Treat Plastic Cartons as Expanded Encapsulated?

2/22/2023

10 Comments

 
I have (2) different storage scenarios with the same product. They are empty 5 liter HDPE containers from 2 different manufactures and packaging slightly different but both having cardboard dividers and on wood pallets.

I am leaning towards exposed expanded encapsulated Group "A" on the pallet load without cardboard sides due to the row of containers enclosed in plastic bags.

The pallet load with the cardboard partial sides and full cardboard top would be the same due to having only partial sides.

Any help would be greatly appreciated. 
​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe

​
10 Comments
Dan Wilder
2/22/2023 07:34:13 am

I've done a couple of these for the half gallon/ 1 gallon size containers and went the same route.

Couple items I ran into:

This biggest issue we had was clearance/excessive clearance due to the temp nature and movement of the commodity within the building (post MFG/extruding, staging warehouse, transportation warehouse). This created a couple situations with exceeding maximum clearances (forcing specific storage configuratins) or we had to add additional in rack protection for partially loaded racks. They also like to stack to the maximum height and not provide the minimum clearances (the 3rd picture).

We found some of the bundles were encapsulated (the pallets on the ground in the 4th picture)

The solid piles with collapse potential stacked up to 18', and sometimes a little higher with the pallet heights and containers combined. Each pallet measured over 6' tall so 1 high vs 2 high vs 3 high all had different criteria.

Reply
Dan
2/22/2023 11:21:10 am

Referencing Appendix A.20.4.5.1 13-22 Ed.

Empty Containers Rigid plastic (not including PET), up to 32 oz (1 L) Nonexpanded
Rigid plastic (not including PET), greater than 32 oz (1 L) Expanded

Reply
Dan Wilder
2/22/2023 11:34:38 am

We have not had good luck trying to explain the difference in PET vs non-PET bottles with their characteristics being so similar.

Table A.20.4(b) 13-22' Ed
PET, bottles or jars Class IV
Rigid plastic (not including PET), up to 32 oz. (1 L) Group A Nonexpanded

Reply
Pete H
3/3/2023 12:51:59 pm

The best shot you can have (in my opinion) is if you can find an MSDS or manufacturer sheet referring to the bottles as PET or polyethylene terephthalate and then you can rely on the code to do the heavy lifting for you. But most AHJ's will want some confirmation or substantiation that you specifically have PET plastic as the commodity if you're trying to use the more relaxed coverage allowed for PET plastic.

Franck
3/7/2023 12:59:25 am

PE (or HDPE) is unfortunately not to be considered as PET. Different chemical formula and different behavior.
This is why NFPA introduced the concept of Class A, B and C plastics.

Just like meat.
Chicken and beef are both meat, but they definitely don’t taste the same in my plate ;)

Jesse
2/22/2023 10:17:29 am

I don't see that as "expanded". Expanded Group A Plastic is a foam-like material with quantities of microscopic air-pockets dispersed through the mass. Think acoustical foam, packing peanuts, mattress foam, etc. Expanded Group A is created by a chemical reaction which is exothermal in most cases.

These bottles are likely blow-molded.

Reply
Franck
2/22/2023 12:18:47 pm

Plastic material categorization is quite difficult as very different fire behaviors are associated to each plastic.
Some of them are considered expanded (such as big recipients) because the fire behavior is as for expanded plastic, caused by the amount of air around the plastic.
You can make the analogy with wood. Wood is normally a class III commodity, but wooden pallets is a category of its own because it burns like hell very fast. You need a much higher sprinkler density.

With encapsulation, it is also another phenomenon: you don’t wet adjacent products, because it’s encapsulated, and it will then burn more easily. Take the example of cardboard. Non burning cardboard adjacent to the fire area will be wetted by the sprinklers and will be more difficult to ignite. If encapsulated, it won’t be wet and burn quicker and easier. Thus the increase of commodity when encapsulated.
But encapsulated plastic does not make a difference… It is still plastic.

To come back to plastic materials, Polyethylene does not burn the same way as PET because it has a different chemical organization. Same with PVC. PVC creates problems because of the release of toxic fumes but does not burn as easily as other plastics.
This is why some plastics are classified as Group B or C and are equivalent to class IV or even III commodity.
Group A plastic are by far the worst (they behave like a flammable liquid when they burn), and when exposed you don’t have the wetting effect to the packaging to limit the speed of fire spread.
Worst case is obviously expanded (lot of air for quicker combustion), exposed (no wetted barrier), group A plastic !

Reply
Franck
2/23/2023 01:17:00 am

As a complement, a little bit of chemistry… that sometimes helps to understand how things burn…

A fire is nothing else than a very quick oxidation reaction (with some rare exceptions). This means that the material is oxydized by consumming oxygen and releasing carbon dioxide (CO2), water vapor (H2O) and other subproducts (CO in poor oxygen condition, No, NO2…).
This is why air (oxygen in reality) is one of the key element of the fire tetrahedron.
This being said, polyethylene is the simplest plastic compound with a chain of carbon and hydrogen. This is why it is prone to burn (oxydize) so easily, producing carbon dioxide and water vapor (and some CO because of poor combustion reaction).
With PVC, you have chlorine (Cl) which is s very reactive chemical that will come in competition with oxygen and react with hydrogen (H) to make hydrogen chloride (HCl), thus limiting the combustion process…

Gasoline, coming from crude oil, is also made of carbon chain. And burn easily because easier to vaporize from the liquid form (need less energy). Propane is even worse because it is already in tha gas form.

Wood is also composed of carbon and hydrogen, plus other compounds. It burns well, but less than PE.
Carboard, as paper, is coming from wood but has a higher moisture content than paper and burns less easily (except some coated paper, because of the coating).

Everything is chemistry!

I am pretty sure you won’t see fires the sane way anymore ;)

Reply
Chris
3/6/2023 05:06:50 pm

I was thinking expanded because of the amount of air within the load after reading Franck's comments on an earlier posts.

Whether or not it is actually considered PET is another great question. The MSDS clearly states they are HDPE jugs, the only place I believe I have seen HDPE come up in NFPA 13 is with plastic pallets.

Reply
Dave
10/23/2023 01:12:32 pm

Well I am presented with another twist on this, rack storage of plastic HDPE containers, stacks of pails (buckets) on wood pallets in this case, which per the NFPA annex table and Franck's explanations on this and a similar post, I was considering it non-cartoned, exposed expanded. So protection and storage configurations very limited. I just learned the empty buckets will be pallet stacks of NESTED pails (cardboard to and bottom, shrink-wrapped). So volumes of air are limited to the top level of pails, and the void spaces between each tower of pails. How do I determine if I still meet the threshhold of expanded per Annex Table A.20.4(b) when the buckets are in nested stacks? I'm already having difficulty squaring all this with the definion of Group A Expanded of 20.4.5.3 (2019 ed.)

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT