Tap Fire Supply for Water Source Heat Pump?

9/1/2021

8 Comments

 
We are working on a project where the site engineer is asking if tapping into the underground fire line is acceptable to supply a water cooling line to a water source heat pump unit with a 3-inch line.

I'm having trouble finding where it is not acceptable and thought I'd reach out to the knowledgeable members here.

This site has a combination potable/fire line as shown in the picture below.

Should we require them to tie into the 8-inch tap from the potable water line upstream of the fire protection vault (blue line in the drawing)?

Or is it OK that they tap into the fire supply line downstream of the fire protection vault (red line below)?

Picture
​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Franck
9/1/2021 08:38:33 am

To my understanding, it would be (more or less) the same as having a process water supply as a fire protection water supply.
It makes no difference if you take the water before or after as it is the same supply to both your systems.
You just have to be sure that the available water supply at the end is still sufficient to meet your requirements for the fire protection systems - the most demanding ones (with some safety margin).

You just have to be sure that a technical impairment on your "process line" will not impair your fire protection system.

But this is a personal technical point of view, I am not an AHJ (even though I would accept it for the locations we do insure if all other reliability topics are ensured).

Reply
Glenn Berger
9/1/2021 08:39:19 am

You will not find any prohibitions from a fire protection standpoint. This is strictly a local jurisdiction item.

The typical issue here is if the building service is metered and the fire water service is not metered or is there a differing requirement for backflow prevention. Some Water Source Heat Pump Systems do require chemical treatment systems.

Reply
Alex
9/1/2021 09:06:09 am

Hi Anonymous,

Is this for commercial or residential?

The IPC (Internal Plumbing Code) 608.17.4 Connections to automatic fire sprinkler systems and standpipe systems, mentioned a combined system. It states that a system that “are not provided with a fire department connection” does not require isolation of the water supply system.

Therefor, if you have an FDC, you will need to protect your sprinkler system with its own backflow assembly.

If you aren’t getting pushback on connecting after your vault, I would recommend connecting upstream to avoid any complications.

Thanks,
Alex

Reply
John G
9/1/2021 09:09:04 am

I don’t believe your picture is indicative of your proposed design for a combined closed loop , circulating, heat pump/fire sprinkler system. ( section was removed temporarily in 2016 edition of 13)
#1. System design Should be a Closed loop system.
#2. The Temperature of sprinklers in the system must be increased due to delta heat gain of the circulating water.
#3. Your sprinkler system hydraulics/ pipe sizes will INCREASE, as the velocity in the piping, including your branch lines must be below certain velocities, so EXCESSIVE NOISE is not produced in the circulating water. Maximum velocities are usually 4 to 6 feet per second. Otherwise buku noise. This dramatically increases the cost of the fire system.
My opinion…… a very expensive and poor choice.
Better off with a geothermal heat pump with 2 wells.

Reply
Casey Milhorn
9/1/2021 09:33:43 am

More of a local water department issue in my eyes. Typically I see double detector check valve assemblies in most jurisdictions for dedicated fire lines. So could be a couple issues here. I would assume that the water department would want a reduced pressure backflow for any potable water connection like this, even though it is more for process piping. Additionally as someone mentioned, you are probably either unmetered (DCVA) or more likely, metered (DDCVA) but they are not meant for accurate continuous water usage. They are more to detect out of the ordinary water usage. By the fact that you show a vault, that means more than likely you don't already have a RPDCVA or RPDDCVA. Some other issues I can think of would be maintenance related or pressure related. If/when the fire protection backflow is being tested/repaired/forward flushed you will lose supply to the heat pump (or any other impairment to the fire line). You could also have an issue if the FDC is not isolated from heat pump, so during pressurization could cause issues to pump.

Reply
Greg
9/1/2021 12:58:02 pm

Has the water utility performed a study or engineering assessment that identified this (new) use? Their understanding of water use, pressures, backflow, etc. is aligned with your design objectives, as the end user of the water, as a customer. Can you lean on their studies (or commission a study) to help bolster the confidence of the sprinkler design, both now and future expectations of heat pumps as a demand on the water utility.

Reply
calvinsclimate link
3/15/2022 04:44:05 am

Automatic sprinklers are the most reliable and effective fire protection devices available today provided they operate correctly. To determine if a sprinkler system can adequately protect a property, underwriters should be familiar with the components, operation, and testing of the systems, as well as potential causes for failure.

Reply
callsmoothsailing link
7/22/2022 08:54:45 am

Heat pumps come with multiple advantages for your home. Pumping the heat uses less electricity as compared to when electricity is solely used as a means to convert it. During the summers, the cycle can be reversed and the unit acts like an air conditioner.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT