MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Standpipes Required for Open Exterior Stair?

2/1/2023

7 Comments

 
Do open (exterior) stairs need standpipes?

If the stairs are more than 50% open, sprinkler protection is not required but what about standpipes?

This building has three stairways. Two are interior and one is open and on the exterior. Standpipes are provided in the two interior stairways.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Anthony
2/1/2023 08:00:56 am

IF the stair is considered a required exit you'll have to provide a standpipe and hose connections. This information can be found on your G series aka life safety or code compliance documents.

NFPA 14-16
7.4 Number of Standpipes. Separate standpipes shall be provided in each required exit stairway.

Reply
Chuck R
2/1/2023 08:24:55 am

The prescriptive locations and charging language (code requirement) comes from the adopted code within the jurisdiction of the project (i.e. IBC, IFC, NFPA 1, NFPA 5000, NFPA 101).
NFPA 14 is the standard that describes how standpipes are to be installed when the "code" indicates they are required.
For example: 2018 IBC 905.3 Required Installations. A Class III standpipe system shall be installed throughout buildings 4 or more stories above or below grade plane. Exception Class I standpipes are allowed in buildings equipped throughout with an automatic sprinkler system...
NFPA 14 7.3 will how and where Class I and Class III systems shall be installed.
FYI - IBC 102.4 Referenced codes and standards.
Where conflicts occur between provisions of this code and referenced codes and standards, the provisions of this code shall apply.
NFPA 14 section 7.4 is only applicable when the CODE requires a standpipe to be installed. 2 & 3 story buildings and their respective exit stairways will not require standpipe installations.

Reply
Todd E Wyatt
2/1/2023 08:29:29 am

ANSWER
Class I Standpipes are required in “every interior exit stairway” but are not required in “exterior exit stairways” by the scoping Code (e.g. 2021 IBC).

EXPLANATION
The adopted scoping Code (2021 IBC) is to be evaluated first ... Chapter 9 Fire Protection and Life Safety Systems, Section 905 Standpipe Systems ... to determine WHERE standpipes are required ...

905.3 Required Installations
Standpipe systems shall be installed where required by Sections 905.3.1 through 905.3.8. Standpipe systems are allowed to be combined with automatic sprinkler systems.
905.3.1 Height
905.3.2 Group A
905.3.3 Covered and Open Mall Buildings
905.3.4 Stages
905.3.5 Underground Buildings
905.3.6 Helistops and Heliports
905.3.7 Marinas and Boatyards
905.3.8 Landscaped Roofs

We’ll assume based on one of these required applications (e.g. Height ... Four or more stories are above or below grade plane.) that a standpipe system IS required.

The next step is to determine the WHERE in the building the standpipe system is required ...

905.4 Location of Class I Standpipe Hose Connections
Class I standpipe hose connections shall be provided in all of the following locations:
1. In every required interior exit stairway ...
2. On each side of the wall adjacent to the exit opening of a horizontal exit ...
3. In every exit passageway, at the entrance from the exit passageway to other areas of a building ...
4. In covered mall buildings, adjacent to each exterior public entrance ...
5. Where the roof has a slope less than 4 units vertical in 12 units horizontal ...
6. Where the most remote portion of a nonsprinklered floor or story is more than 150 feet (45 720 mm) from a hose connection ...

#1 “interior exit stairway” (IES) is applicable to your question ... IES is italicized so this means it is defined :

INTERIOR EXIT STAIRWAY. An exit component that serves to meet one or more means of egress design requirements, such as required number of exits or exit access travel distance, and provides for a protected path of egress travel to the exit discharge or public way.

Section 905 Standpipe Systems does not reference “exterior exit stairways” (EES) ...

EXTERIOR EXIT STAIRWAY. An exit component that serves to meet one or more means of egress design requirements, such as required number of exits or exit access travel distance, and is open to yards, courts or public ways.

... so a standpipe system is NOT required in EES. To determine IF this “EES” is actually a compliant EES, refer to Section 1027 Exterior Exit Stairways and Ramps :

1027.2 Use in a Means of Egress
1027.3 Open Side
Exterior exit stairways and ramps serving as an element of a required means of egress shall be open on not less than one side, except for required structural columns, beams, handrails and guards. An open side shall have not less than 35 square feet (3.3 m2) of aggregate open area adjacent to each floor level and the level of each intermediate landing. The required open area shall be located not less than 42 inches (1067 mm) above the adjacent floor or landing level.
1027.4 Side Yards
1027.5 Location
1027.6 Exterior Exit Stairway and Ramp Protection

Lastly, the scoping Code (2021 IBC) references the applicable standard (NFPA 14, 2019 edition) for the installation of Standpipe Systems ...

905.2 Installation Standard
Standpipe systems shall be installed in accordance with this section and NFPA 14.

... but this reference standard does not determine WHERE Standpipe Systems are to be installed, simply HOW.

Reply
Dan Wilder
2/1/2023 08:42:34 am

There will likely be some Building/Fire code reference that will help on this because I was on the side of "If it's an exit stairwell (typically shown on the Life Safety Sheets as an egress point with occupant load) then it's required to have a standpipe"....

but looking through the IBC/IFC, there is no mention of Exterior stairs and standpipe requirements in the 905 section....but if these are considered horizontal exits or the interior stair hose valves don't reach to that corner, an additional standpipe (or at least additional hose valves) would be required so it kind of defaults to being required in the end.....looks like a learning day

(IBC 2015/2018)905.4 Location of Class I standpipe hose connections.
Class I standpipe hose connections shall be provided in all of
the following locations:
1. In every required interior exit stairway, a hose connection
shall be provided for each story above and below
grade plane. Hose connections shall be located at an
intermediate landing between stories, unless otherwise
approved by the fire code official.

Reply
David Williams
2/1/2023 10:03:07 am

We have a historic building renovation job on Navy property where NAVFAC wants manual exterior dry standpipes (supervised with N2) on new exterior exit stairs, similar to what was there since the 50’s. Keeps the project from adding additional interior stairwells while providing Fire Service access to the upper floors.

Reply
Chuck R
2/1/2023 10:09:28 am

The last response quoting IBC/IFC905.4 is the correct iteration of that code section that indicates where CLASS I standpipes are to be located, but...
Prior to quoting section 905.4 the code has to require the installation of standpipes to begin with. And that beginning is section 905.3-Standpipe systems shall be installed where required by Sections 905.3.1 through 905.3.8, then you proceed into the remainder of Section 905 to determine where Class I, II, or III standpipe systems are to be located.

Reply
James Stever link
2/1/2023 12:35:34 pm

Recommend to contact local fire department to if having the standpipe in the open air stair would be a tactical advantage to fire ground operations. Interior stairwells can impede fire department access when both stairwells are used for exiting.

What code edition of the ICC are you using and it associated reference date of NFPA 14?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT