When would you consider an obstruction no longer an obstruction, vertically below an ESFR sprinkler?
If the top of storage has to be 36" wouldn't 36" be the cut off? Or do the obstruction rules go the floor? I have a warehouse that has 2 x 4 light fixtures which are 6'-0" below the roof deck, and am wondering whether these are considered obstructions. Thanks in advance. Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
1/25/2021 09:09:39 am
We have actually asked the NFPA 13 committee what their intent was for this. Unfortunately, the response was that anything can be considered an obstruction to and ESFR sprinkler, no matter the distance from it. We questioned if this applied to things like rails near the floor to protect walkways from forklifts, and were told that it does.
Reply
Bruce Seiler
1/25/2021 09:15:36 am
Obstruction rules still apply. ESFR sprinkler heads have very specific requirements. NFPA 13 2019 Edition Chapter 14. Section 14.2.1.2 would cover the light fixtures, specifically Item (2). "Additional sprinklers shall not be required where the obstruction is 2 ft. or less in width and the sprinkler is located horizontally 1ft. or greater from the nearest edge of the obstruction. Spacing of lights should follow this standard. The standard does not provide a specific distance below the sprinkler head that obstructions become a problem. It distinguishes between Obstructions at or Near Ceiling for non-continuous obstructions and continuous obstructions.
Reply
Mike
1/25/2021 09:24:19 am
Looking at the Tyco ESFR data sheet, under Obstruction Criteria they say to Refer to FM 2-0 Section 2.2.
Reply
Franck
1/25/2021 11:02:29 am
For that reason, in my previous company, we were saying that you have to build a warehouse around an ESFR protection (to avoid all these issues).
Reply
CJ Bonczyk
1/25/2021 10:50:04 am
Unfortunately all obstruction rules currently stated in code apply whether it be FM Global or NFPA requirements. I prefer to follow the installation guidelines as outlined in FM Global. They provide a clear pictorial view of what is required. In your situation it does not matter whether the obstruction is greater than 36" below the bottom of the deflector.
Reply
Franck
1/25/2021 10:55:20 am
Same rule applies for all sprinklers (even though more restrictive in term of width with ESFR):
Reply
Brian Hoole
1/25/2021 12:24:36 pm
2019 NFPA 13:8.12.6 Clearance to storage (Early Suppression Fast Response Sprinklers). The clearance between the deflector and the top of storage shall be 36 in. or greater.