Standard Spray Allowed in NFPA 13R Design?

3/20/2023

8 Comments

 
Can non-residential sprinklers be used in a NFPA 13R design?

NFPA 13R lists that residential sprinklers are permitted for use but does not list they are required to be used.

My understanding is that sprinklers used in NFPA 13 for light hazard would exceed or meet sprinkler requirements within NFPA 13R

On this premise, would installing a sprinkler for light hazard occupancy be exceeding NFPA 13R minimums, and thus be acceptable?

We have a dry sprinkler system we are installing in a small existing dormitory built with combustible construction.

We are using a NFPA 13R design approach which avoids sprinklering the attic space, with local AHJ approval. We need to have concealed sprinklers under request of the owner based on the occupancy, but there are not residential concealed dry pendent sprinklers, and the contractor is pushing to install recessed dry residential sprinklers.

Thanks in advance.

​
8 Comments
Anthony
3/20/2023 08:04:11 am

No you cant use standard response standard heads.
yes you can use quick response standard heads.

IF you use QR standard spray sprinkler you must use the design basis of NFPA 13. That would require a MINIMUM 900 sqft light hazard design. Assuming you're talking about inside the dwelling unit.

NFPA 13R-2016:
7.1.2 Quick-Response Sprinklers. Where quick-response
sprinklers are used in accordance with 6.2.1.3, the discharge
and design area requirements of NFPA 13 shall apply.

Key phrase here is "design area requirements of NFPA 13."

You cannot apply a 4 head residential sprinkler calculation to non-residential sprinklers.

Note: Residential sprinkler are designed and fire tested to operate with a special listing making them more effective for the smaller broken up and compartmentalized environment of a residential occupancy as compared to the larger open areas that standard spray sprinkler protect. They offer a flatter spray pattern with the objective of wetting walls to contain a fire to a single compartment allowing for residents to evacuate.

see the discussion of ESFR vs Extra hazard sprinklers for additional context on difference in sprinkler type:
https://www.meyerfire.com/daily/can-esfr-be-used-for-extra-hazard-group-2

Reply
Anthony
3/20/2023 08:10:54 am

Note you can get dry side wall sprinklers. but if you're using side wall sprinklers just us regular sprinklers that drain appropriately and are feed from the floor below.

Reply
Alex
3/20/2023 12:22:44 pm

If you are using a dry system because the attic isn’t heated, I would use Anthony’s approach and feed sidewalls from the floor below.

Great post, Anthony.

danefre
3/21/2023 02:59:09 pm

Question on that:

Is it just the density/area requirements that need to abide by NFPA 13? Can you still take a design area reduction even though closets/bathrooms are omitted? Maybe these dorms have common bathrooms over 55 sqft so that wouldn't be an issue.

Never done QR in 13R within dwelling units so not familiar with this.

To the OP: I would try to avoid dry systems in dwelling units. The 15s water delivery time is very difficult to achieve. Of course, this depends on the size of your system. Dry pendents + Dry valve is a lot of $$ compared to tenting over pipe with insulation.

Reply
Jesse
3/20/2023 08:24:14 am

I'm not familiar with dry, concealed pendents. I'm curious as to the driver for the dry system. Clearly the occupiable space is conditioned space. So is it just the attic that isn't conditioned? You're not protecting the attic so you might be able to use one of the freeze protection examples in 13R.

Reply
Shawn G.
3/20/2023 08:36:26 am

You will have to meet the requirements for 13 if you are going with a dry system (NFPA 13R 2016 - 5.4.3). Just fyi, I believe there is a required 15 second water delivery time associated with that.

Reply
JI
3/20/2023 09:40:37 am

It sounds like NFPA 13-R 2019 6.2.1.3 is most applicable in this situation for using quick response sprinklers. Calculation as per 7.1.2. I am not sure why the limitation of four sprinklers within dwelling units other than to align with NFPA 13R calculation requirements or small room rules.

Outside dwelling units is layout of sprinklers as per 6.2.2.1 and calculated to 7.2.3 which does not state a limitation on the amount of sprinklers to be used within an area.

Reply
Pete H
3/20/2023 10:11:06 am

Reliable has a residential dry sidewall that's semi-recessed and not concealed.

Tyco does as well.

I'm going to agree with Anthony, the easiest installation for you would be concealed wet residential sidewalls fed from the floor below.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT