Use Existing Fire Pump for Higher Foam Demand?

9/17/2020

7 Comments

 
We have scenario where we are using foam system under NFPA 11 for a floating roof tank with Crude Oil.

Based on our previous calculation for a prior tank the fire water demand is 1,926 gpm so we have existing 2,000 gpm pump to be able to supply the required flow. But an additional Crude Oil tank has been added and we have run our new hydraulic calculations and we come up with 4,496 gpm new flow requirement.

Is there a way we can still use the existing fire pump?

​​​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
Dan Wilder
9/17/2020 10:52:38 am

The only way I see this working is if you setup the pumps in parallel. As the old pump works for the original remote area it's a matter of setting the second pump up for the correct "PSI ON" for sequencing along with the correct proportioner requirements

The bigger issue is going to be the suction/discharge/testing/bypass piping of the pumps to take on the additional volume (again, the assumption that the current setup is 10", the new setup would require 16" incoming and 14" discharging for example) per NFPA 20.

I am also assuming this is a municipal/site supply capable of handling the flow demand. If it's pulling from a tank/pond/reservoir those calculations will also need to be reviewed.

Reply
Brad K
9/17/2020 12:42:45 pm

I agree with the above. The suction sizing was my first concern for parallel pumps. Please consider the ID of suction pipe if HDPE pipe in play. This is a common issue.
Also, recommend extensive support from the pump supplier to assure sequencing and piping requirements.

Reply
Jon Dimanlig
9/17/2020 08:02:54 pm

Water source is coming from a Fire water storage tank. We are using a balance pressure pump proportioning foam system.

Reply
anthony brown
9/17/2020 01:39:37 pm

Some questions and some assumptions: I am assuming that this is a Wet System and that it is using low expansion foam. Is the Bladder Tank able to hold capacity, I'm assuming that it is sized for the existing system, and if I am reading your question correctly a new oil storage tank was added and that created the additional loading. final assumption is that you are supplying the system from a Municipal source i.e. "City Water".

Running two pumps drawing form one source will require a 16" supply and a 14" system as already mentioned. Can the supply in the street cover that size pipe and can you buy a 16" BFD? In addition it is likely that you will have to get a new Bladder and hopefully you will have space to place it.

I'm thinking your best bet would to be get the new pump and supply it with new street supplied service. Run your calculations to size the required service. I think when all is said and one it will be a safer, cheaper, and efficient way to go.

Reply
Brett
9/17/2020 02:51:39 pm

What is the reason for simultaneous foam application on the two tanks? What is the separation distance between tanks? Most multi-tank farms are not designed for simultaneous foam application across all tanks. I would recommend speaking with the local AHJ to determine what their requirements will be before proceeding. The local fire departments operational procedures for response to the facility should be taken into account in the design.

Reply
SK
9/17/2020 04:40:04 pm

Certainly your new demand (4496 gpm) can not be met by existing Pump (2000 gpm) if scenario established to needing water/foam in both tanks together. The way I see with limited information which you provided, foam system for both tanks together probably not required in any scenario and other tank may need only water spray. It depends where you are applying foam whether it's for Seal RIM fire (external floating room) or for Dike protection. Please note that foam is ONLY meant to protect from pool fire scenario whether it's on roof or at ground. For Exposure/Cooling protection water spray system is required for adjacent tank (s) if these tanks are located downwind and affected by thermal radiation from "Tank on Fire". So in either the case, if foam applying for one tank, other will need water spray only. Water Spray can be limited to unwetted surface only for nearby tanks. Another scenario for crude tank fire is "Roof Lost Fully Involved Tank Fire" where you can not do anything for the "Tank on Fire" except watching helpless, you need to let that burn but your focus should be shifting to protect other adjacent tank(s) from heat exposure to avoid escalation. It is worth noting that "Roof Lost Fully Involved Tank Fire" is not credible scenario and failure frequencies for such scenario are very rare if tanks are complying API/ANSI requirement. However before I address your concerns more appropriately; appreciate following information;

1. Tanks Sizes (ID and Height)
2. Type of Tanks (whether it's Dome Roof with IFR or External floating Roof, If it's Dome roof, what is the slope angle for roof.
3. Are both tanks placed in same dike or not (this will change your protection philosophy.
4. Prevailing wind direction/Or confirm tanks is affected if there is fire on other tank either on top of roof or in dike.
5 Are these semifixed or fixed foam system Automatically operated.
6. How you getting 4496 gpm, I means what is being expected to operate.

Regards
Sunil

Reply
Mike
9/17/2020 04:42:50 pm

I agree with Brett. Scenarios are based on one fire event. In my experience, if tanks are closer than 1 diameter cooling water is used on adjacent tanks. API 2030 and NFPA 15 are good references along with NFPA 30. Maybe a radiation study would be more revealing in actual risks.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT