Waterflow, ITD Req'd for Powder Coating Booth?

3/16/2023

5 Comments

 
We have an internal discussion agreeing to disagree, regarding protection of a non-flammable powder coating booth in a tenant building with existing sprinkler system.

We are installing a dedicated auxiliary wet system dropping down with a loop to pick up a valve for an OHII system per NFPA 33 (2016) 9.4.2 (2). Protection Automatic Systems - Powder coating operations.

First Question - Section 9.2.1 and 9.7.1 indicates there must be a means to accomplish all of the following:
  1. (1) Activate a local alarm in the vicinity of the of the spraying operation
  2. (2) Transmit an alarm signal to the facility fire alarm system if such is provided. "In this case yes existing alarm, with existing overhead sprinkler system"
  3. (3) Shut down the coating material delivery system
  4. (4) Shut down all spray application operations
  5. (5) Stop any conveyors into and out of the spray area.

To accomplish the above one side of the office believes a flow switch is needed to accomplish this requirement with double set of contacts.

The other side of the office contends the existing alarm system is adequate enough and if activated the main flow switch will accomplish this. The argument is if this is a dedicated auxiliary system with potential multiple tenants and requires the water flow switch for the Aux Booth System to activate per 9.2.1 and 9.7.1 as noted.

Is this correct?

Question 2 - if a flow switch is required to accomplish 9.2.1 there shall be a means to test with inspector's test connection or a riser manifold with a combination inspector's test & drain at the new dedicated auxiliary riser. Is that correct?

There needs to be an indicating control valve per 9.4.5 operable from floor level for the Aux. Booth System.

Question 3 - can the valve be chained and locked open or does this control valve need electrically supervised open.?

Does there need to be a main drain for this auxiliary system?

I think everyone can follow the arguments so would appreciate some responses. Much appreciated.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments
Anthony
3/16/2023 08:13:02 am

Question 1) you can't use the riser flow switch because of the requirement for a 'local alarm.' The flow switch will provide a 'general' alarm.

Question 2) Means of testing does not a full test and drain (see below)

Question 3) I don't see why not.
Question 3a) not a main drain per se but a means of fully draining the system via an aux valve/Drian. would depend on total volume of the system for proper sizing. I wouldn't think it would have to be hard piped to the exterior.

This sounds similar to elevator (or any small monitored 'sub system') requirements for a flow switch and a tamper switch on a control valve. Generally I'll design in a tee with a capped/plugged ball valve in a continent location so a tester can come by and attach a garden hose or just put a bucket on a ladder and trip the flow switch. I would think this is the easiest and cleanest instillation. Also you have no idea how long the powered coating room will be used, 5 years? 10 years? after the booth life cycle is over with a control valve in place you can remove or alter the piping servicing the booth without removing the primary system from service.

Reply
Todd E Wyatt
3/16/2023 08:48:46 am

The scoping Code (e.g. 2021 IBC) includes the following reference to “PAINT SPRAY BOOTHS” and associated “WATERFLOW SWITCHES” :

2021 Code
Chapter 9 Fire Protection and Life Safety Systems
Section 903 Automatic Sprinkler Systems
903.1 General
Automatic sprinkler systems shall comply with this section.
903.4 Sprinkler System Supervision and Alarms
Valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels and temperatures, critical air pressures and WATERFLOW SWITCHES on all sprinkler systems shall be electrically supervised by a listed fire alarm control unit.
5. Control valves to commercial kitchen hoods, PAINT SPRAY BOOTHS or dip tanks that are sealed or locked in the open position.

NFPA 33 is not a “Referenced Standard” per 2021 IBC Chapter 35 Referenced Standards but it is a “Referenced Publication“ per 2019 NFPA 13 (which is the referenced standard edition per 2021 IBC) :

2019 NFPA 13
Chapter 2 Referenced Publications
2.1 General.
The documents or portions thereof listed in this chapter are referenced within this standard and shall be considered part of the requirements of this document.
2.2 NFPA Publications.
NFPA 33, Standard for Spray Application Using Flammable or Combustible Materials, 2018 edition.

NFPA 33 is referenced (2) times in 2019 NFPA 13 in Chapter 26 Special Occupancy Requirements :

Chapter 26 Special Occupancy Requirements
ENHANCED CONTENT
Sprinkler criteria from other NFPA codes and standards are consolidated in Chapter 26 of NFPA 13 so that sprinkler design and installation criteria for special occupancies can be found in a single location. These other NFPA standards specify certain design requirements for automatic sprinkler systems, and this chapter extracts those requirements and makes reference to the remaining chapters of this standard. In the extracted material, no method for implementing the design information, such as density/area, is given without referencing the remainder of NFPA 13.
To fully understand the criteria in Chapter 26, the user should consult the referenced NFPA standards. The referenced standards provide options for standard sprinkler protection, such as water spray sprinklers, foam-water sprinklers, and other special extinguishing systems, for the protection of the specified hazards.
REORGANIZATION NOTE
This chapter was Chapter 22 in the 2016 edition of NFPA 13. The entire chapter was carried over and sections renumbered to replace the Chapter 22 prefix with the Chapter 24 prefix.

26.4 Spray Application Using Flammable or Combustible Materials.
26.4.1 Design Requirements.
26.4.1.1*
The automatic sprinkler system shall be a wet pipe system, a dry pipe system, a preaction system, or an open-head deluge system, whichever is most appropriate for the portion of the spray operation being protected. [33:9.6.1]
A.26.4.1.1
Subsection 9.6.1 of NFPA 33 lists four types of automatic sprinkler systems and requires that the one “most appropriate for the portion of the spray area being protected” be used. Generally, an open-head deluge system provides the highest level of protection, given that all sprinklers in the protected area flow simultaneously. This type of system is most appropriate for large, downdraft, water-wash spray booths when protecting automatic electrostatic spray application zones. [33:A.‍9.6.1]
Wet pipe automatic sprinkler systems are appropriate for protecting spray booths that utilize nonelectrostatic application processes or operations using listed electrostatic application processes. Wet pipe systems are also generally used to protect exhaust plenums (eliminator or scrubber sections), exhaust ducts, and air recirculation filter houses. [33:A.‍9.6.1]
Dry pipe systems have been included because some exhaust duct designs include sections that are subject to freezing. [33:A.‍9.6.1]
Preaction systems have been included because some spray application processes and equipment can be damaged by unwanted water discharge. This damage can be disruptive and costly. Powder spray booths and solvent concentrator (air pollution abatement) systems are examples of systems where it is appropriate to use a preaction system. [33:A.‍9.6.1]

ENHANCED CONTENT
NFPA 33, Standard for Spray Application Using Flammable or Combustible Materials, requires that a spray area be protected by an automatic fire protection system but not necessarily by a sprinkler system. Other types of systems, such as a dry chemical extinguishing system or a carbon dioxide system, can be used if the building itself is not protected by sprinklers. The usual situation is protection of an individual spray booth in a nonsprinklered building, such as an auto body shop. Such alternative systems might be more effective and more compatible, depending on the material being sprayed. The intent, however, is that a spray application process located in a sprinklered building should also be protected

Reply
Dan Wilder
3/16/2023 09:06:32 am

Not a FA Guy...but we have done several booths, enclosed equip (tire carousels and the like) and small modular mezzanines with aux systems due to the temporary or potential for relocation of the unit so IMO...

A local flow switch with double contacts would seem to be the best way to approach. This provides a local and limited area of impact specific to the booth and associated delivery/application/and material movement systems instead of running into shutting down an entire operational area from a single flow switch in a remote location (pretty much every time a new ITM person/company comes in). This would also potentially provide a contact for a local alarm vs running new wire (possibly conduit) from a remote location.

A commercial riser assembly (or similar fabbed assembly) would be the best when the flow switch is required, nice plug and play. Best practice would be to provide a hard pipes solution for testing discharge, but I've seen these setups with 50-gallon barrels or gondolas to catch water for the test and subsequent draining (not the best but sometimes needed, nearest janitorial sink is also helpful if not the exterior of the building.

This is AHJ dependent. I have one AHJ that has written into their IFC amendments that ANY valve controlling fire sprinklers needs to be electronically monitored and supervised, the AHJ right next to it allows for a chain/lock for control valves.

NFPA 22' - 16.11.6.2 (Indicating Control Valves)
Such valves shall be sealed, locked, or electrically supervised in the open position.

Reply
franck
3/16/2023 10:26:10 am

Dan summarized it well.
No strong requirement for electrical supervision of the valve. It is up to the AHJ. A locked valve is most of the time sufficient (if regular checks are performed) as the valve is normally not located in an easily accessible location (should be close to the ceiling).

Alarm from the main system is not desirable to interlock the stop of operation in the spray booth as a fire (or even a test of the system) may stop the operations and have quite huge consequences on the process.
I did it once on a rolling mill producing very thin metal sheet for razor blades. Activation of the sprinkler alarm stopped the process and cut the steel plate… Not my best souvenir…

And of course, if you have a system with a dedicated flow switch, you need an ITC to test it (how would you know it works ?) and to drain it properly (future modifications /maintenance operations would be difficult otherwise)

Reply
Jesse
3/16/2023 10:46:20 am

I think Dan and Franck summarized it very well. I like the idea of a localized flow switch.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT