What Air Pressure Matches Hydrostatic Test?

6/24/2020

12 Comments

 
We are pressure testing a sprinkler system but there is no water available.

How much air pressure should be used to equal a 200 psi hydro test?

Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments
Mike L
6/24/2020 07:20:12 am

40 psi is typically used for air testing.

NFPA-13 permits interim air tests for certain applications (ie, systems subject to freezing, dry-systems, preaction systems). The parameters are specified in Section 25.2.2 of the 2016 edition.

Assuming all stakeholders (AHJ, ownership, insurance carriers, etc) agree that an air test is acceptable.

Is it that a water source is not available at the time of testing? if that is the case, an interim air test is acceptable. The system will need to be hydrostatically tested once water is available.

Reply
sean
6/24/2020 07:11:56 pm

it also says to go through with water testing when weather or conditions allow

Reply
Dan Wilder
6/24/2020 08:26:25 am

TL:DR - DON'T. Find a garden hose, rent a water truck, but NEVER fill a sprinkler system to 200PSI of air pressure.

PSI is unit of pressure expressed in measure of force over an area (Pounds per square inch in this case). Something exerting 1 pound per square inch is still 1 pound of pressure regardless of what is providing that 1 pound, the difference is the volume needed to exert that pressure (compression).

Lets assume you have a column of water within a 1 cube (1x1x1). The volume of that water (the cube) is ~7.48 gallons (with a gallon weighing ~8.33 pounds). 7.48 x 8.33 = ~62.3 pounds and dividing this by 144 (12"x12" = the base of the cube) gives you ~.433 pounds per square inch...familiar number right? (this is based on gravity providing the compression force in a downward direction)

Air however is much lighter (comes in at ~.0807 pounds per cubic foot) and all things being standard, if you were at sea level, the weight of all the air above you only comes out to ~14.7 PSI (1 atmosphere).

Now this is where I'm going to tell everyone (again) to NEVER use air pressure above the requirements of NFPA. Water is considered uncompressible but air is highly compressible. The compression rate of air per cubic foot to 200PSI is ~13.6x i.e. it takes nearly 14 times the volume of the system to fill with air (within the same space) to bring it to 200 PSI - Boyle's Law equation if you want the longer version. A 500 gallon system (~66.8 Cu Ft) would contain ~909 cubic feet of air under compression so if something were to fail (a cap for instance), it's that release of energy out of a small orifice that becomes the safety issue.

Will the system hold the pressure (200PSI is still 200PSI), possibly, but the safety of your crew and the others on the site alone should far outweigh the need to perform this test with air.

Reply
Jonathan Sullivan
6/24/2020 10:14:08 am

Interesting aside, this is recognized by other model codes such as IPC. Air tests are prohibited for PVC piping, and if an air test is performed on drain and waste piping, it can't exceed 5 PSI, where if a water test were performed on the entire system, multi-story stack pressure could be many times greater.

Reply
Micheal
6/24/2020 10:17:09 am

I too echo the advice the advice. Considerable damage and even death may result from an air test at the pressures mentioned above.

A leak test at very low pressures may be conducted, under tightly controlled conditions.

Reply
HJ
6/24/2020 10:25:14 am

Do NOT pump up that wet system with air, for all the reasons listed by Dan Wilder. Even if you were to pump air into that system, it doesn't count-- you would still have to perform the hydrostatic test afterwards. Wait for your APPROVED water source to become available for your system.

Reply
Jonathan Joseph
6/24/2020 12:18:38 pm

Have the GC supply the water truck. In most contracts this is an Item that usually gets addressed and typically GC is responsible for supplying water for testing when the tap to a city main, private well or pond is not present.

All systems shall be tested with water. Dry systems should be tested with water and then with air since they are reliant on both pressures and like Dan said the difference of compression is extreme.

Reply
Louie Lincoln link
6/24/2020 02:27:46 pm

I could not agree more. When one has a failure with high air pressure it is basically an uncontrolled explosion. This would lead to property damage and possible loss of life. Should chose to do it anyway. Please give advanced notice so that I can arrange to be out of town,

Reply
Cliff S
6/25/2020 10:09:52 am

Word of caution on air testing. Depending on the size of your system and the amount of noise on your project, it could be very difficult to find an air leak.

Reply
Louie Lincoln link
6/29/2020 07:44:08 am

A little bit of peppermint oil in the air intake works wonders in high noise environments .

Reply
Vahe Zohrabian
6/27/2020 12:54:28 pm

Agreed with all points above plus, Viscosity and surface tension of water is greater than that of air, about 89 times, and that viscosity, internal friction of water making it resist the tendency to flow, particularly through a small opening.
So, air can be leaked from pinholes that water would not and excessive presure of air can couse for that pin holes to get bigger and couse real leaks during water test.

Reply
Vahe Zohrabian
6/27/2020 01:00:07 pm

Below you will find more information,

https://www.google.com/search?q=viscosity&rlz=1C1CHBF_enUS877US877&oq=viscosity&aqs=chrome..69i57j0l7.1597j0j7&sourceid=chrome&ie=UTF-8

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT