Use Drum Drip as Remote Inspector's Test?

11/1/2021

11 Comments

 
Can a drum drip be used as a remote inspector's test for a sprinkler system?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Alex
11/1/2021 06:09:11 am

HI Anonymous,

Do you have a wet or a dry system? If you have a dry system, you are required to provide a drum drip. In addition to your question, I just want to note that you need more than a drum drip, you need a valve normally closed and a site glass.

Joe posted a detailed explanation back in 2017. I recommend giving it a quick read: https://www.meyerfire.com/blog/details-and-requirements-of-the-inspectors-test

Thanks,
Alex

Reply
Dan Wilder
11/1/2021 08:22:29 am

Yep, I do it a lot for odd systems but it typically means running the last branch line low or providing an additional 1" pipe that connects the main to the low point/inspector's test assembly. I will run out the same size branch line through the assembly and keep the discharge that same size.


Making sure you provide the test orifices of the correct size and the valves needed to comply with both an aux drain and an inspector's test and other requirements as Alex linked above. It tends to start looking like Figure 3 in the linked post with larger incoming and outgoing pipe size with the addition of a valve between the last tee and teh tie in to the drain (or discharge to atmosphere) as the construction allows.

Reply
Craig Hanson
11/1/2021 08:45:49 am

No, it cannot. The drum drip comes off the low point of the system for drainage [NFPA 13: 8.16.2.3.5*]. The inspectors test comes off the highest most remote piping [NFPA 13: 8.17.4.2.2]. 2 different animals.

Reply
Jim McHugh link
11/1/2021 09:20:13 am

Craig, What edition of NFPA 13 are you referencing as I looked at 2010, 2013, 2016. 2019 does not have that reference. In each of the prior 3 editions it says in 8.17.4.2.2 "The test connection shall be accessible"

Reply
Craig Hanson
11/1/2021 09:37:21 am

2016:
"8.17.4.2.2 The trip test connection or manifold shall be located on the end of the most distant sprinkler pipe in the upper story and shall be equipped with an accessible shutoff valve and a plug not less than 1 in. (25 mm), of which at least one shall be brass.

Additionally the Hand book commentary explains that the inspectors test connection can be on a drop line but connection should be made at the top of the branch line.

A drum drip is not always at the most remote branch line. It's function is obviously different. The trip test line does not have a drum drip on it as it is out of the top of the piping.

sean
11/6/2021 07:36:21 am

A drum drip is a drain, you can have extra drain that also serves as a test location.

Reply
CJ
11/1/2021 09:43:10 am

I agree with Dan W. I have done that many times as well. Depending on the Fire Marshal they will allow you to combine the exterior discharge line with a site glass or will require two individual lines discharging separately. Always remember the only way this works is if this is the remote end of the system.

Reply
Jim McHugh link
11/1/2021 09:48:36 am

Thanks Craig, turns out I was reading 2 versions of 2013 and not the 2016 book.

Reply
Craig Hanson
11/1/2021 10:08:38 am

I agree with Dan that it is done a lot and accepted by some AHJ's. However, It is not the best way to run an inspectors test and is by code, not the correct way. I was a fitter for years and we always ran separate lines for drains and inspector tests. Granted, we dealt with mostly pipe schedule systems and every bit of help to make the trip test was needed.

Reply
Franck
11/1/2021 04:05:26 pm

As indicated by Craig, it is quite often done… and accepted by some AHJ… but this does mean this is correct.
The purposes are different.
Drum drip is a drainage system and is used to remove as much water / moisture as possible from the piping system. It is located at a low point that is not always representative of the location for the most remote sprinkler.
ITC should be representative of the most remote sprinkler, by the location, as well as the pipe section and orifice opening. This is seldom the case at the drum drip.
Remember the purpose of the ITC for a dry system : not only to check the alarm transmission (as for wet systems) but also the time to have water at the most remote point…
But… it could be acceptable if the drum drip connection to the sprinkler system is the same as for the most remote sprinkler. To be discussed, in that case, with the AHJ.

Reply
sean
11/6/2021 07:37:39 am

I would say you can build your remote test location as a drum drip, but it may not serve as the required aux. drains that are needed.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT