When is Spray-Applied Fireproofing Required?

4/28/2022

6 Comments

 
How is it determined whether a steel structure will have spray-applied fire resistant materials?

I'm creating performance specification for a bid-set on a project, so I don't yet have input from a structural engineer. The project is a warehouse with large fire loads and exposed steel.

Recently, a project out for bid is a low-rise office building, 100% sprinklered with a wet-pipe system that is concealed by a suspended ceiling. On that project, all of the structural steel has spray-applied fire resistant materials.

What drives the issue of spray-applied fire resistive materials?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Corey Eppinghaus
4/28/2022 08:08:05 am

In Canada this would be dictated by the 3.2.2 building designation or if the floor is a fire separation with a FRR, some roof systems also require it under the 3.2.2 but adding sprinklers can wave that requirement. So in short the code that has been adopted by the AHJ would dictate when you need to protect steel.

Reply
Glenn Berger
4/28/2022 08:08:27 am

The use of spray-applied fire resistive materials is derived from a code analysis. For the IBC, you need to match up the occupancy, with the building area, number of floors, etc. and then determine the applicable construction type. Once know if fire resistive construction is required, then the method of achieving the rating is up to the design team.

Reply
Henry
4/28/2022 08:10:56 am

Per the IBC Unprotected non combustible materials can be used for construction types up to type IIB...after that various aspects of the structure must be protected in some manner...if the structure exceeds the allowable area or height for IIB then you need to start providing protection.

Reply
Todd E Wyatt
4/28/2022 08:13:48 am

The Type of Construction (TOC) of the building determines the required fire-resistance rating (FRR) of the "Building Elements" (e.g. structure).

The 2021 IBC identifies the following TOCs :

Types I : Fire Resistive (High-Rises & Mid-Rises)
Type II : Non-Combustible (NC) & Limited-Combustible (LC)
Type III : Exterior Walls : NC & LC & Interior Walls : Any Material
Type IV : Mass Timber and/or NC & LC
Type V : Any Material (e.g. Wood)

The "Building Elements" include the following :

Primary Structural Frame
Bearing Walls (Exterior/Interior)
Nonbearing Walls & Partitions (Exterior) - See Table 705.5
Nonbearing Walls & Partitions (Interior)
Floor Construction & Associated Secondary Structural Members
Roof Construction & Associated Secondary Structural Members

Depending on the TOC, these "Building Elements" require different hourly ratings from 3 hours to 0 hours. Sprayed fire-resistive materials (SFRMs) are passive fire-protection materials that can achieve this required FRR of the structure.

TOC comes into play when determining the "allowables" (maximum building area, maximum number of stories, and maximum building height) based on the Occupancy Classification(s) of the building and whether the building is sprinklered or not.



Reply
Alex
4/28/2022 08:50:02 am

Hi,

Fireproofing is applied to add the fire resistance rating. Using IBC (2015) Table 601, you can determine your type of construction and the respective fire-resistance rating. For example, if you are Type IIB, you are not required to apply fireproofing as there is a 0-hour structural frame requirement.

For new construction, there is a lot of consideration that goes into what construction type the building will be. For example, Chapter 5 outlines general building heights and areas permitted. The following tables below can be used to ensure your occupancy, size, and height are allowed per Construction Type.

- IBC (2015) Table 504.3 outlines the Allowable Building Height per type of construction
- IBC (2015) Table 504.4 outlines the Allowable Number of Stories per type of construction
- IBC (2015) Table 506.2 outlines the Allowable Area per type of construction

Now, for your case. Let’s deem your warehouse as an S-2 occupancy. If you can fall under the restrictions of a Type IIB construction type, you will not need fire proofing: building height under 75 (if sprinklered), 4 stories and under and under 104,000 square feet (not including possible increases based on frontage). Once you go above any of the above, you will need to follow the fire rating outlined in Table 601.

Thank you,
Alex

Reply
Jesse
4/28/2022 08:54:10 am

The requirement is via IBC. Once the design team determines that fire-resistive measures are needed, the spray applied fire resistive material is an option.

Personally, I avoid terms like "fire-proof" as in my experience, few things are truly fire proof. Everything reacts in some way to an impinging fire.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT