Sprinklers Required Within Kids' Play Structure?

3/18/2021

14 Comments

 
Are sprinklers required beneath a McDonald's play structure?

On past projects I have designed roof-level sprinkler protection for the play area additions, but we are becoming involved in a government project where there is ceiling level protection and they are requiring protection beneath what are apparently several areas of the play structure that are greater than 4-feet in width.

I guess I can't argue that it is not "fixed-in-place." I'm sure most of these planes are higher than 24-inches above the ground, so that exception doesn't apply.

​​​​​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
14 Comments
matt
3/18/2021 09:21:06 am

There is an IBC section that deals directly with children's play structures to avoid having them packed full of sprinklers (don't recall the section offhand)

of course - I have also been required to pack a small play structure with over 20 sprinklers to cover inside every cubbie-hole and under every ramp in a non-combustible play-house structure inside a non-combustible building.

It just depends on who is doing the approving.

Reply
Anonymous
3/18/2021 11:06:39 am

Thanks, Matt, I'm reading Section 424 now.,,

Reply
Mike
3/18/2021 09:50:29 am

Have they thought about a little sprinkler cage isn't going to stop a small child from curiously touching that shiny little glass bulb? The next call you'll get is to remove the sprinklers. lol

Reply
matt
3/18/2021 10:37:52 am

I mentioned balancing the risk of fire vs damaged sprinklers/ water discharge/ kids hitting their heads on sprinklers. However, the consulting engineer insisted on full NFPA 13 protection... so that is what they got.

Reply
Glenn Berger
3/18/2021 10:36:08 am

The closest that I have come to issue - is the structure that supports the play equipment. The kidde play stuff on grade - no protection to date in any of my projects.

Reply
CJ Bonczyk
3/18/2021 11:03:33 am

Many times we have followed the NFPA guidelines of obstructions that state "fixed in place". We usually have the discussion with the GC and owner regarding these items and notify them early on that the AHJ may require additional protection as they see fit. When submittal time comes around we submit to the AHJ/Underwriter with specific information on the drawings about the play structure and whether sprinkler protection has been provided or not and let the AHJ determine if that is acceptable during plan review phase.
In your case since it is a government project and the engineer of record sealed documents stating to provide the protection, it should be provided. Provide a note in the area of protection where sprinklers are in the playground "Per engineer of record, sprinklers shall be placed below all play structures 4' wide or greater". Let the fire marshal decide if they want the protection below to be removed, thus taking any liability off of you.

Reply
Jay
3/18/2021 05:29:37 pm

This may not apply here as it's a "government" project, but in regards to comments about AHJ requirements.....keep in mind that you have the right to appeal decisions of the fire Marshal, building official, etc. The administrative chapter of the model code establishes limitations on authority and a board of appeals. Contrary to popular belief, the ahj cannot make you do something just because they say so. I understand the path of least resistance is to just do what they say, but if what they are requiring causes a substantial additional cost thats not required by the codes or standards or they are insisting that you provide a lower level of protection than what's required (insisting it be designed as a light hazard when its clearly required to be OH2-yes I've had this situation), then I would file an appeal with the board.

Reply
atif link
9/20/2021 05:41:34 am

Liberty of having specifications with favorable features helps in achieving satisfactory results for commercial playground equipment

Reply
Greg
9/7/2022 06:47:01 pm

Section 424 of the IBC specifically answers any questions if the structure is under 300 sq. ft. Anything above that may require an FPR (Fire Protection Report) From the report, the local design review will decide if an AMMR (Alternative Means and Methods Report) is required. This report will determine what steps have to take place to allow the structure. You may find yourself dealing with ASTM1918, ASTM,1354, NFPA13, NFPA289, NFPA701, NFPA253, UL1975, In other words, this is a JTHR report (Jump thru Hoops Report) and a PAOMTEACR report (Pay A lot Of Money To Engineers And Consultants Report)

Reply
Johnny Cabrera link
2/19/2025 11:39:04 pm

I'm just now reading this, four years late. Oh well. We have a wooden play structure, and the wood was tested and found to be fire resistant. Still, in order to keep the structure, we were required to install sprinklers in the bottom section. Now we're being told that we still cannot use the bottom section until we find sprinkler head covers that will keep small fingers out and from hanging on them. I can't find anything like this! Does this exist?

Reply
Greg
2/20/2025 10:01:37 am

There is a provision in one of the forementioned NFPA codes that expressly excludes play structures, But an AMMR will be required. With that said the fire marshal still has to accept it

Reply
Connor R link
5/8/2026 09:49:24 am

Hi Johnny,

The challenge is that anything small enough to keep small fingers from reaching in would also be small enough to keep the sprinkler water from distributing properly. Anything attached to the sprinkler needs to be listed/certified by the manufacturer for that specific sprinkler model.

Institutional sprinklers are specifically designed to be resistant to tampering. They are expensive, but worth it for the right application. One example is the Tyco Raven:

https://www.tyco-fire.com/products-and-solutions/sprinklers-nozzles-and-accessories/special-application/raven-i_fis/raven-institutional-sprinklers

This type of sprinkler is normally used in prisons and mental health facilities, but they could be useful in your case as well. The sprinklers are specifically designed to be difficult to hang anything from.

The catch is that if anyone did successfully pull the sprinkler away from the wall, it is designed to break away to avoid ligature. The force needed to cause the sprinkler to break away is probably greater than a child could provide. The manufacturer can provide information on the breakaway force and you could work with the AHJ to decide if the sprinklers are right for your application.

Reply
Ken Wofford
5/14/2025 03:17:39 pm

Any thoughts on the overhead protection of the play area? Playground equipment supplier is stating the the equipment is fire resistant. Overhead in the area is Ordinary Hazard Group 2 but Fire Marshal is questioning if it should be Extra Hazard.
Any thoughts?

Reply
Tim link
7/24/2025 10:10:32 am

Hi, I need advice as a California based indoor softolay owner/operator. My softplay equipments are manufactured overseas (China). Local fire inspector said that I need to show/prove my equipments meet CBC 424 codes. The manufacturer testing reports are internationally based for fire resistant and material testing and certification. How do I proof the equipments and materials meet CBC 424. Can you recommend a few fire protection engineers in Calfiornia to assist with this? Thank you

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT