The difference between "Should" and "Shall" statements is clearly understood by most of us.
How about "Shall be permitted" (for instance NFPA 13, 2019 9.3.2.2)? Splitting frog of hairs but I'm guessing that it equates to "May be allowed"? How do you interpret this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Dan Wilder
3/4/2024 07:06:23 am
It's an allowance to something prior (the "parent" section) that has a hard definition, criteria, or requirement...
Reply
Ricardo Gonzales Jr
3/4/2024 08:33:26 am
As defined in NFPA 1, Shall and Should have two different and distinct requirements.
Reply
Jesse
3/4/2024 09:53:18 am
Shall is typically required as the absolute requirement or allowance whereas should is an advisory recommendation.
Reply
Pete H
3/4/2024 01:05:13 pm
In my opinion, I go by the old rules:
Reply
Glenn Berger
3/4/2024 01:41:31 pm
Not a lawyer here!
Reply
Ivan J Humberson
3/6/2024 03:21:24 pm
Ever since NFPA standards removed "Exceptions", this is the kind of (sometimes confusing) language we now see in many sections. Basically, it usually refers to something that the main section would prohibit, but the "shall be permitted" allows an exception to the overall requirement/restriction. Personally, I felt that having "Exceptions" was a much cleaner and logical manner to describe what is required or not required. Today's methodology requires one to read every subsection just to ensure there are no 'shall be permitted' sections.