Use Normal-Duty, Rated, or Locked-Rotor for Power Demand on Generator?

3/24/2023

3 Comments

 
Thanks for answering my previous questions; I have another one today.

Is the life safety electrical demand on the generator, for the electrical engineer, based on the normal-duty load (346 bhp), motor load (500 bhp), or the maximum locked-rotor road (572 bhp)?

Is there a governing standard that dictates this (IFC/NFPA 20/NFPA 70)?

We have a 2,000 gpm, 185 psi rated electric fire pump. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
Dave Branson
3/24/2023 08:47:11 am

There are several portions of NFPA 20 that address your questions, depending on your specific configuration.

NFPA 20 Para. 9.2.3.4
Where the overcurrent protection permitted by 9.2.3 is installed, the overcurrent protection device shall be rated to carry indefinitely the sum of the locked rotor current of the largest pump motor and the full-load current of all of the other pump motors and accessory equipment.

NFPA 20 Para. 9.6.5.1 says:
Protective devices installed in the fire pump circuits of the on-site generator power source shall allow instantaneous pickup of the full pump room load and shall comply with NFPA 70, Section 700.28.

This should point your electrical engineer to a good starting place.

Reply
Todd E Wyatt
3/24/2023 09:24:57 am

“Duty” is referenced (72) times in 2023 NFPA 70 ... (0) times for “Normal Duty”, “Rated Duty”, and “Locked Duty”.
“Demand” is referenced (74) times in 2023 NFPA 70.
“Load calculations” is referenced (127) times in 2023 NFPA 70.
“Horsepower Ratings” is referenced (33) times in 2023 NFPA 70. As it relates to sizing the generator for the power source of the EES, see the following :

Chapter 4 Equipment for General Use
Article 445 Generators
445.1 Scope.
This article contains installation and other requirements for generators.

ENHANCED CONTENT
Article 445 covers the installation of generators. The following articles cover the use of generators in specific applications:
Article 695 for fire pumps
Article 700 for emergency systems
Article 701 for legally required standby systems
Article 702 for optional standby systems
Article 705 for interconnected electric power production sources
Article 708 for critical operations power systems

445.17 Generator Terminal Housings.
Generator terminal housings shall comply with 430.12. Where a HORSEPOWER rating is required to determine the required minimum size of the generator terminal housing, the full-load current of the generator shall be compared with comparable motors in Table 430.247 through Table 430.250. The higher HORSEPOWER rating of Table 430.247 and Table 430.250 shall be used whenever the generator selection is between two ratings.
Exception: This section shall not apply to generators rated over 600 volts.

The referenced “Article 700 Emergency Systems” states the following :

Article 700 Emergency Systems
Part I. General
700.1 Scope.
This article applies to the electrical safety of the installation, operation, and maintenance of emergency systems consisting of circuits and equipment intended to supply, distribute, and control electricity for illumination, power, or both, to required facilities when the normal electrical supply or system is interrupted.
ENHANCED CONTENT
Emergency systems are designed and installed to maintain a specific level of illumination for means of egress and to provide power for fire alarm systems, fire pumps, automatic doors, and similar equipment if the normal power supply fails.
Article 700 applies to the installation of emergency systems that are essential for safety to human life and are legally required by municipal, state, federal, or other codes or by a governmental agency having jurisdiction. Article 700 does not mandate whether emergency systems are required or where emergency or exit lights should be located. These determinations rely on NFPA 101, Life Safety Code, or the adopted building code. The systems covered by Article 700 are generally viewed as what is necessary for an orderly and safe evacuation from a building or other occupancy type that is required by the applicable codes to be provided with emergency power.
700.4 Capacity and Rating.
(A) Capacity.
An emergency system shall have adequate capacity in accordance with Parts I through IV of Article 220 or by another approved method. The system capacity shall be sufficient for the rapid load changes and transient power and energy requirements associated with any expected loads.
ENHANCED CONTENT
THE EMERGENCY SYSTEM MUST BE DESIGNED WITH ADEQUATE CAPACITY AND RATING TO SAFELY CARRY, AT ONE TIME, THE ENTIRE LOAD CONNECTED TO IT. The system must be capable of restarting emergency loads that have been interrupted, such as motors that may have stopped, and it must be suitable for the available fault current. See also 517.31(D) for the requirement covering acceptable methods to calculate the electrical demand of a hospital’s essential electrical system.

This references 517.31(D) ...

Chapter 5 Special Occupancies
Article 517 Health Care Facilities
517.31 Requirements for the Essential Electrical System.
(D) Capacity of Systems.
The essential electrical system shall have the capacity and rating to meet the maximum actual demand likely to be produced by the connected load.
Feeders shall be sized in accordance with 215.2 and Part III of Article 220. The alternate power source(s) required in 517.30 shall have the CAPACITY AND RATING TO MEET THE DEMAND PRODUCED BY THE LOAD AT ANY GIVEN TIME.
Demand calculations for sizing of the alternate power source(s) shall be based on any of the following:
(1) Prudent demand factors and historical data
(2) Connected load
(3) Feeder calculations
(4) Any combination of the above
The sizing requirements in 700.4 and 701.4 shall not apply to alternate sources.

Reply
Alex
3/24/2023 09:28:57 am

NFPA 20 (Section 9.6.2), the emergency power supply system should be capable of carrying the locked-rotor current of the largest motor and the full-load current of all other connected motors simultaneously. However, this requirement is typically applied to the starting condition of the motors, and once they are up and running, the generator must be sized to handle the actual motor load.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT