Wet-Pipe Sprinkler to Circulate Heat/Cool Water?

11/30/2021

12 Comments

 
Is a wet-pipe sprinkler system allowed to be used to circulate water for heating and cooling purposes?

I am designing a wet-pipe sprinkler system under NFPA 13-2019 Edition. 

The building owner would like to use the sprinkler system as part of the building's heating system. I can find this described as "allowed" in NFPA 13-2016, but not in the 2019 Edition.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Pete H
11/30/2021 07:00:57 am

I'm not sure where this is allowed in 2016 edition. I know 2013 edition talks about that situation as a "Circulating Closed-Loop System" in section 7.7 "Automatic Sprinkler Systems with Non-Fire Protection Connections", but that was removed in 2016 (more here: https://www.csemag.com/articles/combining-hvac-fire-suppression-piping/ ).

Can someone show where it's allowed in 2016? It might be easier to figure out where the verbage got moved to in the 2019 revision from that base point.

Reply
Nick Pierce
4/27/2022 11:24:57 am

Can anyone provide a sequence of operations for a closed loop system? More specifically the order of events when a head is opened. Trying to test a system and a water flow alarm is not reporting back to the fire panel.

Reply
Moderator
4/27/2022 11:50:44 am

Hi Nick, to get traction you might consider posting this as a new question here:
https://promote.meyerfire.com/ask

Thanks!

Jared
11/30/2021 08:14:27 am

From the NFPA 13 2019 Handbook. Chapter 8 - "Prior to the 2016 edition, NFPA 13 provided guidance on circulating closed-loop systems. The technical committee on sprinkler system installation decided to remove the language related to circulating closed-loop systems because they were concerned that additional fluids used to extend the life of nonsprinkler system components, such as heating units, chillers, or companion equipment associated with heating, ventilating, and air conditioning (HVAC) systems, might create a compatibility issue with some sprinkler system components. "

Reply
Glenn Berger
11/30/2021 08:15:51 am

In the 2016 version - See 25.3.

This information was move to Chapter 28 in the 2019 version. However I do not see evidence of any allowance for a circulating closed loop systems.

Reply
Franck
11/30/2021 11:23:09 am

At the end of NFPA 13 Edition 2019, there is a table with correspondences of section numbers between 2016 edition and 2019 edition.
There is no correspondence for section 25.3, which means that the use of circuakting closed loop systems have been abandonned.
In the 2019 Edition, there are 2 references for closed loop systems, one is in chapter 30 (Marine Systems) to indicate that "Circulating closed loop systems shall not be permitted", and one is in teh Annex section of 27.1.5 where there are 2 Working Plans for Circulating Closed-Loop Systems. But probably a mistake to remove the drawings as they have not been reproduced in the 2022 Edition.

In the 2022 Edition, the only reference for closed loop systems is in chapter 31.3.4 (Marine Systems) to indicate that "Circulating closed loop systems shall not be permitted".

Reply
Jesse
11/30/2021 08:22:25 am

I'm not a fan. We have several of these tri-water systems our service division attends to. They were pretty popular a few years ago. The concept is defined in 2016 NFPA 13 3.4.2 just as a general concept. Its not disallowed per se. Thankfully in my area they have fallen out of favor

Reply
Franck
11/30/2021 11:30:47 am

In addition to all above comments, I see many possible issues with such systems.
First one is to be sure that all materials used on the heating systems are pressure compliant with the sprinkler system (175 psi ?)
Second, as you will circulate water, eventhough this is a closed circuit, with no introduction of "new water", you may accelerate corrosion issues and spread other problems such as MIC.
Third, any time you need to make maintenance on the heating system, and it should be more frequent that for sprinkler systems, you may need to empty the water in a portion of the system and bring new water + air afterwards = more corrosion potential.

And now, my personal opiinion: a sprinkler system should be used for firefighting purposes only. If you add anything else, you will reduce the overall reliability of the system. And the cost saving at the initial stage can result in a huge amount of money spent afterwards.

Reply
Jack G
11/30/2021 11:49:44 am

Having installed these systems in the 90 s , there are many characteristics you have to follow, to make these things work properly .
1. Pressure rating of fixtures.
2. Sprinkler head temperature- must increase to intermediate temps.
3. Velocity: unlike sprinkler systems, velocity ( creates noise) in this type system— all the time it’s circulating if pipe size is too small—usually you can’t exceed 6-7 FPS in your piping. So your sprinkler system is way oversized.
4. Must check off flow switch to prevent movement.
I did my best to talk engineers out of this, but I did do a dozen or so of these.

Reply
Dan Wilder
11/30/2021 01:20:58 pm

I've only done TI's on these but some issues we ran into in addition to the above comments on design considerations:

Return Bends - the circulating system ended up putting deposits in the existing drops when piped from the side or bottom (as I have never designed one, my assumption is it should be a requirement).

HVAC shutdowns for chemical adding or flushing - this often times ended up taking out the entire system and we had issues with notifications back to the FD & building owner as to impairment with the ITM of the HVAC system.

Draining was a nightmare with the all the loops (HVAC tended to go up over then down vs under and back up) to avoid a low spots for sediment to build up.

Reply
Alex
12/1/2021 10:31:23 am

Hi,

For new construction, I would recommend you stay away. The cost savings would be negligible in the long run and you will have a ton of headaches on system maintenance.

Alex

Reply
sean
12/31/2021 06:37:39 pm

i would recommend against this as the design now has to meet plumbing and fire sprinkler rules

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT