Sprinklers Required Under Wall-Mounted Shelf?

8/24/2020

5 Comments

 
See this link for garage storage units on a project we're working on: https://www.wirecrafters.com/products/storage-lockers/garage-storage/ .

These are intended to be used for an enclosed parking structure in a mid-rise multi-family rental building.  As indicated in the photos (and photos from similar manufacturers) there are no sprinklers underneath the cages.

Will sprinkler heads be required?

Would appreciate code verbiage as well. We hope to not have to install sprinklers underneath due to cost reasons.

​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments
Dan Wilder
8/24/2020 09:43:10 am

The website says they are 3' deep so there would be no allowable removal of sprinklers beneath as they exceed the 30" maximum.

Depending on what sprinklers are being used adjacent to this and as long as it's not over 24" wide (if they are customizable), you could use the following sections to omit protection beneath without spacing limitations.
13 - 2016
8.6.5.1.2(c)
8.8.5.1.2(c)
8.9.5.1.4(c)
8.10.6.1.2(c)
8.10.7.1.4(c)

If they are up to 30" wide, you could apply the following:
8.6.5.1.2(b)
8.8.5.1.2(b)
8.9.5.1.4(b)
8.10.6.1.2(b)
8.10.7.1.4(b)

Reply
Brian Gerdwagen FPE
8/24/2020 11:34:40 am

You also need to ensure that they have the proper clearance to the sprinklers that are supposed to be protecting the storage. Depending on your type of sprinkler, this is at least 18" below the deflector.

I would say that the second picture on the website is not in compliance because the cage is against the ceiling with a sprinkler in the foreground. 18" can not be maintained between the sprinkler and the combustibles.

Reply
James Phifer
8/24/2020 11:40:16 am

I would review figure A.6.5.1.2 and see if that rule applies. If the top of the cage is 18" below the sprinkler deflector, and the cage is less than 48" wide, then no additional sprinkler protection should be required.

Reply
Cherie
8/25/2020 04:08:07 pm

I agree with James, but I am adding a number to the code reference. NFPA 13 -16 A 8.6.5.1.2
This does allow continuous obstructions of no greater than 4ft if the bottom of the head is at least 18 inches above the obstruction. I learned this one the hard way a couple of years ago, so I will never forget it!

Reply
Franck
8/31/2020 04:33:25 am

Note that the 18'' rule does not apply for storage against walls...
Reference in NFPA 2016: 8.6.6.2:
The 18 in. dimension shall not limit the height of shelving on a wall or shelving against a wall
& 8.6.6.1: Where shelving is installed on a wall and is not directly below sprinklers, the shelves, including storage thereon, shall be permitted to extend above the level of a plane located 18 in. below ceiling sprinkler deflectors.

In addition, NFPA 13 handbook (I recommend it to everyone as you will find useful additional comments and pictures) indicates that the clear space beneath the sprinkler is needed for the spray pattern to fully develop to allow proper wetting of the floor and not the wall. Sprinklers installed near wall-mounted shelves or piled storage against a wall are not intended to be governed by the requirements of 8.6.6.1.

In your case, this would means that if there is storage under your cage, you don't need to provide a sprinkler protection below it and everything is fine.
But if you apply the obstruction rules and provide a sprinkler head below your shelf because there is no storage underneath, it would be like considering that no storage under your shelf is more hazardous than combustible storage... Strange, no?

To be honnest, I would say that the situation is acceptable without sprinkler underneath, because the shelf is against the wall in an open cage.
But this is a personal point of view and the AHJ in your area may have a different one.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT