MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

When Does the 2,000 sqft Minimum Area Apply?

10/17/2023

6 Comments

 
Good morning all.

So I'm looking at an Extra Hazard Group 1 (EH1) dry system under NFPA 13 (2016 edition).

I want to apply multiple adjustments per 11.2.3.2.7 because I want to use high temperature sprinklers to get me a 25% reduction under 11.2.3.2.6.

This can result in the following math: 2,500 * 1.3 for dry system = 3,250 sqft. 3,250 * 0.75 (for 25% reduction) = 2,437.5 sqft.

And this always stays above the 2,000 sqft requirement of 11.2.3.2.6 and everyone is happy.

But it can also result in the following math happening: 2,500 * 0.75 = 1,875 sqft. 1,875 gets forced into 2,000 sqft because I'm not ever supposed to go below a 2,000 sqft design area under 11.2.3.2.6. So then 2,000 * 1.3 (for dry system) = 2,600 sqft.

So would the system have a 2,437.5 sqft design area or a 2,600 sqft design area?

Yeah, it's only two sprinklers, but at these densities that can change a system. I can see an argument for either conclusion. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
danefre
10/17/2023 07:06:46 am

Your first calculation is the correct one. Step 1: make all the area adjustments. Step 2. Check if you are below 2000 sqft.

And as you know, multiplication order doesn't matter.

Reply
Anthony
10/17/2023 07:33:19 am

I don't think either is wrong and this falls under good (or bad, depending on your point of view) "code lawyering." I'd take the smaller area if it was convent and would be compliant and happy with that.

Note NFPA does specifically states there is no order of operations to area reduction or increase:

13-16 annex:
A.11.2.3.2.7

Example 2. A wet pipe sprinkler system (light hazard) in a building with a 16 ft 8 in. (5.1 m) ceiling and a slope exceed-ng 2 in 12 in. (50 in 300 mm) (16.6 percent slope) employs quick-response sprinklers qualifying for a 30 percent reduction as permitted by 11.2.3.2.3. The initial area must be increased 30 percent for the ceiling slope and the resulting area decreased 30 percent for quick-response sprinklers. IT DOES NOT MATTER WHETHER THE REDUCTION IS APPLIED FIRST. If a discharge density of 0.1 gpm/ft2 (4.1 mm/min) over 1500 ft2(139 m2) is chosen from Figure 11.2.3.1.1, the 1500 ft2(139 m2) is increased 450 ft2 (42 m2), resulting in 1950 ft2(181 m2), which is then decreased 585 ft2 (54 m2). The final design is 0.1 gpm/ft2 (4.1 mm/min) over 1365 ft2 (127 m2).

Reply
Dan Wilder
10/17/2023 10:55:43 am

As it looks like you are referencing 2016, my approach would be:

11.2.3.1.1(1) - .3 / 2500
11.2.3.2.5 - Increase 30% = .3 / 3250
11.2.3.2.6 - Reduce 25% = .3 / 2437.5
11.2.3.2.7.1 - This indicates the adjustments shall be compounded based on the area of operation "originally" selected from Figure 11.2.3.1.1, not to apply any other criteria during the process. Any minimums would be checked at the end of the process (see next statement for why).

Also, section 11.2.3.2.7.2 (unsprinklered combustible concealed spaces for 3000 ft²) says that the minimum 3000 ft² is to be applied AFTER all other modifications, not starting with or during the process...so if there is a provision in another area for a minimum square footage, that should also follow the established intent from this section.

Now, looking into the 2019/2022 edition, you can also take an additional 25% off for 11.2K sprinklers. (19.3.3.2.7) but no less than 2,000 ft², which applying the order above, would come 3rd in the list.

I think there is a good argument for the lesser remote area size.

Reply
Jack G
10/17/2023 12:28:45 pm

I would do all required increases to the dry system (bigger number) Then I would apply the discounts.
Do the requirements for the system building first- better fire protection.
Opinion.

Reply
Pete H
10/17/2023 12:31:26 pm

Unfortunately the code doesn't spell it out... but I think the correct math is:

2500 * (All Modifications or Reductions)
2500 * (1.3 * 0.75)
2500 * (0.975)
2437.5

This way the modifiers are applied concurrently.

But as stated, the code does not spell it out plainly enough in my opinion.

To take it further, if you were to use the 11.2k reduction with high temp heads that Dan Wilder was kind enough to point out in 2019-2022 editions:

2500 * (1.3 * 0.75 * 0.75)
2500 * (0.73125)
1828.125, and now that is immediately forced to 2000 square feet.

Which does allow for a 2000 square foot design area for an extra hazard occupancy, which feels kind of dangerous, but it is my interpretation/opinion of the current writing of the code. I could be wrong.

Reply
Pete H
10/17/2023 12:47:41 pm

A dry extra hazard occupancy. I forgot to point out dry in that last paragraph.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT