve (in my mind). Nothing is saying that there isn't a "main riser" controlling the building, but making a calc plate ladder at an individual riser that controls an entire building gets difficult.

I've seen it both ways, especially since some of those risers are open to the public and things go missing.

Reply
chad
4/17/2023 08:46:11 am

Agreed and to add to that:

3.5.10 Risers. The vertical supply pipes in a sprinkler system.

So as soon as goes from aboveground to underground is also a good reference point, though usually its the first control valve on the BFP.

Reply
Franck
4/17/2023 08:45:06 am

As indicated by Dan and Eric, Base of Riser (BOR) is at the alarm check valve, where you put the placard

I don’t like hydraulic calculation at BOR, and always ask to have it to the place you make the water flow test (connection to the city water grid or at discharge side of the fire pump).
That way you can check if your water supply is sufficient for your demand, despite possible fluctuations / degradations.

BOR is typically a US approach as it defines your sprinkler system downstream the alarm check valve and if you modify the connection upstream, it doesn’t change your hydr. calc. results.
But it does not help to make an analysis of existing installations with water flow (pump curve) results as you don’t have the friction losses from your BOR to the water supply testing point.

Reply
OP
4/17/2023 09:37:10 am

There are also no alarm check valves in the entire system, just water flow switches at the zone assemblies.

Reply
Ryan Page
4/17/2023 08:56:27 am

I mostly agree with Eric, except I would not use the pump outlet as the BOR. As he stated, by the book, the BOR would be at the supply side of the control valve serving the system you are calculating.

That being said, an ADDITIONAL placard should be placed in the pump room on the discharge side of the fire pump. This additional placard would correlate with your most demanding calculation and reference the pump outlet instead of the BOR.

Because there is a fire pump, I have to ask, is there a standpipe or just a riser feeding all of the floors? If there is a standpipe, the standpipe calc placard would serve as the “additional” placard mentioned above.

Reply
OP
4/17/2023 09:52:29 am

There is a standpipe as well that is served by the pump. The pipe tees off, and the standpipe routing is completely unrelated to the sprinkler piping. They don't share chases, or routes.

Reply
Eric R
4/17/2023 09:03:07 am

Longer Rant Incoming:

As someone who handles a significant volume of both NFPA 25 inspection work and design work for existing system modifications the way hydraulic placards, general information signs, and the un-defined location of "base-of-risers" are currently handled drives me batty.

Starting with the Hydraulic Placard:
NFPA has always utilized the "base-of-riser" as the location that the system flow and residual pressure should be calculated to FOR DOCUMENTATION ON THE PLACARD ONLY. This however is generally not the end point of a new system calculation as we are required to calculate back to a point where the water supply is known, which is generally a fire hydrant flow test for systems on public water.

Because of this inconsistency a vast majority of hydraulic placards we see during our inspection work have the incorrect flow and pressure data on them. This can be very problematic when you come across a system with no previous inspection records, and the 2" main drain test indicates a static pressure of 100psi, residual of 65psi and the hydraulic placard states that the system needs 350gpm at 75psi at the base-of-riser. Do I suddenly have an impaired sprinkler system, or simply bad data? Unfortunately this little mistake can cost quite a bit of money to investigate if I can't get my hands on the original hydraulic worksheets.

A very easy way to fix this would be for NFPA 13 to require that hydraulic placards state the flow and pressure needed at both the base-of-riser and at the calculation end-point. Most sprinkler design software provides this information already, and if both locations were required on the placard then the likelihood of using the wrong data would drop significantly.

For the Base-of-Riser Location:
In my opinion the value of documenting the hydraulic characteristics at a base-of-riser is that it gives a point where the design can be validated through flow-testing at a location generally accessible to a private inspector or designer.

With this in mind, I feel that the base-of-riser should be a point on the system that has the ability to perform a flow test. This could be the outlet flange on a fire pump as indicated above, or with the (relatively recent) advent of backflow forward-flowtest manifolds, directly after said backflow preventer.

Having both a previously documented hydraulic base-line on a placard, and a way to validate that the water supply at that point then allows a designer to make modifications up-stream of the point without having to worry about obtaining water supply testing on public utilities that could significantly slow down a design process. (actually not quite as there is still an issue of how the base-of-riser flow/pressure interacts with the water source flow/pressure when taking outside hose into account)

Having "base-of-riser" not be a defined term in chapter 3 of NFPA 13 should be corrected if for no other reason to make a determination on if the point should be located before or after the pressure loss of a backflow preventer. (the correct answer is after)

Lastly the General Information sign:
To go along with my above point on having the ability to measure flow/pressure at the backflow preventer test header. I think that this flow test, which is required to be performed at system commissioning, should be documented on the general information sign along with the original main-drain test results. These two pieces of data go hand in hand in allowing validation of the available water supply for as long as the system stays in service.

Reply
Ryan Page
4/17/2023 09:21:27 am

The flow and pressure needed at the calculation endpoint would be that of just one sprinkler. Calculations are based off demand, not supply.

Reply
Eric R
4/17/2023 10:43:00 am

Ryan,

I think this might just be lingo confusion. When I say calculation endpoint I mean the point where the total system demand meets the known water supply point.

As opposed to the calculation start point being the single most demanding sprinkler head in the design area.

Ryan Page
4/17/2023 09:27:56 am

Sorry, forgot to add that flow tests are required to be done within one year of submitting plans to the AHJ (I don’t currently have a copy of 13 in front of me so I cannot quote what section that’s from). So yes, you can do a preliminary design, but you will not be able to submit it for a permit.

Reply
Eric R
4/17/2023 09:41:24 am

I don't necessarily disagree with you, which is why I commented on the issue of base-of-riser flow testing not accurately taking into account outside hose requirements.

However as far as I can tell, performing system modifications that do not increase the system demand above the currently documented values on the hydraulic placard has generally been accepted by AHJs without requiring updated flow test data.

Dan Wilder
4/17/2023 11:47:07 am

Not sure how you're using a main drain to justify hydraulics...that test is to only show history of the water supply and trigger an investigation to a water supply piping obstruction/closed valve or possibly a new hydrant flow test. At that point there is enough information to start reviewing hydraulics within the building.

Jumping straight to fixing the above ground piping without understanding what is going on between the public supply and the main drain location isn't the intended route.

Reply
Eric R
4/17/2023 01:50:06 pm

(Dan, this wall of text isn't particularly aimed at you minus the aboveground piping part :) , it's just a hot topic of mine at the moment)

When we perform an NFPA 25 inspection for a new customer, any main drain results that show a residual pressure below the pressure on the hydraulic placard gets noted down as potentially needing review unless we have other historical data like an initial acceptance test result or some other documentation(generally previous inspection tags from within a year or two of the system age) that make it clear the reading is acceptable. We don't label this as a deficiency, but as a simple comment for review.

I realize that this goes beyond the strict scope of 25, but it makes sense to document the disparity to protect our liability. If there was ever a fire event and the system performed poorly the owner's lawyer would have a field day going all "As an industry expert didn't you realize that reading could have indicated a problem?!?" if we didn't.

I'm not sure where you are getting us jumping straight to changing aboveground piping though. When we find these disparities we will try to get access to the original contractor's certificate or hydraulic worksheets because quite frequently the placard is simply documenting the wrong node and can be easily corrected with a few minutes of review.

If these documents aren't available then determining if the main drain test is acceptable can not be resolved, and it should be left up to the AHJ on if they want further investigation to occur. From my experience they generally want it investigated, which costs money.

I agree that not having a good understanding of what is happening between the public supply and the main drain is the issue at hand. The question is how do you resolve whether or not the system is capable of functioning properly when the placard is potentially incorrect and there is limited ability to verify the water supply without having to involve the public utility.

I've been told that one should just assume the placard is correct. I'm not willing to accept that when my experience has been they are wrong more often then they are correct. Heck I have pictures of placards with negative pressures on them because the system included a fire pump, and whoever created the sign just pasted in the topline water supply residual pressure without any introspection at all.

Requiring two sets of data on the placard, one for the base-of-riser, and one for the water source would force people to at least recognize there is a difference between the two.

Dan Wilder
4/17/2023 10:03:38 pm

No issue documenting an issue on a separate form in addition to the standard NFPA 25 form however the main drain test does nothing to verify overhead design....it's there to be an easy check of possible underground or supply issues. Now with the forward flow testing for backflows, I would love to see the hydraulic BOR be placed there in the future (for in building or dedicated single building riser feeds at least).

I've got inspector's and fire officials that jump straight to needing overhead fixes with main drain tests when there is no correlation to a measured flow, even a diminished flow doesn't paint the correct picture as the error % is huge when comparing the two on a chart...now, after we exhaust the observation and confirmation phase for anything between and consult the water department for historical data in the area, there may be a water supply issue identified.

https://www.meyerfire.com/blog/advantage-of-flowing-more-water-in-a-flow-test

Jessica L
8/20/2024 02:29:21 pm

"Base-of-Riser" terminology awareness is much-needed. I'd love for the term to be more clearly defined by both NFPA, and FM.

Reply
Anthony
4/17/2023 09:17:53 am

The point of the BOR hydraulic point is so that your hydraulic placard that is hung on that riser can be examined and compared to the current pressure gauge on the system. When you preform your quietly main drain test/ water flow alarm test you can see if the residual pressure is greater than the system placard shows required. If the residual pressure is less than 10% of the requires system pressure then you have an impairment.

For that reason, I like the BOR node at the riser where you're going to test the system. You're way more likely to have the inspector actually look at the riser, placard and gauge and care if all the information is right in front of them. Compared to having to do math or think about where the BOR system incoming is.

Reply
Eric R
4/17/2023 09:52:10 am

Anthony, you are on the right track, but it is important to clarify that technically you should not be comparing main drain results to the hydraulic placard.

Main drain tests in NFPA 25 should be compared to the initial main drain test performed at system acceptance and then to prior main-drain tests performed at previous NFPA 25 inspections. A 10% reduction in this comparison is what creates the deficiency.

You can't compare the main drain test directly to the hydraulic placard (even if it is showing the correct data) as the main drain test does not have a GPM component, and also does not take into account any additional residual pressure reduction that would occur if outside hose allowance was applied to the water supply.

However flows of a main-drain that indicated a residual pressure below what is stated on the placard should be noted as such on the inspection report as it may require further investigation. In multiple instances that this has happened to me we have performed water supply validation testing and then supplied signage at the riser with an updated "initial main drain test result" that can then be used for NFPA 25 purposes going forward.

This is why more clarity on the system signage is so important, and why full BOR flow tests should be performed and recorded at system acceptance for future referencing.

Reply
James Art
4/19/2023 11:19:20 pm

Yes, a 2" drain is intended just to watch the water supply, and compared to previous tests.
I have found several partly closed valves, sometimes key valves, paved over, and some obstructed pipes.
In one case there were 3 parallel systems, and one was much lower, but no one did anything, just wrote it in the tally. for several years.

Factory Mutual, and other insurance companies had charts for Long Drains and Short Drains to estimate the flow from a 2" drain test.
We used these to do a quick and dirty analysis of the water supply,which can then be compared to the required water supply,

Another thing that can be done is add a piece of straight 2" pipe and use a pitot tube to get the flow.

In Ca, AHJ's are supposed to retain plans and calcs for most buildings as long as the building lasts. But many do not, and getting that info is often not possible after a few years.

Another recurring problem in CA is AHJ's that force the addition of backflows, and then the system needs to be upsized.
State law and the CaBC prohibit this in most cases, but the water cos just ignore that law, and are bigger than each client.

Peter H
4/17/2023 10:34:23 am

For the full building? At the pump outlet.

For the individual systems in the zones? At the fitting on the supply side before the alarm valve in the respective floor control valve assemblies.

After that, I'm just echoing what Eric R has already posted.

Reply
Cory
5/25/2023 03:44:55 pm

I typically consider the base of riser as the zone control valve assembly as that is where you put the NFPA 13 calc plaque. Which would be after a fire pump, at the inlet to BFP or individual risers if you have multiple. I usually don't see base of riser's outside of the building/riser room.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT