Thoughts on Sprinklered Gas Station Canopies?

12/3/2021

13 Comments

 
I'm an AHJ and we have a local ordinance, that, when taken literally and applied literally, would require sprinklers in the canopies over gas pumps.

I am wondering if anyone has experience, or opinions, on this type of application and if it even makes sense from a real-life point of view?

I am interested in hearing thoughts and opinions and if there are code references, of course that helps too. Thanks.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Taj
12/3/2021 05:48:47 am

In my experience, I've usually seen this practice in the northeast. A lot of local or state fire codes will require the use of a fire suppression system at a gas dispensing facility, which can get most of there language from NFPA 30A. I have seen in older NFPA 30A editions that there are administrative and engineering controls to implement to not have to install a fire suppression system (i.e. total flooding dry chemical). This usually includes having a "full-service" gas station and of course, emergency shut-off on the gas pump. I have seen AHJ's remove the locking mechanism on the gas pump dispensing handle as a control method. It does make sense from a real life point of view, if there was a fire larger than what a portable extinguisher is capable of handling, this comes into a large effect on the mitigation of fire spread to fuel supply or other sensitive items near the fire.

Reply
RJ
12/3/2021 08:13:21 am

In my humble opinion, what TAJ said above makes sense. But that and $1.00 will get you a cup of coffee. I'm old enough to remember a cup of coffee costing 10 cents. And yes, I really am that old!

Reply
Dan McLuen, PE
12/3/2021 08:18:20 am

I have only seen canopy fire protection required where the canopy is attached to the store. In those cases protection consisted of a deluge sprinkler system arranged to protect the store from a fire involving the pumping area.

Reply
Jon R Corbett link
12/3/2021 08:19:03 am

I've designed and installed fire sprinkler systems in gas station canopies in Rohnert Park and Morgan Hill, California. The link below illustrates what can happen when no fire suppression is present. The hazard can be considered EH 2.

https://contracostaherald.com/vehicle-fire-damages-pleasant-hill-gas-station-thursday-night/

Reply
Glenn Berger
12/3/2021 08:45:42 am

The key here is what use can the fire sprinkler system in the canopy provide?

It will not suppress or control a fire originating from the fuel pump. It can control an event prior to the involvement of the fuel pump assembly.

Information that I would like to know is the size of the canopy, the height above the fueling equipment, is the canopy separated from the store, is there visual and remote fuel cut-offs provided, the number of fueling units provided, etc.

Reply
Tom Mroz link
12/3/2021 09:50:05 am

Common in the northeast, very effective

Reply
Alex
12/3/2021 11:12:46 am

Agreed. I haven’t seen a station in the northeast without protection.

Sadly I have no experience with this type of design and cannot provide code sections. Best of luck!

Alex

Reply
Chris Sampson
4/9/2026 12:28:29 pm

I have been a Sunoco dealer in Massachusetts. And have seen first hand the effectiveness of automatic fire suppression, getting the customers away from their vehicles safely . In combination with the electrical shut off. You definitely need both

Joshua Freedman
12/3/2021 11:18:08 am

I am in the Southwest and only occasionally see this arrangement and when I do, it is only exposure type sprinkler layout around the border of the canopy to prevent spread to the store if it is close, connected, or also under the canopy; or, to protect a nearby structure. I think I have seen the deluge exposure design approach really only designed for life safety considerations.

Reply
Dan Wilder
12/3/2021 11:23:08 am

Being from a warm city (Phoenix), our protected canopies just utilize a wet system most times (but we have buried a dry valve inside a built out column in some cases). My opinion on them is the ability for other cars to leave the area is better than having a canopy full of cars go up and you get dilution of the burning fluids, typically to a point where combustion is no longer viable away from the source. The car/truck on fire is typically lost just due to the shielding the frame provides but the adjacent equipment and structure of the canopy remains.

Our AHJ's have mostly amended in gas canopies as "Fuel Dispensing Overhangs" and require sprinklers in most cases.

Reply
sean
12/13/2021 12:52:50 pm

Never seen it done around me.

The type of fire/explosion that would take place I don't think is well suited for fire sprinkler. If anything a dry chemical agent may be more applicable.

Reply
Chris Sampson
4/9/2026 12:30:29 pm

Dry chemicals are the only thing that work

Reply
gas station sign link
11/5/2023 10:13:38 am

Useful submit! I really want this sort of article.. that is very beneficial for me.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT