We have a small building (less than 47,000 sqft) with basement, ground floor, first floor and roof protected with a sprinkler system. Fire pump room is in the basement.
In NFPA 13-2022, Section 16.9.10.3, there is no need to install floor control valve assembly (no need for sprinkler system either, but client insisted). I've never designed such a small system; and as a result I have a couple questions: (1) Is one flow switch after the fire pump sufficient for all floors? If not, do I need to provide each floor with a flow switch? (2) Is an alarm check valve assembly required? If so, can it be used instead of a waterflow switch, or do we need to install both? Any other tips for a smaller building would be greatly appreciated. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Pete H
9/27/2023 06:44:36 am
One Flow switch and one alarm valve is sufficient provided you don't have further floor control valve assemblies separating them. As you stated there is no need to install a floor control valve assembly, but client insisted.
Reply
JI
9/27/2023 08:17:33 am
1) As per NFPA 13, yes, however local building codes may differ.
Reply
Glenn Berger
9/27/2023 08:20:58 am
1) Is a flow switch required for each floor? Is the 47,000 square foot the total floor area in the building or is that 47,000 square feet per floor? What is this building occupancy?
Reply
Jesse
9/27/2023 08:25:47 am
One flow switch should be sufficient provided your local AHJ doesn't have amendments that require them for each floor.
Reply
Inspector
9/27/2023 09:02:44 am
You must live in a big city if you think 47,000 sq ft is a tiny building LOL. You mention ground floor and first floor...Is this a 2 story building?
Reply
Connor R
9/27/2023 01:55:01 pm
I'm reading this as a building with a basement, 2 stories above grade, and a roof level which are all sprinklered. Is there a rooftop bar or something, or a mechanical penthouse? Do you really mean "roof," or do you mean "attic?"