When is Eccentric Reducer's Flat-Side on Bottom?

11/18/2020

14 Comments

 
When/why would an eccentric reducer ever be installed on a fire pump's suction side with the flat side on bottom?

​​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
14 Comments
Wayne Ammons
11/18/2020 08:23:00 am

The purpose of an eccentric reducer on the suction side of a fire pump (when a size change is necessary) is to create a horizontal transfer of air/water into the pump. The orientation of the flat side depends on the direction of incoming water. If the water is incoming from below the pump, the flat side should be on top, if from above the pump, the flat side should be on the bottom, if there is a long horizontal run of water entering the pump the flat side should be on the top. You want as laminar a flow as possible entering the pump to help prevent future wear and tear.

Reply
Paul gowland
10/13/2021 02:38:28 pm

Hello Wayne I understand the eccentric reducer with flat end up under normal circumstances , however when supply comes from above main point of supply & back flow preventer is a floor above. So u are saying the eccentric reducer should be installed with the flat end down ? I did not see this in nfpa 20. Where is this noted per intall requirements? Thx!

Reply
gary lagnese
11/18/2020 10:10:30 am

Flat side is on top to prevent an air pocket that could cause the pump to cavtate.

Reply
Derek Gaston
11/18/2020 10:14:45 am

Hi Gary!

Reply
gary lagnese
11/18/2020 01:07:51 pm

Hi Derek!!!

Craig Vesely
11/18/2020 10:21:06 am

The flat side of the eccentric reducer is to have the flat side of the fitting on the top to prevent an air pocket from forming. Refer to Figure A.6.3.1(a) in the 2019 edition of NFPA 20.

Reply
Franck
11/18/2020 10:35:13 am

Wayne is right
This is a grey area within NFPA which could lead to wrong installation as the flat is not always on top!
The sketch on NFPA only shows the flat at the top, because the drawing is with an horizontal pipe and water coming from below the pump. It is to illustrate that we don't want concentric reductions.

But if the water is coming from above with a vertical pipe to the suction flange, then the flat should be at the bottom.

For more information, have a look at:
https://www.enggcyclopedia.com/2011/12/pumps-suction-piping-eccentric-reducers-straight-lengths-piping/

Reply
gary lagnese
11/18/2020 10:51:20 am

Could not a concentric then be used>

Glenn Berger
11/18/2020 11:01:00 am

Flat on bottom is typically used on steam systems.

Reply
Franck
11/18/2020 11:04:26 am

Not if you want the flow to be as laminar as possible.

Note that is is a pure reliability topic.
Your pump will work well, with a concentric reduction.
But, because of the small perturbation, you may have an early ageing of your impeller.
This would save you some maintenance cost and longer lifetime for your pump.
But it doesn't have an impact on its actual performance for your sprinkler system.

It is more or less the same for the provision of a gate valve on the suction side of your pump.
A butterfly valve will work the same and the small perturbation will not cause your sprinkler system to fail.
But again, you will have an early ageing of your pump... Reliability, reliability...

Plus the fact that you may broke your valve inside the pipe and damage the impeller inside the pump casing (very rare event, but could happen).

Reply
Wayne Ammons
11/18/2020 11:18:05 am

Replying to Gary Lagnese
11/18/2020 10:51:20 am
Could not a concentric then be used>


Concentric reducers are only permitted on the discharge side of the pump. It is the sloping quality of the reducer that has the potential for an air pocket to form if used on the suction side and oriented with the sloping side facing up.

Reply
gary lagnese
11/18/2020 01:12:17 pm

Wayne, I was only asking in reference to a vertical supply feeding the pump.

Franck
11/18/2020 11:12:30 am

You can also add to this list of reliability items the elbow at the intake on the horizontal plane...

I have seen fire pumps installations with all possible mistakes at the intake (elbow + butterfly valve + concentric reduction), and the results (flow curve) were quite good.
In case of fire, it would have done its duty.
But you may need to replace them earlier because of characteristics deviations over the years.

Unless you don't test them (as you create cavitation and degradation only if the pump is running).
But I would not recommend not to test a pump, especially a diesel engine driven fire pump, as the rate of failure increases when the time between 2 tests increases.

But again, the testing frequency of fire pumps is reliability.
And the good balance between testing too often (ageing of material) and not enough (possible failure when you need it) is considered as a weekly test.

Reply
Jack G
10/10/2025 03:30:56 pm

Mechanical pumping systems are installed that way, and they run constantly .
NFPA 20 is vague at best, however I think its installation should mimic mechanical pumps design.
As a Che, I’ve designed oil, Napa pumps this way as fluids are volatile and air must be extracted as much as possible.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT