Two Sprinkler Types, RTI, Hazard for Mezzanine?

12/28/2023

9 Comments

 
We have a showroom with an open mezzanine that takes up around 30% of the floor area. The bottom and the top of the mezzanine are office areas. The showroom has a ceiling height of 23-ft while the mezzanine has a ceiling height of 11-ft.

We designed the the showroom as Ordinary Hazard using standard response, extended coverage sprinklers (18' x 18') on the ceiling with the top part of the mezzanine also being protected with standard response, extended coverage. There are no walls on the top side of mezzanine.

On the flip side, we designed the bottom part of the mezzanine using Quick Response, Light Hazard (15' x 15' ) spacing since it's an office (Light Hazard occupancy).

However, since this is an open mezzanine with no walls separating between the two spaces, this means that both these areas would be considered one compartment. Under NFPA 13, sprinklers in the same compartment should be the same response type and hazard levels.

However, would the elevation difference and the mezzanine floor separating the two make it okay to have two different type of hazard level and response type?

If not, what about adding draft curtains?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
R Jackson link
12/28/2023 08:34:34 am

I have never been accused of being smart, but I was taught, whenever possible, (and it is almost ALWAYS possible), to place outlets on mains 12 feet apart and sprinklers 10 feet apart. This uses less mains and more lines. Less mains and more lines=quicker install. Using extended coverage heads, when standard coverage will work, would be less heads, but longer pipes sizes. I am unable to wrap my feeble old brain around this. And yes, when I started designing, it was pencil and paper.
Based on the information given, is it not possible to space the heads like this?

Reply
Anonymous
12/28/2023 08:37:48 am

Is there a reason you cannot use QR EC at the deck and have the same head type throughout?

Reply
Franck
12/28/2023 08:49:28 am

Yes you can have different sprinklers at ceiling than the ones below the mezzanine. It is not good to mix sprinklers at the same level (below the ceiling, for example) as a single fire will operate different sprinklers.
This is not the case with a mezzanine: a fire below the mezzanine will operate the mezzanine’s sprinklers, and a fire not below the mezzanine will operate the ceiling’s sprinklers. So no confusion and no mix. But a draft curtain is necessary (and beneficial) to be sure you will keep the heat plume below the mezzanine and avoid the activation of the ceiling sprinklers.
This situation is not unusual with ESFR protection at ceiling and standard sprinklers below a mezzanine. And again, draft curtain to be provided.

Reply
Pete H
12/28/2023 08:51:45 am

In my opinion, no, you can't mix response types and because it's an open mezzanine, this is the same compartment.

Frankly even with draft curtains, the definition of compartment in NFPA 13 (2016 edition) 3.3.6 reads very specific rules on openings and their sizes and being completely enclosed.

The easiest fix since the ceiling protection is existing would be a 1:1 switch of the heads below the mezzanine for standard response heads.

But this is just my opinion, take with a grain of salt.

Reply
DE
1/2/2024 08:47:58 am

Can't install SR sprinklers in LH unless it's a retrofit.

Agreed with Pete on the compartment definition.

Reply
Jesse
12/28/2023 10:08:57 am

You can mix these sprinklers protecting the ceiling level and below the mezz. We do this a lot in Storage where we have ESFR at the ceiling / deck and K=8 sprinklers below a mezz. area containing picking shelves to 8-feet or so. The picking area is a different hazard class, in this case OH2.

Reply
Fred Walker
12/28/2023 11:06:42 am

Concur with all sprinklers at the ceiling height being the same. Sprinkler below mezz deck may be a type appropriate to the occupancy below the mezz.
Code is not definitive on this so you still have to present the case to the AHJ and get their acceptance.

Reply
Dan Wilder
12/28/2023 12:44:42 pm

Firstly, above the mezzanine is described as office but it's stated that EC SR sprinklers are used? All light hazard areas require quick response (minus some exceptions that do not seem to apply here) so that will need to be addressed.

If the sprinkler is listed as both QR & SR (typically, the SR listing comes into play with the larger spacing and higher density), it would be allowed per 9.4.3.5 to be installed in the same compartment as the other QR sprinklers.

Interestingly enough, I cannot find a specific section on using a draft curtain for separation of response types outside of ESFR, and even then, use of a draft curtain or other means to trap heat is discussed only for a higher hazard design extension into a lower hazard area. The intent seems to be there, just not the language that I can find?

2019 Referenced
3.3.38 - Compartment, walls and a ceiling, lintel may be required based on opening size

9.4.3.1 - QR for light hazard (with exceptions)
9.4.3.2 - QR required within compartment (no exceptions apply)

14.2.5 - For ESFR & draft curtains

19.2.2 - Extension of high hazard

20.6.5.3.1 & 3.2 - ESFR & control mode sprinkler separation within storage

20.10.1 - Adjacent design hazards

Reply
sean
12/31/2023 06:19:19 pm

I think that being in the same compartment no matter the level still has to face the same issue. We don't want to mix different heads as the response times could have heads outside the expected area to activate sooner then over the fire.

Lets think the opposite. if QR at the ceiling would you permit SR heads below the mezz? No it could result in the QR heads activating sooner. There are just too many factors to take into account.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top June '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    NFPA 415
    NFPA 45
    NFPA 495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • PRICING
    • SOFTWARE & TRAINING
    • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT