MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Standpipe Required In-Between Far-Apart Stairs?

10/17/2022

14 Comments

 
I am reviewing a set of fire suppression drawings from another engineer that is working as a sub to the sprinkler contractor. We created an outline of the fire suppression requirements (a performance spec) and then the contractor hired another engineer to finish the design.

The building is a 6-story wood frame residential project.

There are two exit stairs each with a Class I Standpipe and 2.5-inch fire hose connection (FHC).

The building is an 'L' shape and the total travel distance from one FHC to the other is approximately 300-ft (91m).

There is a 2-hour fire-resistance-rated wall part way along the corridor (124-ft from one FHC, 174-ft from the other).

The contractor's engineer is calling for an additional third standpipe next to the 2-hour rated wall - is this required or not?

I'm not sure how to interpret Sections 7.3.2.3 and 7.3.2.3.1 of NFPA-14. The project is in BC, Canada; and we're using NFPA-14 (2013 Edition). I have attached a markup of a typical floor plan.
Picture
Thanks in advance!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
Dan Wilder
10/17/2022 08:04:12 am

Based on the picture alone, first thought is that the center stair (likely an exit stair) is missing a required hose valve per Section 7.3.2 (1). With that location having a valve, you might be able to omit the third HVC on the floor.

If the 2 locations on the "legs" of the "L" are accurate, then yes, a third HVC would be needed based on the distances shown.

Every layout I have completed is based on 100' of hose lay (including any elevation changes up from a midlevel vs main level stair landing) and 30' of hose spray. This means the hose nozzle at the end of the 100' needs to pretty much be at the door into the last/furthest room on each level and hopefully the room is no deeper than 30'. We start with the required locations (the Exit stairs) and add additional locations for the areas lacking coverage.

Reply
Corey Eppinghaus
10/17/2022 08:10:27 am

The BC building code will have requirements for placement and coverage please see below.


3.2.5.9. Standpipe System Design
1) Except as provided in Sentences (2) to (6), Articles 3.2.5.10. and 3.2.5.11., and Sentence 3.2.4.9.(2), the
design, construction, installation and testing of a standpipe system shall conform to NFPA 14, “Installation of
Standpipe and Hose Systems.”


3.2.5.10. Hose Connections
1) Hose connections shall be located in exits, in accordance with NFPA 14, “Installation of Standpipe and
Hose Systems.”
2) Hose connections are not required within a floor area.
3) Hose connections shall be provided with sufficient clearance to permit the use of a standard fire department
hose key.
4) Except as permitted by Sentence (5), 64 mm diam hose connections shall be installed in a standpipe system.
5) Hose connections for 64 mm diam hose are not required in a building that is not more than 25 m high,
measured between grade and the ceiling level of the top storey and in which an automatic sprinkler system is not
installed.


3.2.5.11. Hose Stations
1) Hose stations for 38 mm diam hose shall be installed for a standpipe system in a building that is not
sprinklered throughout.
2) Hose stations for a 38 mm diam hose shall be installed for a standpipe system within every floor area that is
not sprinklered throughout. (See Note A-3.2.5.11.(2).)
3) Hose stations shall be located in the floor area within 5 m of exits and at other locations to provide coverage of
the entire floor area.
4) A hose station located on one side of a horizontal exit shall be considered to serve only the floor area on that
side of the horizontal exit.
5) A hose cabinet shall be located so that its door, when fully opened, will not obstruct the required width of a
means of egress.
6) Where a building or part thereof is used as a distillery and the building is sprinklered in conformance with
Article 3.2.5.12., small hose (38 mm) stations are permitted to be supplied from interior sprinkler piping.
7) Where a hose station is provided in grain handling and storage facilities in which combustible dusts are
produced in quantities or concentrations that create an explosion or fire hazard, fog and fine spray nozzles shall be
used instead of nozzles that discharge a solid stream of water to prevent combustible dusts from being raised into
suspension.

Reply
Glenn Berger
10/17/2022 08:13:20 am

The drawimg is not marked correctly. The 124' and the 174' needs to identify the distance that it is measuring. In this case it is the top/bottom dimension and then the left/right dimension.

I assume that at the plan left side is an exit stair for which the FHV is located. It is not marked. As Dan mentions, is the stair near the ben an exit stair, for which a FHV needs to be located?

Three hundred feet between FHV is excessive and needs an intermediate valve.

Reply
Moderator
10/17/2022 08:45:46 am

Just updated the image, refresh to see it. Stairs are now marked correctly, thank you Glenn!

Reply
Jesse
10/17/2022 08:13:28 am

I agree with Dan. Looks like the center stair is missing hose valves. Is that a stairwell on the end?

Reply
Moderator
10/17/2022 08:45:22 am

Good questions - just updated the sketch with labels and marked "Stair 1" so it shows more clearly. Yes, there are three stairs. Thanks Jesse.

Reply
Tim
10/17/2022 08:23:35 am

Without looking at coverage from an operational firefighting point of view FHC should always be placed close as possible to stairs. The stairs are the entering or access point for firefighters and rescue personnel. On multi storey buildings you never enter fire floor without charged water line and your escape is always planed back to stair. By instinct and training firefighters will seek the FHC at stairs.

Tim

Reply
Alex
10/17/2022 08:58:38 am

Hi,

Within the question, you mention a 2-hour fire-resistance-rated wall. I don't believe this is shown on the drawing. Is this a horizontal separation? What is the purpose of the wall. If you have a horizontal exit, a hose valve is required (NFPA 14 7.3.2).

Thanks

Reply
Jessica
10/17/2022 01:25:38 pm

See Corey's comments. Section 3.2.5.10 (2) of the BC code. Hose connections are not required within a floor area. I have done residential buildings in BC recently and got push back from the client when we showed hose valves outside of the stairs.

Reply
SCHULMAN
10/18/2022 07:11:05 am

EVER TRIED TO CARRY MORE THAN 100' OF FIRE HOSE ?

Reply
Brian H
5/9/2025 01:40:11 pm

Have you ever followed a hose line out of a burning building only to end up in the middle of the corridor?

Reply
James Art, Ca FPE
10/19/2022 11:18:34 am

Looks like that 3rd stair is missing a standpipe.
And some codes want a standpipe outlet near the Horizontal Separation.

Sure Glad that ugly BC code is NOT used here.
Omitting the Standpipe for buildings below 25 meters (about 82 feet) would mean fire fighters need to manually carry hose up the stairs, prop stair doors open, then charge the hoses, and eventually put water on the fire.
Anyone trying to exit from above a fire would need to pass an open fire door.

Normally buildings need standpipes when 4 stories or more.

Often firefighters tie in to the floor below, or at the intermediate landing,if the outlet is there. That way if when they open the door, they have some distance from the fire, and can control the valves more safely.

Read all about it:
Here's a link to a recent fire in Oakland, Ca where the standpipe failed, 401 Santa Clara, 10/17/22

https://mng-prod.auth0.com/login?state=hKFo2SBVcFFwa3VoMzFoRXZfNzA5VEtpRy03bjdZd0NfR3RlWKFupWxvZ2luo3RpZNkgcXRjUFhnb1FoSHNlTmVuaFpUa1ZKRUN1WEg4Sk9wVEqjY2lk2SBoN1Y0TWdkcldMYnAxbHkySXVvOTg3akNyczA1T0FmTQ&client=h7V4MgdrWLbp1ly2Iuo987jCrs05OAfM&protocol=oauth2&response_type=id_token%20token&response_mode=form_post&redirect_uri=https%3A%2F%2Factivate.mercurynews.com%2Fgateway%2Fgeneric.aspx%3Fpbid%3D704bc66e-2c99-475b-83aa-c7f296287203&scope=openid%20profile%20email&nonce=032bd54e-f53c-493b-9953-beaad077a65a

The News reports problems,sometimes accurately,
, but rarely follow up with the WWW:
What Went Wrong?

Please post or let me know if anyone sees more about that fire!!
THANKS.
Jim
Former FPE for City of Oakland

Reply
Casey Milhorn
10/20/2022 06:53:35 pm

I'm not sure how this particular Canadian code works, but typically here in the states, IBC requires either no standpipes, Class I, or Class III standpipes, depending on the height of the building. From there NFPA 14 tells you that standpipes must be located in every required exit stairwell (not convenience or strictly ornamental stairwells). From what I understand, the travel distance in IBC matches hose lay now in most cases. Which typically means no need for additional hose stations or standpipes. Code typically tells you when something is required, standards tell you how to do it and where to place them.

Reply
Thomas Duross
10/25/2022 05:08:03 pm

I would think a third standpipe required in Stair 2. Depending on your building code in use, if the building is fully sprinklered the travel distance is extended from 100' to 200'.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT