|
We have a wet system. Inside the system is a walk-in freezer, which has less than 10-ft of rack storage, Class I-III commodities, protected by dry pendent sprinklers from the wet system. Ceiling height is 11'-9".
Using the chart for Miscellaneous Storage up to 12-ft in Height (Table 13.2.1 of NFPA 13, 2016 Edition), thi is to use the design curve for OH2 on Figure 13.2.1. Since the ceiling height is so low, and it's equivalent to an OH2 design curve, there's a request to apply Figure 11.2.3.2.3.1 and reduce the design area within that freezer by 37% and use the smaller hydraulic design area. However, it's not an Ordinary Hazard area, it's a Miscellaneous storage area that is equivalent to an OH2 curve. Are you permitted to use the remote area reduction for Miscellaneous Storage here? Thank you for your time. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
7/25/2023 06:43:46 am
So I think I may have asked this one... and it's one I'm pretty sure I've answered in the mean time:
Reply
Anthony
7/25/2023 08:09:23 am
The system is wet but the drops will have to be dry for the freezer. Does anyone think that would affect the "wet system only" stipulation on 11.2.3.2.3.1?
Reply
Anthony
7/25/2023 08:10:42 am
I'd also note that high temp heads should be used in all freezers so heads don't go off during a defrost cycle.
Reply
Taylor
7/25/2023 08:17:50 am
No, that doesn't change that it is a wet system. Dry sprinklers do not have the same delayed discharge inherent with a dry system.
Reply
Casey Milhorn
7/25/2023 08:17:07 am
I was about to say no until I saw Pete's reply. If you were to read the reduced area section for QR sprinklers (see below) you would have to say no at first. But I'm with Pete on this one, it appears you can. Make sure you are using QR dry pendent sprinklers. Sometimes those can get hard to find in the larger orifice sizes, so make sure the model used does indeed have the QR listing and it's applicable to the spacing and intended use.
Reply
Jesse
7/25/2023 08:31:01 am
I'm confused by the statement
Reply
Pete H
7/25/2023 12:43:17 pm
Similar to the code itself, "ordinary hazard" can be used as a generalized term when it is either ordinary hazard group 1 or 2, and whichever it is isn't actually important to the discussion.
Reply
Dan Wilder
7/25/2023 08:37:56 am
As long as you're not in the 2002 edition (Sept 2010 #4 Tech Notes NFSA), the QR area reduction is applicable and to give Pete some backup. It is not as clear in the more current versions from digging around a bit.
Reply
Franck
7/25/2023 10:05:55 am
Yes you can
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
