Sprinkler Protection for Large Boxed Furniture?

5/1/2020

7 Comments

 
There are restoration companies like Servpro that store furniture in large boxes in warehouses (some are wood and some are metal) for restoration. I have been told that the boxes are considered temporary since the items are restored and then moved back into the facility where it came from, but they can still be in the warehouse for months packed with all types of furniture.

NFPA 13, 2016 Table A.5.6 specifically lists "Storage container- Large container storage of household goods" as an example of a commodity that is not addressed by NFPA 13. I'm not intentionally picking on servpro because there are other companies like this, but servpro happens to be a popular one in my area so this is the example being used.

See an example of wooden storage boxes in the warehouse here:
https://www.youtube.com/watch?v=OiyPxTr2Tgg

1) Has anyone else protected an occupancy similar to this and can provide some insight? Do the boxes need to have sprinklers dropped in them while they are in the warehouse?

2) If this situation does fall into the "Large storage containers" not addressed by NFPA 13, does anyone know what standard I can utilize to adequately protect this space?

I appreciate any feedback.

Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments
sean
5/1/2020 11:15:00 am

you would not put sprinkler inside the wood boxes.

I would treat it as cartoned expanded plastic unless they can provide you additional information. Go for the worse case.

Reply
Noah Koski
5/1/2020 11:52:33 am

I sent this situation NFSA's "Expert of the day" service for their opinion and their unofficial interpretation is that this does fall into Table A.5.6 for examples of commodities that are not addressed by NFPA 13. The recommended solution in this situation would be to consult a Fire Protection Engineer for guidance to come up with a protection criteria that is acceptable to the AHJ since it is not addressed by any NFPA or FM Global standards at this time. Apparently this was discussed with PODs storage and there were plans of doing large scale testing of large storage containers stacked up to four units high in 2018, but I haven't been able to find anyone about it.

Sean how do you figure this should be protected as cartoned expanded plastic?

Reply
sean
5/1/2020 03:58:49 pm

I am looking at what I would expect to see in the wood crate. That would be some form of group A plastics (between modern furniture, and we have in our houses today). Glancing at NFPA 13 2016 table A.5.6.1.1 under group a plastics they have examples of just plastics or mixed materials. If people are storing furniture and house hold goods you would expect it to be a mix, but you never know so I would assume someone is storing a full container of cushions or all plastic parts,etc. The next column specifically calls out wooden crates. This differs from PODs they use a metal container and why testing would be warrented. So half way down you get the following:

material used to construct product:
Entirely expanded Group A
plastic
packaging material:
Corrugated cartons, wooden
crates, or wood boxes, with or
without internal plastic
packaging
pallet material:
None, metal, wood, or plastic
commodity class:
Cartoned expanded Group A
plastic

Is it perfect no but i think it takes into account enough information that an experienced designer and fire protection staff can agree to the commodity classification.

Reply
Mike
5/1/2020 12:43:07 pm

Go for the worst case. No one can fault you for that.

I've done Storage reports where the contractor used the smallest pipes and valves for the minimum and when a new occupant rented the warehouse, there was no capacity for his storage arrangements.

He used a 4" UG lateral, 3" riser in a 40' tall tilt up.

Occupant had to power his racks one level.

CYA

Reply
Franck
5/4/2020 04:53:04 am

By looking on the youtube video you provided, I don't think that your commodity falls into the "large storage containers" (just like the one you send overseas on large boats), but is indeed "stuff stored inside wooden boxes".
As indicated by Sean, I would consider the worst case commodity (and a class IV in all cases, as a minimum, if you take the chance of having not only boxes full of plastic).
All the more since you will have high probabilities to have the worst case commodity inside, based on the principle of storage.
As a tip, when choosing the right design density by using the curves with NFPA (if you go for a class I to IV...), I would look for a large area of application (not trying to have the density for 2000 sq ft, but rather for 3000 sq ft). This is because you will have larger boxes than just goods stored on pallets. The fire could also develop inside the box, being protected from the ceiling sprinkler protection and affect a larger area when it breaks out.
The good news is that because of the wooden boxes (which is thicker than small wooden boxes or cardboard boxes), the fire may be controlled by wetting the outside of the neighboring boxes before it can spread inside...
The bad news is the difficulty to have space between the boxes to enable the water to go down to the ground. Thus the larger area of application.
Don't consider to provide sprinklers inside the boxes. This is not practical and will never be done.
And what about the clearance inside your box and chances to damage the sprinkler heads while packing stuff inside. No to speak about the nightmare to connect your sprinkler inside the box to a fix sprinkler piping and the difficulty when you will pack boxes one over the others.

Reply
Noah Koski
5/4/2020 06:03:57 am

I found a great article on the SFPE page that covers this topic really well.

https://www.sfpe.org/page/2006_Q1_2/Warehouse-Sprinkler-Design-Configurations-Not-Covered-by-NFPA-13.htm

Reply
Dilan link
1/23/2021 10:12:01 pm

The business owners and realtors, clearance defines how high they will physically store. Clearances are typically are considered the space from the ground to bottom of roof structures like trusses, etc. To the hearth departments and code users, clearances are short for usually termed to explain the space between the highest of the storage to the sprinkler deflector.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT