What Code Req'mt Triggers a Backflow Retrofit?

10/6/2022

11 Comments

 
While doing a sprinkler inspection it was found that the main check valve for the system failed. The system was installed before backflows were mandated on sprinkler systems.

I know that a backflow preventer needs to be installed in its place, but have been unable to find any code that says it does.

Anyone able to help?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Anthony
10/6/2022 07:38:21 am

This will be part of the plumbing or heath code not from NFPA 13. Check your state or local building code for backflow prevention requirements.

Reply
Corey Eppinghaus
10/6/2022 08:05:00 am

As Anthony noted it will be in the plumbing code or health code you may also want to check to see if the municipality has a backflow prevention program, they might be able to force them to install one/repair.

Reply
Robb
10/6/2022 08:08:43 am

agreee 100% with Anthony. AWWA and UPC requires these, not the fire code. Is your sprinkler connected to Potable water system (public drinking water)- than yes a BFD is required. if connected to a private fire main -and not cross conencted to the city or campus water mains - than not required.

Reply
[email protected]
10/6/2022 08:14:37 am

Here in Metro NY backflow devices are initiated by the local Water District for their review and then forwarded if required, to the County Health Department.

I would check with the local Water supplier.

Reply
Jesse
10/6/2022 08:16:53 am

This is part of the plumbing code. You won't find it in 13.

Reply
Dan Wilder
10/6/2022 08:41:56 am

The system was installed with a check valve and assumed approved with that installation, its failure during a 25 inspection means repair or replace like for like not add a backflow and potentially change the hydraulics of the system.

If the local AHJ required the replacement with a backflow, they would also (likely) require a hydraulic evaluation of the system for the change. There is no provision to bring a system or portions of that system to current standards based on a NFPA 25 inspection for failed valve only....it would (potentially) allow the AHJ to require a permit to review the work and at that time they can identify on that inspection any additional deficiencies from a FD/AHJ perspective.

If you are a NFSA member, Terry Victor does a great presentation on NFPA 25 and there is a free one available from the canceled Annual Seminar.

Reply
Alex
10/6/2022 08:43:40 am

Hi,

As others have mentioned, the requirement of a backflow will fall under the Plumbing Code.

For example, the International Plumbing Code (2021 edition) 608.17.4 outline connections to automatic sprinkler systems and standpipe systems. The section states that "the potable water supply to automatic sprinkler systems and standpipe systems shall be protected against backflow by a double check backflow prevention assembly, a double check fire protection backflow prevention assembly or a reduced pressure principle fire protection backflow prevention assembly."

There are a few exceptions that you may fall under so worth a shot reading through the section.

Thanks,
Alex

Reply
HJ
10/6/2022 09:21:37 am

NFPA 1 (2018) contains the following:

NFPA 1:13.5.3* The installation of devices to protect the public water supply from contamination shall comply with the provisions of NFPA 13, NFPA 13D,NFPA 13R, NFPA 24, and the plumbing code.

NFPA 1:A.13.5.3 The installation of backflow prevention devices on services supplying water to existing fire protection systems can result in excessive pressure losses. Therefore, installation of backflow prevention devices to protect public health has to be
accomplished with due regard for the implications on fire
protection. The provisions of AWWA M14, Backflow Prevention
and Cross-Connection Control: Recommended Practices, should be used as a guide for determining the appropriate protection for public health. Hydraulic calculations and water supply analysis should be conducted prior to installation to determine the impact on fire protection.

Reply
Brian
10/6/2022 11:33:36 am

The type of system wasn't stated. If this is a dry system then only the single check in addition to the dry riser should be needed. Also is there a fire service main with a pit where the backflow device could already be located?

Often there are limitations to space for revised piping to include such a major modification. Perhaps if a backflow is deemed to be needed then putting outside in a pit could be valuable. You may also find that while evaluating the hydraulics that the underground supply could be undersized with the additional losses. Keep in mind to weigh the costs/ability to perform the modifications to the building versus the site.

Reply
Mark Harris
10/6/2022 12:29:21 pm

Agree that plumbing codes and water suppliers are where you will find the requirements. But think they are trying to conform to the EPA Safe Water Drinking Act of 1974 but as I recall fire sprinkler systems came into play with the 1986 amendments.

Brian mentions single check for dry systems and I have seen that reference over the years but in general think almost all installs today that are off a public water system will get an approved double check or RPZ assembly. I

From a service standpoint never liked the backflow in a pit because of the confined space entry requirements for the annual testing. If RPZ device could be a contamination issue if pit floods.

Reply
James Art
10/12/2022 01:12:44 pm

Backflows Devices are forbidden in CA:
Backflow devices are extremely negative for fire sprinkler systems.
They add friction loss, installation costs, and if properly maintained, ongoing costs, that do not help with fire protection.

And mostly they are unnecessary.
The water in supplied from a water company to the fire system is usually the same water supplied to drink.There is very little evidence that the water is toxic. It does pick up iron in steel pipe, same as in vitamin pills.

In California, the Health and Safety Code clearly states Backflows are NOT required for Class 1 and II systems*, and most water companies, are prohibited from requiring them.
See California Code, Health and Safety Code - HSC § 13114.7

An Excerpt:
(b) Automatic fire sprinkler systems described in subdivision (a) shall not require any backflow protection equipment at the service connection other than required by standards for those systems contained in the publication of the National Fire Protection Association entitled “Installation of Sprinkler Systems” (N.F.P.A. Pamphlet No. 13, 1980 edition).

NFPA 13 is clear then, and now that backflows are NOT required.

Note that many water co. and others just ignore this law!
And each individual is unlikely to fight the system.

*Definitions of Class 1 and II avail. here:
https://codes.findlaw.com/ca/health-and-safety-code/hsc-sect-13114-7.html- Basically with NO cross connections, etc.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top May '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT