Standpipe Req'd, Supply Size for Small Building?

6/6/2022

12 Comments

 
According to the International Building Code Section 905.3 (2018 Edition), a standpipe is required in any building with four or more stories.

We have a small building (three family homes) but the first floor is all a parking garage, and then 3 more floors over the parking garage (one home per floor).

According to the IBC, do we still need a standpipe even if it's such a small building?

If we do need a standpipe, does the service have to be 4-inches or can we have it at 2-inches and increase the riser up to 4-inches to feed the manual wet standpipe?

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments
Alex
6/6/2022 07:04:10 am

Hi,

IBC (2018) 905.3.1 outlines the maximum height until standpipes are required.

You are correct, if you have four or more stories, your building requires standpipes. Although, the code goes on to read if the floor of the height story is located more than 30 feet above the lowest level of fire department access, you also require standpipes. My guess, from your question, is that you will exceed 30 feet.

NFPA 14 7.6.1 states that for a Class III standpipe, the minimum diameter is 4 inches. NOW, you have me thinking. Where does the standpipe system "start"? Is it after your backflow? At the first flange in the building? What if your service is 2 inches, you install a reducer to get to 4". Then go through your backflow? I dont see any issues with that as long as all hydraulic calculations work and are done accurately. What are others thoughts on this?

Thanks
Alex

Reply
Pete H
6/6/2022 07:37:26 am

I'm inclined to agree with Alex, you need the standpipe (you got four stories). And to continue to agree, you can probably get away with the 2" service that increases to 4" at the riser (so after the backflow) provided you can make the mandatory calculations work.

However, the 2" Backflow and service will make it a lot harder to make those calculations work without an extremely fortunate water supply. So good luck.

Reply
Anthony
6/6/2022 08:56:27 am

No calculations required, It would be a manual standpipe system, assuming there is a sprinkler system. The 2'' backflow it a sprinkler problem, not a standpipe problem.

Reply
Alex
6/6/2022 01:19:07 pm

Anthony,

I still calculate manual standpipes. Determine what flow/pressure the local Fire Department Engines can provide and ensure that your pipe sizes work.

In my opinion, calculations for everything should be required. They are so simple to provide and ensure the design actually works.

Alex

Todd E Wyatt
6/6/2022 08:49:05 am

The first step in evaluating fire protection requirements is to identify the Occupancy Classifications (OC) of the building. You state that the building includes "three family homes" which could be classified as Group R-2 Residential. (Standpipes are not required in R-3 occupancies).

As Alex has identified, there are (3) building height/stories conditions that require Class III standpipes but (6) exceptions to these requirements. "Section 905 Standpipe Systems" then goes on to identifiy individual requirements based on the Occupancy Classifications (e.g. Group A) and/or special conditions (e.g. Underground buildings).

Once you determine IF a standpipe system is required based on building height and/or OC/special conditions, the next step is to determine where Class I, II, and III standpipes are to be located. In your case, the standpipes' locations may be different for the Group S-2 Low-Hazard Storage (parking garage) portion and the Group R Residential portion.

Reply
M. Newell
6/6/2022 08:49:23 am

I think it largely depends on the occupancy above your parking garage.

If it is an R-3 the IBC does not require it to have a standpipe even if over 30’ above FD access.

If it is not an R-3 then when you are over 30’ you would likely need to have a standpipe.

You could likely look into a manual standpipe if needed and if allowed per your local codes. This would allow you to size your standpipe from the supply of a fire fighter apparatus and eliminate the potential need for a fire pump.

Then you would need your standpipe to come off the end of your system similar to an end of system FDC.

Reply
Dan Wilder
6/6/2022 08:58:56 am

Points of clarification:

Is the garage for the units specifically or is it publicly accessible?
Is the building over 60' tall? (the top of roof, not highest occupiable floor)

The design (assumption) is based on a 13R approach to the standpipes as a manual wet, 4" minimum sizing and FDC.

NFPA 14 A.6.3.4.5 has a little bit stating: "...common scenario is to connect the system to the potable water system (the automatic water supply for sprinklers & hence a likely back flow requirement)...There is no minimum size requirement for this connection."

The standpipe start point (in my mind) needs to be identified as from the location of the FDC to the feed main to the standpipe(s). The automatic water supply location feed to wherever it ties into the standpipe can be sized per calculations and would not be required to be up sized to the minimum.

The best visual aid I can find is NFPA 14 19' Ed Figure A7.10.1.1.6 for the riser and FDC being separately located but tie into each other. Those pipe sizes can be different up until that tie in point, then the larger requirement (the 4" or whatever the calc shows is needed) overrides the automatic source sizing.

Reply
Todd E Wyatt
6/6/2022 10:01:02 am

2021 IBC

905.3 Required Installations
Standpipe systems shall be installed where required by Sections 905.3.1 through 905.3.8. Standpipe systems are allowed to be combined with automatic sprinkler systems.

Exception: Standpipe systems are not required in Group R-3 occupancies.


[F] 905.3.1 Height
Class III standpipe systems shall be installed throughout buildings where any of the following conditions exist:
1. Four or more stories are above or below grade plane.
2. The floor level of the highest story is located more than 30 feet (9144 mm) above the lowest level of fire department vehicle access.
3. The floor level of the lowest story is located more than 30 feet (9144 mm) below the highest level of fire department vehicle access.

Reply
Dan Wilder
6/6/2022 11:04:40 am

My request was not to remove the standpipe requirement but identify if a 13R system is even the correct application. If the building goes to a full 13 due to the height of the building, a 2" domestic water feed isn't going to cut it.

I recently had a 3 story building, as identified within the local predesign IBC/IFC, which had 22' between floors. The setup was similar to a loft style with the front living area & windows being the full height of the floor and the back area having the bedrooms and bath on a "mezzanine" over the kitchen and lower RR/closets/entry. The building initially was designed as being sprinklered per 13R (multiple units) in plan review with the Building Department, but the height of the building required a full 13 system once the fire department saw the plans. Required a full redesign once they (the arch) lost the appeal and the owner didn't want to lose floor heights.

Ed Kramer
6/6/2022 11:33:07 am

Designed a project a few years ago that required a manual wet Class I standpipe. The standpipe system (from the most remote hose valve to the FDC) was sized via hydraulically calculations. Most of the standpipe system was 4" with some of the common supply pipe near the FDC as 6". I don't recall the reasoning, but we chose to run a separate vertical supply for the sprinkler system, so the standpipe was standpipe only - not a combined system. To make the standpipe 'wet', we connected it to the sprinkler system riser using 1" pipe.

Reply
Jesse
6/6/2022 02:44:11 pm

Its not stories, per se. But rather vertical distance of the occupiable floors above lowest level of fire apparatus access. I actually have a 4 story hotel right now with the 4th floor 28-6 above the fire lane so it has no standpipe. Likewise, I had a 3 sto prior that did.

And I always calculate manual standpipes.

Reply
Menachem D
9/4/2023 02:36:32 pm

I am working on an R-2 multi-family house three stories + underground basement + Attic.
Fire department access to eave 29’-8” Top of plate attic floor +30’ (30’8”) Attic is unfinished, but stairs, heated, and lights are in place. (It might be used in the future for a big playroom or…)
Are standpipe systems required?

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '25 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    Nfpa-409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE 100-Day Marathon
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT