When are Post-Indicating Valves Required?

12/13/2018

6 Comments

 
Where does the requirement for a post-indicating valve originate? If I only have a sprinkler system, is a post-indicating valve required?

Posted anonymously by a member for discussion. Discuss this | Subscribe
6 Comments
ZS
12/13/2018 06:32:54 am

My understanding is PIVs are needed based on NFPA 13 8.16.1.1.1.2 - at least one indicating valve is required in each source of supply. If for some reason you can't put a control valve on your supply line inside the building, you can use a PIV instead.

One place I saw PIVs used was outside an existing building. My assumption at the time was that they had more than one connection to the water main, and this would allow for each supply to be isolated.

I've also seen them used for convenience. For example, when it would be beneficial to have system control in an area that is subject to freezing.

Reply
Franck
12/13/2018 11:12:48 am

What is the purpose of having a PIV at 40 ft (12 m) ? If you unferstand the « why » behind, you will better understand the purpose.
The aim is to be able to isolate your sprinkler system from the water supply in case of total loss of your building. There are many possible reasons such as a change in occupancy, an impaired system...
If your sprinklers cannot control the fire, there might be a moment when you need to shut the supply to the system to save water for other systems and manual firefighting.
If the building collapse, you also need to isolate the system.
Here comes the 40 ft distance. Most industrial buildings are 30 ft high max. in case of collapse of the wall, the PIV is still accessible.
This means also that the distance may be reduced for a lower building (or increased).
Therefore, for reliability purposes, order of preference is
1. Piv ar safe distance
2. Piv wall (valve on the outside side of the bldg)
3. Valve inside

Some insurance companies such as FM Global (Factory Mutual) strongly recommend PIV and accept other situations on a case by case study (if putting the PIV valve at 40 ft means having the valve in the middle of the road, it doesn’t really make sense).

My motto : every time there is a rule, try to understand the reason behind. It will also help you to accept (or not) alternative solutions.

Reply
Stephen
9/18/2019 01:50:54 pm

It has to be outside of the Collapsible zone of the building which 40'

Reply
Dave L.
12/13/2018 11:44:16 am

It would be good if ANY Civil Engineering types could chime in in this one. ZS, do you mean a PIV as the only means? I am assuming you mean in addition to other indicating control valve(s) inside. In which case, correct me if I’m wrong, but as far as a PIV requirement, I think NFPA 24 used to require a yard PIV (unless the AHJ said otherwise) up through the 2007 edition. But that section (Chapter 6) has since changed. (I think it now only says what to do IF you have one.) With most AHJ,’s their municipal codes are available and searchable on-line, that is where I look for requirements on a case-by-case basis. Around here, some require PIV’s, others do not, and some require it if there is no outside access to the riser room. In some situations wall P.I. is an option, but as Franck says, building collapse zones sometimes factor in. I also check the public works/water purveyor standard details. And my notes from previous jobs. But when in doubt, for me it often comes down to a phone call or email to the AHJ, then document that communication. Similar applies to FDC location requirements.

Reply
EdwH
1/4/2019 10:00:57 am

NFPA 13-2016
8.16.1.1.1.1 Each sprinkler system shall be provided with a listed indicating valve in an accessible location, so located as to control all automatic sources of water supply.
A.8.16.1.1.1 A water supply connection should not extend into a building or through a building wall unless such connection is under the control of an outside listed indicating valve or an inside listed indicating valve located near the outside wall of the building. All valves controlling water supplies for sprinkler systems or portions thereof, including floor control valves, should be accessible to authorized persons during emergencies.
Outside control valves are suggested in the following order of preference:
(1) Listed indicating valves at each connection into the building at least 40 ft (12 m) from buildings if space permits
(2) Control valves installed in a cutoff stair tower or valve room accessible from outside
(3) Valves located in risers with indicating posts arranged for outside operation
(4) Key-operated valves in each connection into the building

the reasoning behind (1) is to avoid collapse of a wall, the reasoning behind (2) and (3) is to be able to isolate a system without entry.
The local AHJ may not allow a wall mounted PIV for the same reasons.

In every case, the reasoning is to be able to isolate a system for maintenance, or repair.

Reply
Joe A link
6/27/2021 04:45:35 pm

One very important reason was left out in this thread. Codes like these were adopted,usually because of an incident that occurred and there was loss of life, property or severe injuries.
PIV’s let firefighters know that the water supply serving the fire sprinkler systems and or FDC connections has water to fight the fire before they send a crew in the building to battle the fire. Without PIV’s in good working conditions there is no way of knowing those valves have been tampered with or shut off by a maintenance crews to fix a water supply line

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT