Sprinklers Required Underneath Large Tanks?

8/5/2020

9 Comments

 
I have a water treatment plant with 3 tanks, 9 feet in diameter. The fire protection contractor feels we need to install a sprinkler under each tank, following the greater than 4 wide rule for obstructed construction. The tanks are located on a concrete floor. The tanks are supported on legs, and the clearance from the bottom of the tank to the floor is about 2 feet.

​Remembering that code tells us where to install sprinklers; my argument is this is not an occupiable space and sprinklers are not needed. The tanks are part of a water filter system, and not a hazardous type chemical storage.

Are sprinklers required underneath these tanks?

Any thoughts or input is most graciously appreciated.

​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
FIREPE25
8/5/2020 10:10:34 am

Sprinklers are required. Any obstruction greater than 18" below the deflector that is greater than 4' wide needs sprinklers. I believe the 2016 edition of NFPA 13 added some context about not needing them if the obstruction was close enough to the ground, but I am not sure on the exact language.

Reply
James
8/5/2020 10:11:40 am

Additional protection under the tank should not be required provided the bottom of the tank is 24" or less from the floor.

8.5.5.3.1.4 Sprinklers shall not be required under noncombustible
obstructions over 4 ft (1.2 m) wide where the bottom of the obstruction is 24 in. (600 mm) or less above the floor or
deck.

Reply
Paul
8/5/2020 11:16:13 am

Keep in mind, the 24 inch clearance was only added in the 2016 Edition of NFPA 13, so may not be adopted everywhere. This has not stopped me from submitting a variance/equivalent design to the AHJ's for approval, which most circumstance a valid argument/discussion allowed it to be approved.

Also, what are the sprinklers protecting, contents of the tank? The standard upright/pendent may not be applicable, just make sure.

Reply
GLENN BERGER
8/5/2020 11:58:23 am

Sprinklers are required. It will be easy for combustibles or other materials to eventually find its way to this "obstructed" space.

Reply
Mark C.
8/5/2020 01:34:03 pm

Is there a possibility to enclose the area below the tanks? If a noncombustible or limited-combustible concealed space is created, Section 8.15.1 allows for certain concealed spaces to not require sprinkler protection. If access for any type of piping or maintenance is required below the tanks, 8.15.1.2.2 specifically may still apply:

8.15.1.2.2 Concealed spaces of noncombustible and limited-combustible construction with limited access and not permitting
occupancy or storage of combustibles shall not require sprinkler protection.

Reply
Jonathan Joseph
8/5/2020 01:49:43 pm

I would put some kind of wired mesh screen and wrap around the legs so debris will not collect under the tanks if that is an issue.

Paul and James have mention the codes that meets the requirements of not having sprinkler protection as long as it is not over 24 inches in height and the contents inside the tanks are not hazardous storage.


Reply
Franck
8/6/2020 10:44:55 am

I'm afraid that every body is right (or wrong) and all refernecs are correct (even though they might be contradictory).
This will all depend on your AHJ or Insurance company and their interpretation of the situation.

I would personally not require a sprinkler underneath the tanks (but again, personal opinion) as long as we ensure that:
- the tank is non combustible
- the content of the tank is non combustible/flammable
- there is no other tank with flammable/combustible liquid in the same area
- there will be no combustible storage underneath (with 2 feet, there is little chance anyway to have combustible storage).

This being said, if combustible/flammable liquids are present in the area, it is a good practice to provide a sprinkler protection underneath. The same with combustible storage of goods.
With fl. liquids, sprinklers are usually installed upside down (i.e. pendent sprinkler in the upright position) to cool down the underneath of the tank, as it was required by a standard named Discuss (used for the process of distilleries of alcohol) which is quite a good document if you can read it.
The purpose of that sprinkler is that there is no pool fire underneath the tank that could expose the flammable/combustible liquid inside.

Be careful with the 4 in. rule and sense of judgement is of high importance.
There is no requirement, for example, to provide a sprinkler protection underneath tables, even though they are more than 2 ft, because it is highly improbable that storage will be present underneath.
The 4 ft dimension is justified, according to NFPA handbook, through past practice and experience, not through fire testing.
But some AHJ apply the zero-tolerance rule... And no argument can convince them.

Reply
Makc
4/11/2025 01:58:57 pm

There is no requirement for the tables because they are movable and NFPA 13 states that. I thought NFPA 13 is the minimum standard, how can AHJ "bless" anything less than a minimum?

Reply
Dale Morris
8/10/2020 10:57:31 am

I want to thank you all for your input. At the time I posted the question, I was not informed of the actual space under the tank. The clearance is 9 inches from the bottom of the tank to the floor. I love the idea of placing some mesh around the bottom to keep trash from accumulating under the tank.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT