|
At a tire store we currently have 25.2K ESFR at the roof, and they have some open grated flooring down at about 10-ft above finished floor where their tire areas are. We are currently protecting the areas that are wider than 4ft.
There are some other runs that are just under 4-ft wide and the AHJ is saying we need to protect those. They're 86% open grates, deeper than 1/4". I'm fine with adding the heads under these, however the AHJ is stating that we must protect below them with ESFR's instead of an intermediate level/rack style sprinkler. I've never seen this approach in 20 years nor can find any justification in the code to support this. The AHJs comments suggest the water shields are necessary to prevent cold soldering from ESFR sprinklers above. Is there a code basis to use intermediate level/rack style sprinklers under obstructions with ESFR at the deck? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
FIREPE25
5/25/2021 08:16:48 am
The open grating is essentially just an obstruction that is over 4'-0" in width. I believe NFPA 13 says that you need to protect under obstructions using the same sprinklers as above. NFPA also says you need shields below open grating. They actually do make certain ESFR sprinklers with guards and shields now that you could potentially use.
Reply
Dan Wilder
5/25/2021 08:54:45 am
In 13-19 Ed.
Reply
I was looking for some information today to pass on to an owner who wants to avoid having to put guardrails around an open grate walkway over a 240'-0 x 10'-0 tunnel/pit below finish floor- the open grate walkway is above at finish floor level. I digress.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
